    Does anyone see an issue with this. The rafter were 2x8's and the ridge 2x6.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: Rafters larger than ridge

    Gregg,
    While this may not be "Inspector 101" it's pretty close and has been covered many times in this thread.

    I hope that you called it out as a defect.
    JF


  3. #3
    Join Date
    Mar 2007
    Location
    Garland, TX
    Posts
    652

    Default Re: Rafters larger than ridge

    Yes the ridge is not the proper size and collar beams are also required unless they are present and out of the frame.
    I looks like there is one back by the vent.

    badair http://www.adairinspection.com Garland, TX 75042
    Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
    life is the random lottery of events followed by numerous narrow escapes...accept the good

  4. #4
    Richard Rushing's Avatar
    Richard Rushing Guest

    Post Re: Rafters larger than ridge

    Hello Gregg,

    For future reference, here is the IRC back up for the requirement;

    R802.3 Framing details. Rafters shall be framed to ridge board or to each other with a gusset plate as a tie. Ridge board shall be at least 1-inch (25.4 mm) nominal thickness and not less in depth than the cut end of the rafter. At all valleys and hips there shall be a valley or hip rafter not less than 2-inch (51mm) nominal thickness and not less in depth than the cut end of the rafter. Hip and valley rafters shall be supported at the ridge by a brace to a bearing partition or be designed to carry and distribute the specific load at that point. Where the roof pitch is less than three units vertical in 12 units horizontal (25-percent slope), structural members that support rafters and ceiling joists, such as ridge beams, hips and valleys, shall be designed as beams. installed to bearing walls at a slope not less than 45 degrees from the horizontal. The braces shall be spaced not more than 4 feet (1219 mm) on center and the unbraced length of braces shall not exceed 8 feet (2438 mm).

    Hope this helps...

    Rich



  5. #5
    Chad Fabry's Avatar
    Chad Fabry Guest

    Default Re: Rafters larger than ridge

    Yes the ridge is not the proper size and collar beams are also required unless they are present and out of the frame.
    I looks like there is one back by the vent.
    Collar ties are required?

    The ridge board isn't required, but if it's there it must be big enough to fully support the rafter.


  6. #6
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Rafters larger than ridge

    Barry,

    Coud you quote the section of the code that states collar ties are required?

    According to the NJDCA (the board that oversees NJ code); collar ties are NOT required by code; the only time they are required is if they are part of the engineers design.


    Darren

    New Jersey Home Inspection - About the House!

    Last edited by Darren Miller; 04-27-2007 at 05:17 AM.

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Rafters larger than ridge

    From the IRC.

    (Tucked back in the wording of R802.3.1, just before R802.3.2.)

    Collar ties or ridge straps to resist wind uplift shall be connected in the upper third of the attic space in accordance with Table R602.3(1).

    Collar ties shall be a minimum of 1-inch by 4-inch (25 mm by 102 mm) (nominal), spaced not more than 4 feet (1219 mm) on center.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Garland, TX
    Posts
    652

    Default Re: Rafters larger than ridge

    Jerry,
    Thanks!

    Whew, that almost felt like I walked into a room full of builders going over one of my reports.

    also from TREC SOP
    (6) report as in need of repair the lack of or inappropriate installation of components such as purlins, struts, collar ties or rafter ties, where necessary

    I was taught, back in the '70s by an Old World carpenter most of his plans were on a legal pad or napkin and designs were created on site, collar ties are required and therfore their absence in the subject photo would be noted as a repair in my report.

    Last edited by BARRY ADAIR; 04-27-2007 at 06:25 AM.
    badair http://www.adairinspection.com Garland, TX 75042
    Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
    life is the random lottery of events followed by numerous narrow escapes...accept the good

  9. #9
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Rafters larger than ridge

    Here is the whole enchilada:

    2006 IRC: R802.3.1 Ceiling joist and rafter connections. Ceiling joists and rafters shall be nailed to each other in accordance with Table R802.5.1(9), and the rafter shall be nailed to the top wall plate in accordance with Table R602.3(1). Ceiling joists shall be continuous or securely joined in accordance with Table R802.5.1(9) where they meet over interior partitions and are nailed to adjacent rafters to provide a continuous tie across the building when such joists are parallel to the rafters. Where ceiling joists are not connected to the rafters at the top wall plate, joists connected higher in the attic shall be installed as rafter ties, or rafter ties shall be installed to provide a continuous tie. Where ceiling joists are not parallel to rafters, rafter ties shall be installed. Rafter ties shall be a minimum of 2-inch by 4-inch (51 mm by 102 mm) (nominal), installed in accordance with the connection requirements in Table R802.5.1(9), or connections of equivalent capacities shall be provided. Where ceiling joists or rafter ties are not provided, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice.Collar ties or ridge straps to resist wind uplift shall be connected in the upper third of the attic space in accordance with Table R602.3(1). Collar ties shall be a minimum of 1-inch by 4-inch (25 mm by 102 mm) (nominal), spaced not more than 4 feet (1219 mm) on center.


  10. #10
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Rafters larger than ridge

    See that, just goes to show the difference is state requirements.

    "Collar ties or ridge straps to resist wind uplift shall be connected in the upper third of the attic space in accordance with Table R602.3(1). Collar ties shall be a minimum of 1-inch by 4-inch (25 mm by 102 mm) (nominal), spaced not more than 4 feet (1219 mm) on center." does not appear in the NJ code.


    "Where ceiling joists or rafter ties are not provided, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice." the next sentence states 'Rafter ties shall be spaced not more than 4 feet (1219) on center.' end of section.



    Guess our wind isn't as strong as the rest of the country.


    Darren
    New Jersey Home Inspection - About the House!


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Rafters larger than ridge

    Quote Originally Posted by Darren Miller View Post
    See that, just goes to show the difference is state requirements.

    "Collar ties or ridge straps to resist wind uplift shall be connected in the upper third of the attic space in accordance with Table R602.3(1). Collar ties shall be a minimum of 1-inch by 4-inch (25 mm by 102 mm) (nominal), spaced not more than 4 feet (1219 mm) on center." does not appear in the NJ code.


    "Where ceiling joists or rafter ties are not provided, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice." the next sentence states 'Rafter ties shall be spaced not more than 4 feet (1219) on center.' end of section.



    Guess our wind isn't as strong as the rest of the country.


    Darren
    Actually, I think there is a wording recognition problem with the builders up there.

    *I* *think* they are using the term "rafter ties" and are meaning "collar ties".

    Are "rafter ties" defined in the NJ code? Does it say where the "rafter ties" are to be installed?


    I'm going with 'they mean *collar* ties'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Rafters larger than ridge

    "Where ceiling joists are not connected to the rafters at the top wall plate, joists connected higher in the attic shall be installed as rafter ties, or rafter ties shall be installed to provide a continuous tie. Where ceiling joists are not parallel to rafters, rafter ties shall be installed. Rafter ties shall be a minimum of 2-inch by 4-inch (51 mm by 102 mm) (nominal), installed in accordance with the connection requirements in Table R802.5.1(9), or connections of equivalent capacities shall be provided. Where ceiling joists or rafter ties are not provided, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice."

    That's what the code says; obviously it defines rafter ties.

    I just attended a NJDCA seminar on Framing Inspection and using a Checklist last week. That's how I know collar ties are not required here.

    http://www.nj.gov/dca/codes/forms/pd...gchecklist.pdf

    Here is the check list that all builders are required to fill out prior to calling for a framing inspection. He then hands the signed list to the building inspector and he conducts another inspection.

    Darren

    New Jersey Home Inspection - About the House!


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Rafters larger than ridge

    Quote Originally Posted by Darren Miller View Post
    That's what the code says; obviously it defines rafter ties.
    Actually, that does not define what a, nor state where a, "rafter tie" is or goes, other than "joists connected higher in the attic shall be installed as rafter ties".

    How high, within the bottom third (a rater tie), within the middle third (a whatever), within the top third (a collar tie)?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Rafters larger than ridge

    like this....


    Rich

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  15. #15
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Rafters larger than ridge

    Actually in NJ it does:

    "Where ceiling joists or rafter ties are not provided at the top plate, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice."

    The words "at the top plate" are in our code books.

    Darren


  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Rafters larger than ridge

    Quote Originally Posted by Darren Miller View Post
    Actually in NJ it does:

    "Where ceiling joists or rafter ties are not provided at the top plate, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice."

    The words "at the top plate" are in our code books.

    Darren
    No, that does not "define" "rafter ties", besides, you mis-quoted the section you provided, see below. (bold is mine)

    "Where ceiling joists are not connected to the rafters at the top wall plate, joists connected higher in the attic shall be installed as rafter ties, or rafter ties shall be installed to provide a continuous tie. Where ceiling joists are not parallel to rafters, rafter ties shall be installed. Rafter ties shall be a minimum of 2-inch by 4-inch (51 mm by 102 mm) (nominal), installed in accordance with the connection requirements in Table R802.5.1(9), or connections of equivalent capacities shall be provided. Where ceiling joists or rafter ties are not provided, the ridge formed by these rafters shall be supported by a wall or girder designed in accordance with accepted engineering practice."

    Darren, it's your code, but it does not say what you say it does, you are mixing parts of sentences with other parts of other sentences.

    *IS* there "definition" for "rafter ties"?

    Look in the definitions section. If your code is based on the ICC codes, that will be chapter 2, and Section 2 of other chapters.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Rafters larger than ridge

    Darren
    At the risk of sounding like a total "suck-up" listen to Jerry P as he has it right. He and I have had our disputes regarding code interpretations in the past, but this ain't one of them. If I had a nickle for every rafter tie somebody called a collar tie and visa-versa, deedle, deedle dum, da, da, dee....................!


    Jerry McCarthy
    Building Code/ Construction Consultant

  18. #18
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Rafters larger than ridge

    I have to agree with Jerry P. Another good point is that it is just good building practice.

    I have also seen them referred to as Collar beams.

    They tie the rafters and ridge together, reinforcing the roof frame and securing them against spreading outward.

    Scott Patterson, ACI