 I found a house that installed weepholes
		It's nice to see weep holes/wick but do you think they could have installed them in the right place?

Similar Threads:
 - 
	03-27-2008, 04:02 PM #2
 Re: I found a house that installed weepholes
		Here's the picture.
 - 
	03-27-2008, 10:03 PM #3
 Re: I found a house that installed weepholes
		
 - 
	03-27-2008, 10:05 PM #4
 Re: I found a house that installed weepholes
		why?

 - 
	03-27-2008, 10:12 PM #5
 Re: I found a house that installed weepholes
		Because a window is basically just another hole in the wall where water seepage occurs quite often.
rick
 - 
	03-27-2008, 10:13 PM #6
 Re: I found a house that installed weepholes
		The are to help with any water/moisture that might seep in through the masonry around the windows. Then further down the wall as the brick joins the foundation you should see additional weeps.
Some AHJ's require weeps at just about every window and door opening in a home and some could care less about them.
 - 
	03-27-2008, 10:17 PM #7
 Re: I found a house that installed weepholes
		Shouldn't the flashing be visible beneath those weeps?
 - 
	03-27-2008, 10:19 PM #8
 Re: I found a house that installed weepholes
		Kevin,
Check out: BIA.org The tech notes have great diagrams or weep and flashing placement, etc.
 - 
	03-27-2008, 10:20 PM #9
 Re: I found a house that installed weepholes
		Nah, because it was probably never installed!
Sometimes you can see it and sometimes the mortar over it.
Weep holes are home inspection 101 basics. I would have thought that this was being taught in every HI school around the country. Y'all need to know about this stuff or it's going to get ya in trouble sooner or later.
 - 
	03-27-2008, 10:22 PM #10
 Re: I found a house that installed weepholes
		Referencing the 2003 IRC R703.7.6 then R703.7.5 then the location where flashing needs to be installed R703.8, there is no mention of flashing or weepholes under the window. Around here, I'm happy to see weep holes at all.
I'll check out the BIA.org. It will be interesting to read because at this time, I think their purpose of being there is pretty weak. But I like to think I have an open mind.
 - 
	03-27-2008, 10:33 PM #11
 Re: I found a house that installed weepholes
		
I think that it is coverd under the flashing section.
As I said it all depends on the AHJ and what they want.R703.7.6 Weepholes. Weepholes shall be provided in the
outside wythe of masonry walls at a maximum spacing of
33 inches (838 mm) on center.Weepholes shall not be less
than 3/16 inch (4.8mm) in diameter.Weepholes shall be lo-
cated immediately above the flashing.
R703.8 Flashing.Approved corrosion-resistive flashing shall
be provided in the exterior wall envelope in such a manner as
to prevent entry of water into the wall cavity or penetration of
water to the building structural framing components. The
flashing shall extend to the surface of the exterior wall finish
and shall be installed to prevent water from reentering the ex-
terior wall envelope. Approved corrosion-resistant flashings
shall be installed at all of the following locations:
1. At top of all exterior window and door openings in such
a manner as to be leakproof, except that self-flashing
windows having a continuous lap of not less than11/8
inches (28 mm) over the sheathing material around the
perimeter of the opening, including corners, do not re-
quire additional flashing; jamb flashing may also be
omitted when specifically approved by the building of-
ficial.
2. At the intersection of chimneys or other masonry
constructionwith frameor stuccowalls,with projecting
lips on both sides under stucco copings.
3. Under and at the ends of masonry, wood or metal cop-
ings and sills.
4. Continuously above all projecting wood trim.
5. Where exterior porches, decks or stairs attach to a wall
or floor assembly of wood-frame construction.
6. At wall and roof intersections.
7. At built-in gutters.
 - 
	03-27-2008, 10:41 PM #12
 Re: I found a house that installed weepholes
		I finally noticed that.
 - 
	03-27-2008, 11:23 PM #13
 - 
	03-28-2008, 06:59 AM #14
 Re: I found a house that installed weepholes
		
 - 
	03-28-2008, 09:13 AM #15
 Re: I found a house that installed weepholes
		I don't know what the deal is in my area, but weep holes are like .99cent gas... non-existent.
It must be an "east Texan" thang.
When I was building my home, I came in one day AFTER the brick mason was finished. I asked him where the weep holes were and he looked at me like I was a UFO. He said, "we don't do that anymore".
I fell out
 
and then got my drill and a masonry bit and proceeded to make my own (small as they are).
Bruce
We don't do that anymore, TX
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
 - 
	03-28-2008, 09:39 AM #16
 - 
	03-28-2008, 09:58 AM #17
 Re: I found a house that installed weepholes
		Scott,
Technical Notes
Under flashing and weeps (tech note 7b) they clearly indicate that the flashing should extend beyond the surface of the brick/ mortar the way I read it.
As far as weeps at windows.. good practice-- yes. Required... not according to the 2003 IRC if you believe in self flashing windows, and I can't tell you the last time I saw weeps at windows.
 - 
	03-28-2008, 09:59 AM #18
 Re: I found a house that installed weepholes
		
 - 
	03-28-2008, 10:19 AM #19
 Re: I found a house that installed weepholes
		
Brandon,
First, re-read that code. That is not what it says. Then, look at the drawing on the next page.
From the 2003 IRC. (underlining is mine)
- R703.8 Flashing.Approved corrosion-resistive flashing shall be provided in the exterior wall envelope in such a manner as to prevent entry of water into the wall cavity or penetration of water to the building structural framing components. The flashing shall extend to the surface of the exterior wall finish and shall be installed to prevent water from reentering the exterior wall envelope. Approved corrosion-resistant flashings shall be installed at all of the following locations:
- - 1. At top of all exterior window and door openings in such a manner as to be leakproof, except that self-flashing inches (28 mm) over the sheathing material around the perimeter of the opening, including corners, do not require additional flashing; jamb flashing may also be omitted when specifically approved by the building official.
- - 2. At the intersection of chimneys or other masonry construction with frame or stucco walls, with projecting lips on both sides under stucco copings.
- - 3. Under and at the ends of masonry, wood or metal copings and sills.
- - 4. Continuously above all projecting wood trim.
- - 5. Where exterior porches, decks or stairs attach to a wall or floor assembly of wood-frame construction.
- - 6. At wall and roof intersections.
- - 7. At built-in gutters.
That self-flashing exception ONLY applies to the TOP flashing.
 - 
	03-28-2008, 10:22 AM #20
 Re: I found a house that installed weepholes
		Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
 - 
	03-28-2008, 10:49 AM #21
 Re: I found a house that installed weepholes
		I would take that to mean no flashing is required around the window opening. Not saying I am right... just wish things were worded better.over the sheathing material around the perimeter of the opening, including corners, do not require additional flashing; jamb flashing may also be omitted when specifically approved by the building official.
Say there is no through wall flashing at the sill area of a window, and the housewrap and flashing was properly installed. Most of the water should drain down the backside of the brick veneer, and the water that seeps onto the housewrap should drain down the housewrap onto the through wall flashing at the base of the wall.... that water should then drain out of the wall cavity.
Nothing listed above is best practice, just bare min. standards being applied.
 - 
	03-28-2008, 11:02 AM #22
 Re: I found a house that installed weepholes
		No, that is not what it is saying.over the sheathing material around the perimeter of the opening, including corners, do not require additional flashing; jamb flashing may also be omitted when specifically approved by the building official.
It is saying flashing is required at the top of the window ... unless it is a self-flashing window which meets those requirements.
It is also saying that flashing is required at the jambs of the window ... unless the building official *SPECIFICALLY* approves it otherwise ... not 'approves it' by virtue of signing the inspection card, but *SPECIFICALLY* approves it.
Yeah, like deleting the part about the building official having the right to approve no jamb flashing.... just wish things were worded better.
 
You can say that, but one is required.Say there is no through wall flashing at the sill area of a window,
 
... if that flashing is installed ...and the housewrap and flashing was properly installed. Most of the water should drain down the backside of the brick veneer, and the water that seeps onto the housewrap should drain down the housewrap onto the through wall flashing at the base of the wall...
Yes, but why risk putting more water into the wall cavity than necessary, if, when done correctly, that will not happen.that water should then drain out of the wall cavity.
That's like saying the speed limit is 70 mph, but, if I drive careful, and there is little traffic, I might be able to drive 120 mph and never have an accident.
Yeah, maybe, but ... maybe not.
 - 
	03-28-2008, 11:46 AM #23
 Re: I found a house that installed weepholes
		Every time I read R703.8 I get confused on exactly what it says... I am not a code official and don't get paid to interpret the codes.
I may just write up the lack of flashing as being questionable at this location, and let the buyer know they would have to contact the AHJ to determine their take on it.
For the record, I hope you are right since it would be better to have the flashing at this location. It just seems dumb that they would allow head flashing to be omitted while requiring sill flashing beneath the windows... it doesn't make sense to me.
 - 
	03-28-2008, 03:03 PM #24
 Re: I found a house that installed weepholes
		Think of it this way ...
The head flashing is to keep the water out from getting into the top of the window.
With a self-flashed window, you don't have to worry about that ('should not have to' worry about that).
The sill flashing is a through the wall flashing and is intended to bring any water back out to the exterior face of the wall. Thus, because you have a rather large opening in the brick veneer (the window), all the water which passes through that opening (and hits the window) should be, to the best extent possible, taken back out to the exterior face of the brick veneer.
Sure, there is a weather resisting barrier, house wrap, (WRB) on the house, but you don't want anymore water on it than need be. The more water you keep off of it, the less chance there is of water penetrating through flaws in the WRB.
 - 
	03-29-2008, 07:59 AM #25
 Re: I found a house that installed weepholes
		These installation details have been around for a while.
Where did they drill the alarm sensor holes?
I hope not through the sill, like most that I see.
Window warranty shot along with any attempts at properly flashing the sill.
Last edited by BARRY ADAIR; 03-29-2008 at 08:08 AM.
badair http://www.adairinspection.com Garland, TX 75042
Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
life is the random lottery of events followed by numerous narrow escapes...accept the good
 - 
	03-29-2008, 09:15 AM #26
 Re: I found a house that installed weepholes
		While we're on this subject...what is the name of the product or group of products that looks like one-sided fly paper and is stuck above a door or window? It has an adhesive on one side and presses over the item to be flashed.
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
 - 
	03-29-2008, 09:18 AM #27
 Re: I found a house that installed weepholes
		
 - 
	03-29-2008, 11:11 AM #28
 Re: I found a house that installed weepholes
		Thanks.
So, (and I don't have a diagram) is it to be stuck over the building wrap or under?
The reason I'm asking is that I did some draw inspections yesterday on new const. I had seen the peel/stick flashing previously but not used in the same manner as I did yesterday.
I wish I had a picture but I was a long way from the truck.
 
I was over the building wrap and had been secured with nails and staples.
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
 - 
	03-29-2008, 07:25 PM #29
 Re: I found a house that installed weepholes
		Depends. (Dang, don't you hate answers like that?)
Some say 'over the building wrap', some say 'directly on the sheathing with the building wrap over it', some say either way, some 'allow' the other way not stated (i.e., at least one brand states 'directly on the sheathing with the building wrap over it and taped and sealed to it', then the manufacturer will send a letter stating it 'may be applied over the building wrap').
The best way to find out is to read of box left on the job, or, if nothing is left on the job, look the manufacturer up on the internet and look for installation instructions on their web site ... then call them and ask them (to verify that is what they really mean).The reason I'm asking is that I did some draw inspections yesterday on new const. I had seen the peel/stick flashing previously but not used in the same manner as I did yesterday.
 - 
	03-29-2008, 07:51 PM #30
 Re: I found a house that installed weepholes
		Bruce Thompson, Lic. #9199