    Default Service Clearance

    What is the minimum clearance over a detached garge or other structure for a overhead service line. 18" or 3 feet? The service does not attach to the structure it passes over it. The roof on the detached garage is 4:12 and is metal. I hope someone can clear this up for me. Thanks

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Service Clearance

    Quote Originally Posted by allen elliott View Post
    18" or 3 feet? The service does not attach to the structure it passes over it. The roof on the detached garage is 4:12 and is metal.

    Clearance 'above' the 4/12 roof is 3 feet.

    Clearance 'above' the 4/12 roof at the final drip loop where it is attached to the mast and 'above the overhang' is 18 inches.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Service Clearance

    Allen

    Refer NEC 2005 Article 230-24 (A) and read exceptions.