    This is a meltal flue, metal box and solid fuel burning fire place. There was the metal skirt but no glass doors. It looked alittle odd, but i am not sure about the need or requirement. It seems like i always have noted glass doors present on these type units.
    Thanks!
    Jerome


    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Jerome W. Young; 01-16-2008 at 02:44 PM. Reason: forgot picture
    OREP Insurance

  2. #2
    imported_John Smith's Avatar
    imported_John Smith Guest

    Default Re: are glass doors required

    Not required, but a good idea to have for energy conservation.


  3. #3
    Randy Brooks's Avatar
    Randy Brooks Guest

    Default Re: are glass doors required

    Jerome,

    This is a factory built fireplace and if its location is the state of California, and if it was install since 1988, glass doors would be required. This was a California Energy Code requirement in 1988 aimed at energy conservation. That being said, any glass door would have to listed and tested for use with this specific fireplace model. That is to say, just any glass door can not be installed as it may block important cooling vents or alter the venting in some way.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    In Florida, it is: (underlining is mine)
    13-606.1.ABC.1.3 Additional Infiltration Requirements. The following additional requirements shall be met:
    - 1. All exhaust fans vented to the outdoors shall have dampers. This does not apply to combustion devices with integral exhaust ductwork, which shall comply with NFPA 54 or the locally adopted code.
    - 2. All combustion space heaters, furnaces, and water heaters shall be provided with adequate combustion air. Such devices shall comply with NFPA or the locally adopted code.
    - 3. All fireplaces and wood stoves shall have flue dampers.

    Last edited by Jerry Peck; 01-17-2008 at 11:58 AM. Reason: to correct font size / style
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: are glass doors required

    Jerry?

    Glass doors = flue dampers??

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    Quote Originally Posted by Jim Luttrall View Post
    Jerry?

    Glass doors = flue dampers??
    Jim,

    No. Presumably (like, yeah, right) the owners will close the damper when they do not have a fire in the fireplace / wood stove, thereby reducing heat gain / heat loss through air infiltration through the chimney / vent.

    Glass doors help even more (of course, though, with fresh air from outdoors sufficient enough to feed the fire) by restricting the amount of conditioned air which goes up the chimney / vent when the fireplace / wood stove is in use. Provided, of course, the unit is new enough to have come with a make up combustion air intake.

    Our vented gas fireplace has a damper (which I never close - Oh no, don't send the energy police! - just like *most* people probably do not close their damper), it has no real outside combustion make up air (although there is a large vent grill through the back of the wood frame chimney enclosure to outdoor air and one vent at the top of the shelves on each side of the fireplace ... see photo ... which are probably there to provide make up combustion air, doubtful as to how good it is though - glass doors would simply cut that off anyway, if that is the intent).

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    wayne stritsman's Avatar
    wayne stritsman Guest

    Default Re: are glass doors required

    The fireplace in question appears to be a factory built model that is tested to UL standards. in the test standard only doors that have been tested for this manufacturer and model are allowed to be used.
    they were intended as an accessory by the manufacturer.
    the screens on the other hand are a requirement.
    in some jurisdictions, such as New York the local energy code requires door so as to comply with enregy conversation code but are not required for safety.
    you made need to check your local code


  8. #8
    imported_John Smith's Avatar
    imported_John Smith Guest

    Default Re: are glass doors required

    Jerry, I dont understand your connection to flue dampers. How can you make the connection that glass doors = flue damper? I didnt really understand your response. Could you elaborate? Could you reference the specific requirement to glass doors?


  9. #9
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: are glass doors required

    Jerry,

    That decorative broom is combustible material on your hearth is it not?

    Be careful with those fires.

    rick


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    Quote Originally Posted by imported_John Smith View Post
    Jerry, I dont understand your connection to flue dampers. How can you make the connection that glass doors = flue damper?
    I was not making that connection.

    I was making the connect that the Florida energy code ONLY requires a "damper".

    Then I explained (obviously not very well) what difference dampers and glass doors do.

    Could you reference the specific requirement to glass doors?
    To my knowledge, there is none, which is why I did not reference one. At least not unless the manufacturer requires a glass door or, like CA, an energy code requires them. The Florida Energy Code ONLY requires a damper.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    Quote Originally Posted by Rick Hurst View Post
    That decorative broom is combustible material on your hearth is it not?
    So are those "stockings hung on the chimney with care".

    That broom is one of those cinnamon brooms which made it all smell nice for the holidays, it does not reside there all the time.

    Be careful with those fires.
    Rick,

    Yes, but is a gas fireplace so I don't have any logs to worry about rolling out. In fact, we will be replacing the log set and burner soon ... or, should I say 'we will be replacing the burner soon, and because the log set and burner together as a set are not much more than just a replacement burner, so we are getting new ceramic logs too'. I will clean up the old ceramic logs and stack them outside the fireplace like you would keep a stack of wood logs - what to heck, I will have them, might as well use them for something.

    Stop by for a visit, you will be 'in good hands' ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: are glass doors required

    Jerry,

    Did you pay money for those chairs?

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    Quote Originally Posted by Gunnar Alquist View Post
    Jerry,

    Did you pay money for those chairs?
    Yessiree!

    And we have a right hand one and a left hand one.

    By the way, they are each carved out as a single piece of wood.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: are glass doors required

    Jerry P; I was going to ask what Gunner did and now that I know that those are actually your chairs when do you think you will be able to afford the rest of them? Also, it appears one must be careful when sitting down?

    Jerry McCarthy
    Building Code/ Construction Consultant

  15. #15
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: are glass doors required

    Quote Originally Posted by Jerry McCarthy View Post
    Also, it appears one must be careful when sitting down?
    Jerry Mc.,

    Actually, they are quite comfortable. The top of the thumb serves as an arm rest for one side. Now, if only they are carved the little finger bent over, there would be an arm rest for the other side.

    They are also quite heavy.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  16. #16
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: are glass doors required

    Which is your sock?

    California Energy Code
    10/7/97 - Energy Efficiency Standards for
    Residential and Non Residential Buildings
    July 1992 - California Energy Commission
    Subchapter 7 (Section 150):
    (e) Installation of Fireplaces, Decorative Gas Appliances, and Gas Logs
    1. If a masonry or factory-built fireplace is installed, it shall have the following:
    A. Closable metal or glass doors covering the entire opening of the firebox;
    B. A combustion air intake to draw air from the outside of the building directly into the firebox, which is at least 6-square inches in area and is equipped with a readily accessible, operable, and tight-fitting damper or combustion air control device; and
    EXCEPTION to Section 150(e)1.B: An outside combustion air intake is not required if the fireplace will be installed over concrete slab flooring and the fireplace will not be located on an exterior wall.
    C. A flue damper with a readily accessible control.
    EXCEPTION to Section 150(e)1.C: When a gas log, log lighter, or decorative gas appliance is installed in a fireplace, the flue damper shall be blocked open if required by the manufacturer's installation instructions or the State Mechanical Code.

    Jerry McCarthy
    Building Code/ Construction Consultant

  17. #17
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: are glass doors required

    Jerry P.

    I dunno... I think I would feel like I was in an Allstate commercial.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •