    Default Honey, your hot bath is awaiting you

    The tub is almost full and ready for you dear.

    You need to turn off the light on the fan and get you some peace and quiet.

    I'm going out to clean out that garage your been complaining about.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Honey, your hot bath is awaiting you

    *IF* the bottom of the light globes are over 8' above the top of the tub, that installation is okay (presumably, thereby putting the ceiling fan 'out-of-reach').

    Looks like an 8' ceiling from the photo, so I'd say the bottom of the globes are only about 5' above the top of the tub ... if that high.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Honey, your hot bath is awaiting you

    Oh Gladys, while your taking a soak I'll take a nice hot shower!

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry McCarthy
    Building Code/ Construction Consultant

  4. #4
    jerry attaway's Avatar
    jerry attaway Guest

    Default Re: Honey, your hot bath is awaiting you

    Is the fan over the tub? 2006 NEC E3903.10 Exhibit 410.1 Bathtub Clearances


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Honey, your hot bath is awaiting you

    Quote Originally Posted by jerry attaway View Post
    Is the fan over the tub? 2006 NEC E3903.10 Exhibit 410.1 Bathtub Clearances

    You mean 2006 *IRC* E3903.10, right?

    That references the 8 feet height above the tub I mentioned in my post above - the NEC section is:

    2008 NEC
    - 410.10 Luminaires in Specific Locations.
    - - (D) Bathtub and Shower Areas. No parts of cord-connected luminaires, chain-, cable-, or cord-suspended luminaires, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the space directly over the tub or shower stall. Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Honey, your hot bath is awaiting you

    A visual flesh-out of Jerry's code quote:

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images