Results 1 to 16 of 16
  1. #1
    Join Date
    Sep 2007
    Location
    San Antonio TX
    Posts
    88

    Default Crazy Electrician.

    This is in-sight shut off switch for A/C. I need description of the problems.
    Thanks.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Crazy Electrician.

    Quote Originally Posted by Zibby Swieca View Post
    This is in-sight shut off switch for A/C. I need description of the problems.
    Thanks.
    Are you saying that this is "in sight" or "inside" of the A/C disconnect?

    Did it have a dead front cover on it?

    Where does the exposed NM line on the left side go? It looks like it is connected to the terminals on the bottom, if so this is wrong.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Sep 2007
    Location
    San Antonio TX
    Posts
    88

    Default Re: Crazy Electrician.

    It did not have dead front cover on it and it is in-sight switch behind condenser.


  4. #4
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Crazy Electrician.

    Zibby,

    Make it simple if you need.

    Electrical repairs are needed to the disconnect switch box to the condensing unit. Contact a Licensed Electrician for repairs.

    As a inspector, don't feel you have to explain every detail as what is wrong. You recognize it needs repair and call it out as so.

    JMHO

    Rick


  5. #5
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Crazy Electrician.

    Quote Originally Posted by Zibby Swieca View Post
    This is in-sight shut off switch for A/C. I need description of the problems.
    Thanks.
    .
    Also low voltage wires are not allowed inside the box.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  6. #6
    Join Date
    Sep 2007
    Location
    San Antonio TX
    Posts
    88

    Default Re: Crazy Electrician.

    This is excellent suggestion.
    Thank you


  7. #7
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Crazy Electrician.

    Do as Rick said. I'm going to say that the "Old" disconnect has several problems that I can see from the photo. Just missing the dead front cover is enough to call it out, then add on the unprotected NM cable, the double taps and the low voltage control lines for the thermostat.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Crazy Electrician.

    Just to name a few thing I see in there:
    - As stated by others - no dead front cover.
    - What does that safety switch operate? Has the switching guts been removed?
    - The neutral on the 240 volt circuit is connected to ground.
    - The ground terminal is most likely only rated for one conductor and has at least 3 conductors in it (3 are visible).
    - As stated by others - no low voltage is allowed in there with the power circuit conductors.
    - There is a good potential for the bare ground to come in contact with a hot terminal.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Crazy Electrician.

    That switch used to have a insulating (cardboard) cover in it, the retaining screw is still there, (it's a ITE disco) ,another thing is the switch is a 1Ø 2 W , no provision for a neutral, & if A/C data plate states "maximum fuse or HACR circuit breaker size __" a non fusible disco may not be used.

    BTW, other then the insulating cover, the switch is complete.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Crazy Electrician.

    Quote Originally Posted by Rollie Meyers View Post
    if A/C data plate states "maximum fuse or HACR circuit breaker size __" a non fusible disco may not be used.
    Rollie,

    With a non-fused disconnect at the a/c condenser unit, there would be a fused disconnect at the supply to those circuit conductor, which most likely originate at a panel and are protected by the breaker (or fuse) at that panel. The conductors are *required* to be protected on their supply end.

    Once protected, the name plate on the a/c disconnect does not require an additional overcurrent device (breaker or fuse) - unless the first overcurrent device is too large, in which case a lower rated overcurrent device could be installed in place of the first overcurrent device, or, a lower rated overcurrent device could be added at any convenient point (which is most typically at the required disconnect for the unit).

    Now, to take this a little further, if the name plate states "Max Fuse Size" ... a "fuse" must be used for overcurrent protection, not a breaker.

    Most modern units will state "Max Fuse or HACR Breaker Size", meaning that either may be used.

    The maximum nameplate rating has nothing to do with using a fused or non-fused disconnect.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Crazy Electrician.

    "Flip this house"?.

    One of many details at a flip, what's your vote: report it, or just shake your head and keep moving?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Michael Thomas; 03-01-2008 at 11:12 AM.
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  12. #12
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Crazy Electrician.

    Michael,

    You might want to start An Apparent Amateur Installation Section.

    Along with .

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  13. #13
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Crazy Electrician.

    Quote Originally Posted by Billy Stephens View Post
    Michael,

    You might want to start An Apparent Amateur Installation Section.

    Are that many bytes available on the Internet?

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  14. #14
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Crazy Electrician.

    Quote Originally Posted by Michael Thomas View Post
    Are that many bytes available on the Internet?

    I feel your pain.

    Had a Bank Repo I had to burn a CD just for the picture section of the Report.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  15. #15
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Crazy Electrician.

    Easy for a flipper to fix, at least.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  16. #16
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: Crazy Electrician.

    Do you know your tree is sideways?