	03-12-2008, 11:50 AM #1 Entrance From Garage Entrance From GarageHello Everyone, 
 I know that the garage-dwelling door should not enter a bedroom due to the risk of vehicle fumes and/or fire entering the bedroom(s). But is it permissible to enter into a closet that is attached to the bedroom as seen in the photos? Garage to closet to bedroom.
 Similar Threads:
 
- 
	03-12-2008, 12:32 PM #2 Re: Entrance From Garage Re: Entrance From GarageAs long as there's a door between the closet and bedroom and the door opening from the closet into the garage is a 1-3/8" in thickness, solid-core or honeycomb core steel door, or a 20 minute fire-rated door. ref: 2006 IRC 309.1 and for the west coast; 2007 CBC 406.1.4. BTW, the first ICBO code published in California in 1927 stated the same that there shall be no direct opening between a garage and a sleeping room. #1505. 
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-12-2008, 12:37 PM #3 Re: Entrance From Garage Re: Entrance From GarageRon, 
 
 This is the 2006 IRC wording, my answer, and why my answer is that:
 
 - SECTION R309
 - - GARAGES AND CARPORTS
 - - - R309.1 Opening protection.
 Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.
 "Openings from a private garage directly into a room used for sleeping purposes shall not be permitted."
 No, that door is not allowed.
 The closet is part of the bedroom, it is part of what makes a room a 'bedroom', also, the closet, as part of a bedroom, requires AFCI protection for any and all circuits which have outlets in the bedroom (and closet).
 
 The simple solution is to make a 3' deep alcove with another door to the closet, separating the closet from the garage.
 
 Last edited by Jerry Peck; 03-12-2008 at 05:56 PM. Reason: speelin' 
 
- 
	03-12-2008, 01:31 PM #4 Re: Entrance From Garage Re: Entrance From GarageThanks for your quick response, both of you. I can now finish my report. 
 
 
- 
	03-12-2008, 03:26 PM #5 Re: Entrance From Garage Re: Entrance From GarageHow about if the "fire" door was between the bedroom and the closet? 
 
 
- 
	03-13-2008, 06:32 AM #6 Re: Entrance From Garage Re: Entrance From GarageJerry, I am surprised how lenient the IRC is on the door. Our Code also does not allow an exit path through a bedroom. However, our Code requires at least a B door or 3 hour steel door, (it's been a while, I don't remember exactly) between a DU and an attached garage. No wood door at all allowed I remember that for sure. Must also have rated jamb and rated self-closer and rated hinges. 
 
 
- 
	03-13-2008, 06:36 AM #7 Re: Entrance From Garage Re: Entrance From Garage
 Markus,
 
 The only reason to have a door like that would be if the wall itself is a "fire rated assembly", and to require a 3 hour rated door would indicate that was a 4 hour rated wall.
 
 I think you are thinking of something else ... could you go back and check it? Thanks.
 
 
- 
	03-13-2008, 12:35 PM #8 Re: Entrance From Garage Re: Entrance From GarageLet's talk about a walk-in bedroom closet separated from the bedroom by a door being considered an integral part of the bedroom? (sleeping room) 
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-13-2008, 05:00 PM #9 Re: Entrance From Garage Re: Entrance From Garage
 
- 
	03-13-2008, 05:15 PM #10 Re: Entrance From Garage Re: Entrance From GarageJust being silly Jerry. BUT, if one has to walk through a doored space into another doored space I miss the point of why you want to say the closet space doesn't count as a true separation from the garage to bedroom. Of course I'm assuming the door from the garage into the closet is a fire rated door, etc. 
 
 PS: I’m also aware there is no such word as “doored” but I know you get my drift.
 
 (this should make for a good discussion?) 
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-13-2008, 05:33 PM #11 Re: Entrance From Garage Re: Entrance From GarageJerry Mc., 
 
 If the closet space is considered part of the bedroom I don't see how the garage door would be allowed.
 
 Closet doors are changed or removed (mirrored ,bia., latts ect.)
 
 Please elaborate how the closet space is not considered part of a bedroom. 
 It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
 Billy J. Stephens HI Service Memphis TN.
 
- 
	03-13-2008, 05:37 PM #12 Re: Entrance From Garage Re: Entrance From GarageBecause the closet is part of the 'private bedroom' and many people leave "closet doors" open or ajar - as there is no real reason to close them. 
 
 Thus, you end up with a bedroom and its closet opening directly to the garage.
 
 The closet is 'part of' the bedroom, and no bedroom ("room used for sleeping purposes") is allowed to open directly to a garage - the 'part of the bedroom' which is a closet does (in this case) open directly to the garage, hence 'the bedroom' opens directly to the garage (which is not allowed).
 
 
- 
	03-13-2008, 06:30 PM #13 Re: Entrance From Garage Re: Entrance From GarageJerry, your answer was correct. The items I mentioned were for garage/repair shop separation. 
 On the DU/attached garage separation Chicago Code states:
 1 hr. separation, only one access door no more than 21 sqft in size, self-closing door not less fire-resistive than a solid wood door one and three-quarters inches thick; sill not less than 8 inches above the garage floor.
 Correction posted.
 
 
- 
	03-13-2008, 06:45 PM #14 Re: Entrance From Garage Re: Entrance From GarageJerry P said: “Because the closet is part of the 'private bedroom' and many people leave "closet doors" open or ajar - as there is no real reason to close them. Thus, you end up with a bedroom and its closet opening directly to the garage.” 
 
 I say: I cannot buy that argument in that many folks take the automatic closer, if there is one, off the door between the garage and house and leave it open a crack or even wide open. Is not a walk-in closet a separate space in an R-3 residential dwelling? If so how can a bedroom open directly into a garage when it actually opens into a closet that opens into a garage?
 
 I can't find any definitive reference in the codes to my dilemma and if you can I will stand corrected, chastised, ashamed, and suitably contrite.
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-13-2008, 06:53 PM #15 Re: Entrance From Garage Re: Entrance From Garage
 
- 
	03-14-2008, 04:40 AM #16 Re: Entrance From Garage Re: Entrance From GarageYes and? Come on JP, you can make a better argument than that. Until somebody shoots down my two doors between a bedroom and garage theory I'll stick to my argument. BTW, because somebody could possibly change a door or remove it doesn't fly with me.  
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-14-2008, 05:11 AM #17 Re: Entrance From Garage Re: Entrance From GarageTonight at 9:00, only on cable (hight speed internet). 
 It's "East Coast Jerry" vs "West Coast Jerry", in a no holds barred extravaganza, for the World Championship title.
 
 Brought to you by your friends at Hann Tech . 
 ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
 
- 
	03-14-2008, 05:42 AM #18 Re: Entrance From Garage Re: Entrance From GarageAND if the closet is considered part of the bedroom and requires afci for its electrical outlets AND if the bedroom is a habitable room, THEN lighting should be required for the closet!!! 
 
 
- 
	03-14-2008, 06:40 AM #19 Re: Entrance From Garage Re: Entrance From GarageThe idea of considering the closet or walk-in closet as a separate room between the bedroom/garage doesn't work at least on the following 2 points: 
 1- closet most likely doesn't meet minimum sqft requirements to be considered a habitable room;
 2- the bedroom is still within the exit path
 Trying to rationalize that the closet scenario is OK, is just that, rationalization (bullshit)
 so ...
 - why not cut another access into a hallway a few feet over?
 - make it an office until the deal is done?
 
 
- 
	03-14-2008, 12:15 PM #20 Re: Entrance From Garage Re: Entrance From Garage
 And ....
 
 That's because the closet *IS* 'part of the bedroom', hence, in referring to the bedroom, that includes the closet.
 
 Since 'the bedroom' is 'a room used for sleeping purposes' (that is what a bedroom is), 'the bedroom' would not be allowed to have a door,i.e., "an opening", here: "Openings from a private garage directly into a room used for sleeping purposes shall not be permitted."
 
 
- 
	03-14-2008, 02:00 PM #21 Re: Entrance From Garage Re: Entrance From GarageJP stated: "Openings from a private garage directly into a room used for sleeping purposes shall not be permitted." 
 JM says: The Key Word here is "directly" So in real life the door from the garage does not actually open directly into the bedroom, yes/no? 
 Jerry McCarthy
 Building Code/ Construction Consultant
 
- 
	03-14-2008, 04:23 PM #22 Re: Entrance From Garage Re: Entrance From Garage
 
- 
	03-15-2008, 07:19 PM #23 Re: Entrance From Garage Re: Entrance From GarageSheeeesh! Quible, quible. LOL 
 All I know is that if I leave MY closet door ajar I'll find all my shoes in the back yard. My dog is a thief!
 Dana
 True Professionals, Inc. Property Consultant
 877-466-8504
 
- 
	03-31-2008, 10:29 PM #24 Re: Entrance From Garage Re: Entrance From GarageJerry or one of the other Florida guys: 
 
 I did an inspection on a house last week that was built in 2003. Had a standard interior door from the garage to the house. I wrote it up as: "Openings between the garage and residence shall be equipped with solid wood doors not less than 1-3/8 inches in thickness, solid or honeycomb core steel doors not less than 1-3/8 inches thick, or 20-minute fire-rated door."
 
 The buyer called me today to verify this was code at the time of construction. Of course I told him a home inspection is not a code inspection and recommended the door be changed regardless. He still wanted to know. I have an IRC 2000 that verifies the requirement but not a FBC 2001. Do you know if the FBC 2001 had this requirement? If so what chapter and section?
 
 Thanks,
 
 Larry
 
 
- 
	04-01-2008, 05:46 AM #25 Re: Entrance From Garage Re: Entrance From GarageLarry, 
 
 Regarding "separation" - That was one of the things lost when Florida went to its first 2001 Florida Building Code:
 
 - §411.2.6 Automobile parking garages shall be separated from other occupancies in accordance with §704.
 - - EXCEPTION: Separation is not required between a Group R3 building and an attached garage.
 
 - R3: Residential occupancies including the following:
 - - Child care facilities which accommodate 3 or fewer children of any age for any time period.
 - - One-and two-family dwellings where the occupants are primarily permanent in nature and not classified as R1, R2 or I.
 - - Rooming houses (transient)
 - - Rectories, parsonages
 
 That said (regarding "separation"), that door needs to meet the same requirements of any other exterior door regarding separating the conditioned space from non-conditioned space and outdoors, i.e., it needs to be a solid wood or metal insulated door with weather stripping, threshold, etc.
 
 Ultimately, when they meet the above, they will also be meeting the requirements for "separation" in today's code.
 
 
- 
	04-01-2008, 08:48 AM #26 Re: Entrance From Garage Re: Entrance From GarageHey Jerry: 
 
 Thanks for the info; I will pass it along.
 
 Thanks,
 
 Larry
 
 


 
 
						
					
 
				
				
				
					 Reply With Quote
  Reply With Quote 
					
					 Originally Posted by Markus Keller
 Originally Posted by Markus Keller
					

Bookmarks