Results 1 to 7 of 7
  1. #1
    Michael Vasquez's Avatar
    Michael Vasquez Guest

    Default Aluminum duct at the water heater

    This is the first time I have seen an aluminum duct (dryer type duct) used for a gas water heater vent. Just want to make sure if this is acceptable or not before I comment on it. Thank You

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Aluminum duct at the water heater

    It is probably a listed 'vent connector'.

    You should have been able to find a label on it stating it was listed for that use.

    Those 'are not' allowed to go through a wall or ceiling, they are only allowed to connect the appliance to the Type B Gas Vent.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Michael Vasquez's Avatar
    Michael Vasquez Guest

    Default Re: Aluminum duct at the water heater

    Thanks again Jerry


  4. #4
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Aluminum duct at the water heater

    IFGC 503.10.1 General. A vent connector shall be made of noncombustible corrosion resistant material capable of withstanding the vent gas temperature produced by the equipment and of sufficient thickness to withstand physical damage.

    NFPA 211 dittoes this but adds if corrugated, must be listed. This is due to decreased flow capacity by corrugated ducts.

    I recently ran to a hardware store to get some vent connector and all they had was cheap aluminum flex, like you see with dryer vent kits. Its tag stated it was rated to 480F. I told the homeowner it was suitable for an overnight repair but that was it. This duct does Not meet the requirements for physical damage. Moreover, it comes apart really easily.

    Make sure it is not a listed aluminum flex connector, which has listing stickers on it and is much more rigid and substantial than dryer vent flex.

    HTH

    Keep the fire in the fireplace.

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Aluminum duct at the water heater

    IFGC 503.10.1 General. A vent connector shall be made of noncombustible corrosion resistant material capable of withstanding the vent gas temperature produced by the equipment and of sufficient thickness to withstand physical damage.

    NFPA 211 dittoes this but adds if corrugated, must be listed. This is due to decreased flow capacity by corrugated ducts.

    I recently ran to a hardware store to get some vent connector and all they had was cheap aluminum flex, like you see with dryer vent kits. Its tag stated it was rated to 480F. I told the homeowner it was suitable for an overnight repair but that was it. This duct does Not meet the requirements for physical damage. Moreover, it comes apart really easily. It is so sloppy, it cannot hold its shape and needs much more support than rigid pipe. You need slings. If you try to screw through a "drive' into it, the flex just crushes and comes apart. Real junk. All it's good for is making robot arms for the kid's school play...

    Make sure it is not a listed aluminum flex connector, which has listing stickers on it and is much more rigid and substantial than dryer vent flex.

    HTH

    Keep the fire in the fireplace.

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Aluminum duct at the water heater

    Quote Originally Posted by Bob Harper View Post
    Make sure it is not a listed aluminum flex connector, which has listing stickers on it and is much more rigid and substantial than dryer vent flex.
    Bob,

    Er ... did you mean to say "Make sure it is not a listed ", or "Make sure it is a listed "?



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Talking Re: Aluminum duct at the water heater

    Listed means it is ok. The stiff stuff with the listing stickers is ok. The dryer vent hose is crap.

    Keep the fire in the fireplace.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •