    I know the gas line to a gas furnace or gas stove that is properly grounded is considered bonded.
    What about the same gas line that supplies the standard gas water heater, is it also bonded due to the furnace, stove, gas dryer etc being on a grounded circuit? I know this is nit picky but if you have to bond the water line to the water heater why not the gas line also?

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: gas line bonding

    Quote Originally Posted by Don Hawley View Post
    I know the gas line to a gas furnace or gas stove that is properly grounded is considered bonded.
    What about the same gas line that supplies the standard gas water heater, is it also bonded due to the furnace, stove, gas dryer etc being on a grounded circuit? I know this is nit picky but if you have to bond the water line to the water heater why not the gas line also?
    Don,

    From the 2011 NEC (I had that handy, but it's pretty much the same in later editions)

    250.104
    (B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.


    The clue is the second to last sentence. Since gas-fired forced air furnaces (blowers) are generally powered by 120 volts, theirs is the "circuit that is likely to energize the piping". Most gas-fired water heaters do not have 120 or 240 volts, so they are not "likely to energize the piping".

    However, now that you bring this up, some of the newer high-efficiency water heaters do use 120 volts to power the forced-draft blower.

    Does this help?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3

    Default Re: gas line bonding

    Quote Originally Posted by Gunnar Alquist View Post
    Don,

    From the 2011 NEC (I had that handy, but it's pretty much the same in later editions)

    250.104
    (B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.


    The clue is the second to last sentence. Since gas-fired forced air furnaces (blowers) are generally powered by 120 volts, theirs is the "circuit that is likely to energize the piping". Most gas-fired water heaters do not have 120 or 240 volts, so they are not "likely to energize the piping".

    However, now that you bring this up, some of the newer high-efficiency water heaters do use 120 volts to power the forced-draft blower.

    Does this help?
    Thanks Gunner, but you just restated what I said I understood. Had a spirited discussion with a seller's electrician over whether the standard water heater gas line needed to be bonded since the furnace was connected by 12-2 w/g. His point was the gas lines were all connected. Copper water lines were bonded and this could have been fixed with two clamps and 12 inches of wire. Was i wrong to call for bonding of the water heater gas line.


  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: gas line bonding

    Quote Originally Posted by Don Hawley View Post
    Thanks Gunner, but you just restated what I said I understood. Had a spirited discussion with a seller's electrician over whether the standard water heater gas line needed to be bonded since the furnace was connected by 12-2 w/g. His point was the gas lines were all connected. Copper water lines were bonded and this could have been fixed with two clamps and 12 inches of wire. Was i wrong to call for bonding of the water heater gas line.
    Hi Don,

    Sorry, I apparently misunderstood your question.

    I have a difficult time with bonding myself. There are a few things that I don't entirely understand about it. For example around here, the gas line is now (maybe for the past 6 or 7 years) always bonded at the meter with a bonding clamp similar to the type found on the water supply line. However, as discussed, the code says that it can be bonded with the heater grounding conductor. So why are my local building departments requiring the independent bonding? I haven't asked yet.

    As far as bonding the gas piping goes, one place should be fine, whether at the heater, water heater or meter. As you said, the piping is interconnected. Black pipe will have greater resistance than copper, so there is a possibility of a difference in potential voltage at various points along the piping, but in a residence it should not be significant.

    My understanding about bonding the hot and cold at the water heater is to ensure both the hot and cold pipes are always bonded. If a water heater is removed, the piping should remain bonded, to prevent any difference in voltage between the two pipes (might shock the plumber replacing the tank). In my area, the water heater is not going to provide the bond between hot and cold because dielectric fittings are typically used at the water supply connections. Therefore, the jumper above the water heater is required. I would expect that brass plumbing fixtures (shower & tub) would provide a positive connection between hot and cold water pipes, but, again, in my area, the AHJ requires the bonding jumper above the water heater. It might just be redundant, it might be to ensure bonding without relying on a mixing valve or it might be that some plumbing fixtures are coming out with nonconductive materials. Not sure there.

    Back to gas piping... Currently, CSST must be bonded with a #6 conductor. I am guessing here, but my local AHJs might be figuring that CSST is going to be installed at some time in the future and they want to make sure that it is bonded, even if an adventurous homeowner does it. As we all know, homeowners rarely let a lack of knowledge stop them from making modifications to their homes. As a result, I feel that bonding with a #6 is the better choice.

    Hopefully, Jerry Peck will chime in soon to tell me why I am wrong and what I missed.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Let's start with bonding piping systems.

    from the 2017 NEC:

    - 250.104 Bonding of Piping Systems and Exposed Structural Metal.
    - - (A) Metal Water Piping. (a different discussion)
    - - (B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to any of the following:
    - - - (1) Equipment grounding conductor for the circuit that is likely to energize the piping system
    - - - (2) Service equipment enclosure
    - - - (3) Grounded conductor at the service
    - - - (4) Grounding electrode conductor, if of sufficient size
    - - - (5) One or more grounding electrodes used
    - - - The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The points of attachment of the bonding jumper(s) shall be accessible.

    And

    - 110.3 Examination, Identification, Installation, and Use of Equipment
    - - (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.

    110.3(B) says "shall be installed and used in accordance with" the manufacturer's installation instructions (because those are part of the listing or labeling). And CSST manufacturers require addition bonding.

    Back to the original question:

    Quote Originally Posted by Don Hawley View Post
    Had a spirited discussion with a seller's electrician over whether the standard water heater gas line needed to be bonded since the furnace was connected by 12-2 w/g. His point was the gas lines were all connected. Copper water lines were bonded and this could have been fixed with two clamps and 12 inches of wire. Was i wrong to call for bonding of the water heater gas line.
    His point was that it "was not required", and your point was "but it is cheap and easy enough to do" ... both of which are valid and correct.

    Is there any reason not to bond the gas piping to the already bonded interior metal water piping at the gas fired water heater with no electric equipment on it?

    Yes, there is one reason.

    "It is not required."

    Is there any harm in bonding the gas piping to the already bonded interior metal water piping at the gas fired water heater with no electric equipment on it?

    Nope.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,873

    Default Re: gas line bonding

    Quote Originally Posted by Gunnar Alquist View Post
    Don,

    From the 2011 NEC (I had that handy, but it's pretty much the same in later editions)

    250.104
    (B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.


    The clue is the second to last sentence. Since gas-fired forced air furnaces (blowers) are generally powered by 120 volts, theirs is the "circuit that is likely to energize the piping". Most gas-fired water heaters do not have 120 or 240 volts, so they are not "likely to energize the piping".

    However, now that you bring this up, some of the newer high-efficiency water heaters do use 120 volts to power the forced-draft blower.

    Does this help?
    We have to jump the hot / cold and gas of a water heater with a #8 in my city


  7. #7
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: gas line bonding

    Quote Originally Posted by Marc M View Post
    We have to jump the hot / cold and gas of a water heater with a #8 in my city
    Marc,

    #8, not #6? Interesting. I believe I have only seen #6 around here. What city? I wouldn't have to ask if you had it in your profile like I do.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  8. #8
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: gas line bonding

    I believe the Mechanical code wants the incoming gas line bonded . (I will be researching this)
    I see it being done on houses all the time .
    They run a #4 bare copper from the electrical panel ground bar to the incoming gas line. They are connecting it ahead of the meter.
    I have had spirited conversations with some people about this. As it is creating a violation of the NEC, as the NEC says one can not use the incoming metallic gas piping as an grounding electrode.


  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Quote Originally Posted by jack davenport View Post
    I have had spirited conversations with some people about this. As it is creating a violation of the NEC, as the NEC says one can not use the incoming metallic gas piping as an grounding electrode.
    And they aren't using the gas line as a grounding electrode, they are simply bonding the gas line to the grounding system.

    Think of it this way: Interior metal water piping and underground metal water piping

    Interior metal water piping is bonded to the grounding system while the underground metal water piping is being used as a grounding electrode, and the location of the grounding electrode conductor to the underground metal water piping must be within 5 feet of the entrance of the underground metal water piping into the structure (not the exact wording, but that's basically what it says), however, if there is interior metal water piping only, the location of the bonding conductor no longer has to be at that within 5 feet point, and, if the exterior underground metal water piping is replaced with PVC ... and replaced all the way into the building for (let's just say) 10 feet, what was the grounding electrode conductor now becomes a bonding jumper, and (naturally) cannot be, nor needs to be, within that 5 feet of the entrance. (Whew! That was a long run-on sentence!)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,873

    Default Re: gas line bonding

    Quote Originally Posted by Gunnar Alquist View Post
    Marc,

    #8, not #6? Interesting. I believe I have only seen #6 around here. What city? I wouldn't have to ask if you had it in your profile like I do.
    Im in Santa Clarita. just installed a water heater and it was what was required


  11. #11
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: gas line bonding

    Bonding and connection to the Grounding electrode are similar in look and function, really only different in intent.
    The intent of the code is to provide a Grounding electrode to communicate/dissipate to the ground. The gas line cannot be used for the purpose of a Grounding Electrode, you must provide some other GE such as water line, UFER, plate, ring, or rod. Once the Grounding electrode system is in place then EVERYTHING must be bonded to that system which is why the gas pipe system IS connected to the Grounding electrode as part of the required bonding.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  12. #12
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: gas line bonding

    Quote Originally Posted by jack davenport View Post
    I believe the Mechanical code wants the incoming gas line bonded . (I will be researching this)
    I see it being done on houses all the time .
    They run a #4 bare copper from the electrical panel ground bar to the incoming gas line. They are connecting it ahead of the meter.
    I have had spirited conversations with some people about this. As it is creating a violation of the NEC, as the NEC says one can not use the incoming metallic gas piping as an grounding electrode.
    Quote Originally Posted by Jerry Peck View Post
    And they aren't using the gas line as a grounding electrode, they are simply bonding the gas line to the grounding system.

    Think of it this way: Interior metal water piping and underground metal water piping

    Interior metal water piping is bonded to the grounding system while the underground metal water piping is being used as a grounding electrode, and the location of the grounding electrode conductor to the underground metal water piping must be within 5 feet of the entrance of the underground metal water piping into the structure (not the exact wording, but that's basically what it says), however, if there is interior metal water piping only, the location of the bonding conductor no longer has to be at that within 5 feet point, and, if the exterior underground metal water piping is replaced with PVC ... and replaced all the way into the building for (let's just say) 10 feet, what was the grounding electrode conductor now becomes a bonding jumper, and (naturally) cannot be, nor needs to be, within that 5 feet of the entrance. (Whew! That was a long run-on sentence!)
    They ARE NOT attaching the #4 Bare Copper to the interior gas piping. The Gas meters are on the exterior of the dwellings. They are attaching to the INCOMING GAS LINE AHEAD OF THE METER where the piping exits the ground. Thus they are creating a Grounding Electrode out of the underground gas line. ( metallic pipe underground for 10 feet or more)

    Trust me I know about and understand all about grounding and bonding of a service.


  13. #13
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: gas line bonding

    Quote Originally Posted by Jim Luttrall View Post
    Bonding and connection to the Grounding electrode are similar in look and function, really only different in intent.
    The intent of the code is to provide a Grounding electrode to communicate/dissipate to the ground. The gas line cannot be used for the purpose of a Grounding Electrode, you must provide some other GE such as water line, UFER, plate, ring, or rod. Once the Grounding electrode system is in place then EVERYTHING must be bonded to that system which is why the gas pipe system IS connected to the Grounding electrode as part of the required bonding.

    In reality the Grounding electrode is basically for surges and lightning strikes. In a ground fault of the circuit, the current is looking to go back to the source not earth. Thats why the grounded
    ( neutral) and the grounded ( Neutral) / grounding ( ground) connection is so important. Without out it the overcurrent device would not open in a fault condition.


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Quote Originally Posted by jack davenport View Post
    They ARE NOT attaching the #4 Bare Copper to the interior gas piping. The Gas meters are on the exterior of the dwellings. They are attaching to the INCOMING GAS LINE AHEAD OF THE METER where the piping exits the ground. Thus they are creating a Grounding Electrode out of the underground gas line. ( metallic pipe underground for 10 feet or more)
    That does not make it a grounding electrode.

    Trust me I know about and understand all about grounding and bonding of a service.
    I do know that you know a lot about grounding and bonding of a service, but that does not mean that what you described is "Thus they are creating a Grounding Electrode out of the underground gas line."

    (all caps are mine, asterisks are mine too)
    250.104(B) Other Metal Piping. If installed IN, or ATTACHED TO, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to any of the following:
    (1) Equipment grounding conductor for the circuit that is likely to energize the piping system.
    (2) Service equipment enclosure*
    (3) Grounded conductor at the service**
    (4) Grounding electrode conductor, is of sufficient size***
    (5) One ore more grounding electrodes used****

    - "in, or attached to" ... means that it can be outside
    - * The service equipment enclosure is bonded to the grounding electrode system through the grounded service conductor.
    - ** The grounded conductor at the service is grounded to the grounding electrode system.
    - *** Grounding electrode conductor ... the gas piping can be bonded directly to a grounding electrode conductor without making the gas piping a grounding electrode.
    - **** One or more grounding electrodes ... the gas piping can be bonded directly to any of the grounding electrodes without making the gas piping another grounding electrode.

    Now if ... that Big IF ... IF the gas piping you describe is the only grounding electrode, then, yes, that use would be as a/the grounding electrode and not allowed ... but you did not say that there were no grounding electrodes present, only that the gas piping system was bonded to 'something', with the implication being that the 'something' was the grounding electrode conductor, or possibly to a grounding electrode, or possibly to the service equipment and something in it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: gas line bonding

    I can see the debate about the gas line being used as an electrode. It would act the same as a metallic water line effectively becoming an electrode. The only difference is that the connection is at the meter and not remote from the meter and being used as a conductor to get back to the panel.

    Jack, call me if you get a chance.

    All answers based on unamended National Electrical codes.

  16. #16
    Join Date
    Mar 2013
    Location
    Md and or PA
    Posts
    137

    Default Re: gas line bonding

    In Theory there is NO difference in the way they are bonding the gas line then one would utilize the metallic incoming water line ..
    They both originate at the service entrance panel , terminated on the grounded conductor terminal bar ...............?

    I am not arguing the wording and your post but In reality the words do not change whats installed .....
    A pig in a dress is still a pig ............?

    Just saying ??..

    Jim I will reach out tomorrow


  17. #17
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: gas line bonding

    I don't know about other parts of the country but where I worked the gas utility would have a fit if they found a connection between the incoming supply (pre-meter) gas line and the electrical panel.

    Gas meters are specifically made (isolation connection fittings) to prevent current being induced on a supply gas line. A gas line bonded supply would have just that if there were neutral supply issues as the current would use the gas line as a conductor to find a return path to the transformer. It would do this to a much smaller extent anyway as electricity seeks all paths. And, this process causes electrolysis that deteriorates the gas line, which will eventually leak and can and does cause explosions. Been there, seen that. Ain't pretty.

    Anyway, in most cases the grounding conductor used on gas appliances is sufficient to handle the required bonding of a gas line. Tying the hot and cold together at the water heater isn't a bad idea but the connection is often times made by a tub/shower valve. The requirement is the "system" be bonded, and if there is a physical connection between the hot and cold pipes then the requirement is met.

    Hopefully as plastic pipe starts replacing metallic pipe even in older residences all the "I've got a better way" crap local jurisdictions come up with regarding this stuff will start to go away.

    Last time I checked the bonding of CSST was a manufacturer's requirement and not an NEC code issue. And, so called black CSST isn't required to be bonded like the yellow variety is. Local requirements vary. See 2018 International Fuel Gas Code. Scroll down about 4 pages

    https://iccsafe.org/wp-content/uploads/PMG_CodeNotes_CSST.pdf






    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  18. #18
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: gas line bonding

    Quote Originally Posted by jack davenport View Post
    They ARE NOT attaching the #4 Bare Copper to the interior gas piping. The Gas meters are on the exterior of the dwellings. They are attaching to the INCOMING GAS LINE AHEAD OF THE METER where the piping exits the ground. Thus they are creating a Grounding Electrode out of the underground gas line. ( metallic pipe underground for 10 feet or more)
    This confuses me.

    Around here, any buried gas pipe must be factory-wrapped (I believe the yellow stuff is PVC) to prevent corrosion. All of the more current buried pipe that is installed by the utility company is plastic. I would have thought that the PVC wrap would also essentially isolate the pipe electrically from the soil. I suppose a really high voltage could breach the PVC wrap, but it would prevent the gas pipe from being an effective grounding electrode.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  19. #19
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    461

    Default Re: gas line bonding

    To belabor what's probably obvious, when we're talking conductor sizes, 250.66/250.102(C) size main bonding or grounding electrode conductors by the size of the ungrounded conductor/s, as in the service conductors. That's where we get sizes like 4 or 6 AWG in residential bonding, as opposed to 250.122, where we size equipment grounding conductors in accordance with the OC protection of the circuit that we want to trip in the event of a fault. Bonding gas equipment normally relies on smaller conductors used for motors associated with residential gas equipment.

    I can easily understand calling a 6 AWG conductor a GEC rather than an EGC in such cases, unless . . .
    . . . unless the jurisdiction is actually saying you need to bond the internal gas piping from the very point it enters the building. Furthermore, bond it using a conductor that won't be removed with replacement of any particular piece of gas equipment. What's more, bond it with a conductor that is exempt from the rules about protection from damage.

    That's my apologia for the AHJ.


  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Quote Originally Posted by david shapiro View Post
    To belabor what's probably obvious, when we're talking conductor sizes, 250.66...
    From the TracPipe CSST installation guide ( http://www.tracpipe.com/wp-content/u...1_DI_Guide.pdf ): (underlining is mine)

    1. When additional bonding of the TracPipe? CounterStrike?, yellow jacketed TracPipe? or TracPipe? PS-II? system is required by local codes, a bonding clamp must be attached to either the brass TracPipe? AutoFlare? or AutoSnap? fitting adapter Figure: 4-56, or to a black pipe component (pipe or fitting) within the gas piping system. The corrugated stainless steel portion of the gas piping system SHALL NOT be used as the bonding attachment point.

    The bonding should be in accordance with the National Electrical Code NFPA 70. Bonding electrode conductor sizing shall be in accordance with NFPA 70 Article 250.66 and Table: 250-66.

    3. If possible, avoid running the bonding conductor a long distance through the building. The connection should be as short as practical. The bonding clamp can be connected at a point on the piping system near the grounding electrode system.

    6. Original yellow jacketed TracPipe? must be bonded in accordance with this Section.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    461

    Default Re: gas line bonding

    Bonding aside, I tremble at the thought of running a fish tape through a space containing CSST and tearing it.

    Quote Originally Posted by Jerry Peck View Post
    From the TracPipe CSST installation guide ( http://www.tracpipe.com/wp-content/u...1_DI_Guide.pdf ): (underlining is mine)

    1. When additional bonding of the TracPipe? CounterStrike?, yellow jacketed TracPipe? or TracPipe? PS-II? system is required by local codes,
    6. Original yellow jacketed TracPipe? must be bonded in accordance with this Section.



  22. #22
    Join Date
    Apr 2010
    Location
    Reisterstown, MD
    Posts
    40

    Default Re: gas line bonding

    In Maryland we are required to include a statement in the report for homes that use CSST gas lines. Essentially the statement must say that the home contains CSST gas line and that only a licensed Master Electrician can verify a proper earth bond.

    The legislation requiring this disclaimer passed a couple of years ago when the state legislature decided that un-bonded CSST provided a substantial fire hazard from lightening strikes. Not a position substantiated by any research I've done or the millions of installations across the country (there are no successful class action lawsuits against CSST), but it does conveniently relieve Home Inspectors in Maryland from any liability.

    Bob Kenney
    www.IndependentHomeInspectionMD.com
    Call or TEXT : 410-504-3751 rkenney74@comcast.net

  23. #23
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    461

    Default Re: gas line bonding

    Bob, I can add one tiny bit to the discussion. At last week's NFPA conference we were shown a picture, from a forensic report, of CSST that had been pinholed by a nearby lightning strike in the opinion of the investigator, leading to an explosion.


  24. #24
    Join Date
    Apr 2010
    Location
    Reisterstown, MD
    Posts
    40

    Default Re: gas line bonding

    Quote Originally Posted by david shapiro View Post
    Bob, I can add one tiny bit to the discussion. At last week's NFPA conference we were shown a picture, from a forensic report, of CSST that had been pinholed by a nearby lightning strike in the opinion of the investigator, leading to an explosion.
    Thank you David, I too have seen evidence of lightning strike damage to CSST. We all know it has occured. Be that as it may, there has been no successful class action suit against CSST to date that I have seen. My conclusion is simply that it represents only a small fraction of total installations, the majority of which are as poorly bonded as my photo.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Bob Kenney
    www.IndependentHomeInspectionMD.com
    Call or TEXT : 410-504-3751 rkenney74@comcast.net

  25. #25
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: gas line bonding

    Bob,

    I do not believe that bonding to the CSST will actually allow it to be a part of the ground path, any more than attaching to hard pipe or a fitting. I would be more inclined to state that the bonding clamp (in your example) will crush the pipe and will not provide adequate bonding. As I'm sure you know, it is supposed to be bonded on a fitting or the rigid pipe.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  26. #26
    Join Date
    Apr 2010
    Location
    Reisterstown, MD
    Posts
    40

    Default Re: gas line bonding

    If I'm not mistaken the whole idea of grounding or bonding as it relates to lightening suppression is to prevent certain parts from becoming energized. House wiring for example or in this case the CSST. Old time lightening rods on barns are a perfect example of this.

    The instances we've all seen of CSST perforation and the resulting fires occur from the high current imposed by a lightening strike energizing and damaging the CSST itself as it arcs off of it to adjacent metal. If the current has to travel along the CSST before it reaches the bonding wire, you might as well not even use a wire. As far as the connection itself, as inadequate as it might be, a loose connection causes arcing and I am quite sure that lightening will not care.

    Bob Kenney
    www.IndependentHomeInspectionMD.com
    Call or TEXT : 410-504-3751 rkenney74@comcast.net

  27. #27
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Quote Originally Posted by Bob Kenney View Post
    As far as the connection itself, as inadequate as it might be, a loose connection causes arcing and I am quite sure that lightening will not care.
    Have you seen what lightning does to NM cable when it finds a path to ground and that path is partly NM cable?

    I posted photos of it years ago, and still have the photos if I need to repost them.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  28. #28
    Join Date
    Apr 2010
    Location
    Reisterstown, MD
    Posts
    40

    Default Re: gas line bonding

    Quote Originally Posted by Jerry Peck View Post
    Have you seen what lightning does to NM cable when it finds a path to ground and that path is partly NM cable?

    I posted photos of it years ago, and still have the photos if I need to repost them.
    That's exactly my point. If CSST is part of the ground path it is sure to cause a fire.

    Bob Kenney
    www.IndependentHomeInspectionMD.com
    Call or TEXT : 410-504-3751 rkenney74@comcast.net

  29. #29
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Quote Originally Posted by Bob Kenney View Post
    That's exactly my point. If CSST is part of the ground path it is sure to cause a fire.
    I'm going to guess that you haven't seen the photos.

    If it's a good ... "good" ... ground path it may survive a lightning strike ... "may".

    The problem is that lightning is such a high energy pulse, and given that electricity takes all available paths, a lightning strike will take "available paths" which were considered as "available paths" ... lightning 'makes its own available paths'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  30. #30
    Join Date
    Apr 2010
    Location
    Reisterstown, MD
    Posts
    40

    Default Re: gas line bonding

    Quote Originally Posted by Jerry Peck View Post
    I'm going to guess that you haven't seen the photos.

    If it's a good ... "good" ... ground path it may survive a lightning strike ... "may".

    The problem is that lightning is such a high energy pulse, and given that electricity takes all available paths, a lightning strike will take "available paths" which were considered as "available paths" ... lightning 'makes its own available paths'.
    The point of lightening rods is to divert the electrical energy along a "chosen" path rather than let it choose its own (which it sometimes does anyway). When CSST becomes the lightening's path to ground it can become perforated leaking gas and igniting the gas. The perforation occurs when the electrical energy arcs (think arc welding) to adjacent metal conductors of any kind; fittings, pipes, appliance cabinets, or in this case a ground wire making a loose fit connection.

    The picture I posted shows an improperly bonded CSST gas line more likely to create damage than to avert it in the case of a lightening strike.

    Bob Kenney
    www.IndependentHomeInspectionMD.com
    Call or TEXT : 410-504-3751 rkenney74@comcast.net

  31. #31
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line bonding

    Bob,

    My point is, whether the CSST is bonded to ground or not ... lightning WILL LIKELY find it.

    The key at that point is to keep the lightning energy already on the CSST ... on the CSST. Not jumping to and from the CSST.

    Reduced risk of penetration of the CSST, and leakage which will follow.

    Nothing will "eliminate" the risk with CSST, reducing the risk is all which can be hoped for.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •