    can you put a type 1 indoor sub panel in an outdoor shed.

    Note the service wiring size? pretty sure that is too small

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Question Re: type 1 enclosure

    Not sure about the type of panel, but that wire feeding the panel appears to be #12 which is good for 20 Amps. Looks like youve got a minimum of 60 Amps there. So yes its too small. I sure the rest of us will tear apart the rest of that setup

    Paul Kondzich
    Ft. Myers, FL.

  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: type 1 enclosure

    Quote Originally Posted by Paul Kondzich View Post
    ... that wire feeding the panel appears to be #12 which is good for 20 Amps. Looks like youve got a minimum of 60 Amps there. So yes its too small. ..
    Comparing the sum of the breaker ratings to the size of the feeders doesn't really tell you much. Many 100 amp panels have 300+ amps in breakers installed.


  4. #4
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: type 1 enclosure

    I understand that John, but, it (appears) that the wire coming off the breakers is larger than the wire feeding the panel. No way is that right.

    Paul Kondzich
    Ft. Myers, FL.

  5. #5
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: type 1 enclosure

    Quote Originally Posted by Paul Kondzich View Post
    ...the wire coming off the breakers is larger than the wire feeding the panel. No way is that right.
    The fact that the branch conductors might be bigger than the feeders isn't in itself a problem.


  6. #6
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Question Re: type 1 enclosure

    OK I guess we will have to see what the rest of the peanut gallery thinks

    Paul Kondzich
    Ft. Myers, FL.

  7. #7
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: type 1 enclosure

    Are those white wires attached to the bus bar charred? They look black... which could certainly accompany the problems already mentioned.

    I think HD should make you fill out a competency test before selling people electrical equipment.


  8. #8
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default Re: type 1 enclosure

    cabinet rated for 60 amp; yes neutrals and grounds connected and black


  9. #9
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: type 1 enclosure

    Quote Originally Posted by Jerome W. Young View Post

    Note the service wiring size? pretty sure that is too small
    # 6 cooper would be the minimum or #4 Aluminum.

    If it's inside an enclosed building it doesn't matter if it's a 3500sf house or 100 sq. ft shed.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  10. #10
    John Steinke's Avatar
    John Steinke Guest

    Default Re: type 1 enclosure

    The size of the feeder wire is determined entirely by the size of the breaker feeding it - and not the size of the breakers, or wires, being fed. As long as those wires come from a 20 amp (or smaller) breaker, they're fine.

    To answer your original question, though .... "inside" is inside. If it's got a roof over it, NEMA-1 is just fine. Or, perhaps more accurately ... NEMA-1 is just fine for any dry, or damp, location.


  11. #11
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: type 1 enclosure

    Quote Originally Posted by Jerome W. Young View Post

    Note the service wiring size? pretty sure that is too small
    Quote Originally Posted by John Steinke View Post
    The size of the feeder wire is determined entirely by the size of the breaker feeding it - and not the size of the breakers, or wires, being fed. As long as those wires come from a 20 amp (or smaller) breaker, they're fine.

    .
    John,

    ?????

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: type 1 enclosure

    John is correct.

    Billy,

    Think of it this way: 20 amp breaker feeds a #12 AWG circuit (20 amps), which feeds a 60 amp panel, which has 60 amps of breakers in it.

    Question: How much current is going to be able to be drawn through that #12 AWG wire?

    Answer: 20 amps - otherwise the 20 amp breaker feeding it will trip.

    Okay, though, here is something else to consider: I doubt those terminals (the mains or the neutral) are rated for use with that small of a conductor. The neutral is an easy fix, and I have no idea why it was not done - simply move it to a smaller terminal on that same bar.

    Don't forget the open knock out on the right.

    Also, that is not the "service equipment" yet the green ground conductor is in the same terminal bar as the neutral - and that is not allowed.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: type 1 enclosure

    Quote Originally Posted by Jerome W. Young View Post

    Note the service wiring size? pretty sure that is too small
    Jerome,

    What Size breaker was in the Main Service Panel that feeds this panel?

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •