Results 1 to 24 of 24
  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default 3-wire dryer receptacle outlet

    Last edited by Jeff Eastman; 12-19-2007 at 04:32 PM.
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 3-wire dryer receptacle outlet

    Not 100% sure
    New dryers are 4 prong
    Older dryers were 3
    Same for stoves

    Most of the appliances that use 220 also have 110 circuits for the clock, and controls. In the past you would get the 110 off one leg and the ground, now with 4 prong you have a neutral and ground.

    So 3 prong outlet was correct, but should be changed to 4, if possible, may only have 3 wires.
    It does not HAVE be be changed to 4. but would be better as 4.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Jeff Eastman View Post
    I'm sure you will, but pipe up if I'm wrong!

    The 3-wire dryer receptacle outlets have one wire serving both as a neutral and an equipment ground. I consider this as a safety hazard and have been putting this a repair item in my reports. The electrician said it was okay and not a safety hazard. I think I'm right but will swallow my already beaten up pride if I must.
    Ask electrician why they are now required to be 4-wire, if 3-wire is ok.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Houston, Texas
    Posts
    294

    Default Re: 3-wire dryer receptacle outlet

    The four prong outlets with four wires are electrically safer. As Rcik points out though, you have to have four wires present if you want to upgrade to the 4 prong outlet (or be willing to run a new wire).

    The reasons that the four prong outlets are safer is the same reason you need a four wire feeder to electrical panels downstream of the service equipment. The only interconnection between the ground and neutral you want in your electrical system is at the service equipment.


  5. #5
    Bob Mayer's Avatar
    Bob Mayer Guest

    Default Re: 3-wire dryer receptacle outlet

    I believe the change from three to four wires started with the 1996 NEC.

    In the three-wire system there are (at least) two possible problems.

    1. There is relatively high resistance in the neutral line. To the extent that the neutral is carrying significant current (think the 115V drum motor in a dryer) there will be a voltage on the appliance frame equal to the voltage drop in the neutral line.

    2. There is an open in the neutral line. If one of the 115V devices is turned on you could have close to 115V on the appliance frame. This situation is why the neutrals on receptacle outlets in split circuits are required to be pigtailed and not just daisy-chained through the device.

    That said, the NEC folks took their sweet time to finally disallow 3-wire circuits, I guess there were few problems in real life.

    If the circuit were run before the 1996 NEC took effect I would make a comment, but say that upgrading is not required. If the circuit war run when the new rule was in force I would have a problem with that.

    - BOB


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Jeff Eastman View Post
    The electrician said it was okay and not a safety hazard.
    That answer (to some extent), as some have already pointed out, is that of timing.

    The answer (to the rest of the extent) is that the electrician is wrong, and, depending on what you said and your wording, you may also be wrong.

    First, let's take what the electrician said: "The electrician said it was okay and not a safety hazard."

    "The electrician said it was okay ... "

    It was, for eons.

    " ... and not a safety hazard." I was always a safety hazard. Always was, and, until those old ones are changed, always will be.

    No "upgrade", as Bob called it, is *ever* required. If the circuit 'should have been' run with 4 wires, then it 'shall' be replaced, meaning it is wrong, dead wrong.

    If the circuit 'was not required to have been' run with 4 wires, then it 'should' be replaced, meaning it is safer to replace it, however, *IF* it is a 3 prong plug for the range or dryer, *IT IS* most likely only wired with 3 wires, meaning that correcting it may not be real easy - all depends on where the dryer is located in relation to the panel.

    So, depending on 'how' you write them up, you could be right, or just partially right.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: 3-wire dryer receptacle outlet

    I don't have an issue with it, nor do I report if it is a 3 or 4 wire equipped receptacle. I don't consider a 3 wire system a safety issue either. But this is me, and your opinions may differ.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  8. #8
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 3-wire dryer receptacle outlet

    That brings up a question.
    You buy a house with the 3 prong outlets, and your stove and dryer are the newer 4 prong style. Is it allowed ( by code and/or manufacture) to install a 3 prong cord on the stove, dryer?

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  9. #9
    Bob Mayer's Avatar
    Bob Mayer Guest

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Rick Cantrell View Post
    That brings up a question.
    You buy a house with the 3 prong outlets, and your stove and dryer are the newer 4 prong style. Is it allowed ( by code and/or manufacture) to install a 3 prong cord on the stove, dryer?
    I do not know, but I believe that the answer is yes. Buying a new appliance does not require running a new cable from the panel to the receptacle outlet.

    - BOB


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 3-wire dryer receptacle outlet

    Bob,

    Rich said this:

    That brings up a question.
    You buy a house with the 3 prong outlets, and your stove and dryer are the newer 4 prong style. Is it allowed ( by code and/or manufacture) to install a 3 prong cord on the stove, dryer?
    Which means those circuits already 'have' the four prong receptacle, and, presumably, four wires.

    You said:
    Quote Originally Posted by Bob Mayer View Post
    I do not know, but I believe that the answer is yes. Buying a new appliance does not require running a new cable from the panel to the receptacle outlet.
    In answer to Rick's questions, if the receptacles are already four prong, then a four conductor cord and plug would be needed to install the range or dryer.

    I'm guessing that is what the manufacturer's installation instructions will say, and the code does not say that you may change the receptacle out to a three prong type from a four prong type. (But I could be wrong, I've been wrong before.)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 3-wire dryer receptacle outlet

    Jerry
    Thanks for answering, but you misread my question.
    3 prong receptacles
    4 prong cord

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Rick Cantrell View Post
    Jerry
    Thanks for answering, but you misread my question.
    3 prong receptacles
    4 prong cord
    Man I sure did. I must be losing my mind??? Can't seem to read anymore.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: 3-wire dryer receptacle outlet

    One of the reason that dryers and stoves don't come with the connecting wire and plug.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  14. #14
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: 3-wire dryer receptacle outlet

    A few years ago I bought a new dryer. The appliance company came out and installed the dryer. The dryer did not have a cord on it already. I noticed they brought with them both cords, 3 and 4 prong to use accordingly.


  15. #15
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: 3-wire dryer receptacle outlet

    What difference does it make if you have a 3 or 4 wire dryer if both of the wires go back to the *Service Equipment* panel and are bonded together there anyway.

    Now if the go back to a panel that is not *Service* then I would agree.

    Am I looking at this correctly or not???


  16. #16
    Bob Mayer's Avatar
    Bob Mayer Guest

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Tim Moreira View Post
    What difference does it make if you have a 3 or 4 wire dryer if both of the wires go back to the *Service Equipment* panel and are bonded together there anyway.

    Now if the go back to a panel that is not *Service* then I would agree.

    Am I looking at this correctly or not???
    There are two possible problems, which I mentioned in an earlier post.

    Quote Originally Posted by Bob Mayer View Post
    I believe the change from three to four wires started with the 1996 NEC.

    In the three-wire system there are (at least) two possible problems.

    1. There is relatively high resistance in the neutral line. To the extent that the neutral is carrying significant current (think the 115V drum motor in a dryer) there will be a voltage on the appliance frame equal to the voltage drop in the neutral line.

    2. There is an open in the neutral line. If one of the 115V devices is turned on you could have close to 115V on the appliance frame. This situation is why the neutrals on receptacle outlets in split circuits are required to be pigtailed and not just daisy-chained through the device.

    That said, the NEC folks took their sweet time to finally disallow 3-wire circuits, I guess there were few problems in real life.

    If the circuit were run before the 1996 NEC took effect I would make a comment, but say that upgrading is not required. If the circuit war run when the new rule was in force I would have a problem with that.

    - BOB
    In case 1. the problem is that the "ground" is also the neutral, there is current flowing through it, and the voltage at the "ground" point on the appliance frame is not the ground potential at the service because of voltage drop. With four conductors this is not a problem, because there is no current flowing through the ground conductor. The voltage here would probably be small, but real.

    In case 2. we violate your assumption "if both of the wires go back to the *Service Equipment* panel". If there is a break in the neutral circuit, There could be almost 115V on the appliance frame. This is a similar problem to losing the neutral on a split circuit or on the service except here the neutral, with the far from zero voltage, is on the appliance frame. (A friend called me out for an electrical problem last autumn, weird voltages all over. The neutral was open at the transformer.)

    - BOB


  17. #17
    Bob Mayer's Avatar
    Bob Mayer Guest

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Tim Moreira View Post
    What difference does it make if you have a 3 or 4 wire dryer if both of the wires go back to the *Service Equipment* panel and are bonded together there anyway.

    Now if the go back to a panel that is not *Service* then I would agree.

    Am I looking at this correctly or not???
    "Now if the go back to a panel that is not *Service* then I would agree."

    The only difference that makes is that the resistance in the neutral may be higher (case1.) and there are more points of failure for the neutral (case2.) In a properly (other than being 3-wire instead of 4-wire) operating system, it does not matter if the panel to which the circuit is connected is the service or not.

    - BOB


  18. #18
    John Steinke's Avatar
    John Steinke Guest

    Default Re: 3-wire dryer receptacle outlet

    It's not really an "either/or' issue.

    The old style ... neutral bonded to the appliance, three wire plug ... was, for the most part, safe enough. There was, nonetheless, a drive to change from this to the four wire plug, and with the neutral isolated from the case of the dryer.

    Earlier dryers had no need for a neutral ... everything was 240v- switches, timers, and all. For reasons on economy, manufacturers were able to use 120v timers, etc .... by simply using the appliance case as a neutral, as well as ground.

    Sure, the code says 'no objectionable current on the ground." Care to define 'objectionable?'

    For reasons that had absolutely nothing to do with dryers, the electrical trade began to recognize the need to connect the ground to the neutral at only one place- and that place was the service entrance. Many problems, many dangers, were corrected once this was done. Yet, we still had those three-prong plugs on the dryers and ranges.

    Still, for the typical romex-wired home, the "parallel path" created with this second neutral / ground connection was pretty much a non-issue. Make that a house wired in pipe, add a loose connection, have the dryer 'on' ... and you now have a section of the pipe that's "hot." Not a good situation.

    For the sake of consistency, it was decided to change over to four-prong plugs.

    More important than the type of plug is that the appliance be wired correctly for the plug that is used. If a four prong plug is used, yet the case is still bonded to neutral, this situation can still develop.
    The reverse situation is even more dangerous ... a three prong plug on an appliance whose case is not bonded. That could allow the case to become "hot."


  19. #19
    James Duffin's Avatar
    James Duffin Guest

    Default Re: 3-wire dryer receptacle outlet

    I believe 4 wire plugs for dryers and ranges was the code for mobile homes years before it was for code for non-metal housing. The more grounding paths the safer it should be in theory...


  20. #20
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 3-wire dryer receptacle outlet

    Calling it a repair, I don't think so. Though you might mention it has a 3 wire plug.

    Kinka of like 2 prong ungrounded receptacles. Calling to replace all the wiring is not the answer, making a notation that there are 2 prong outlets would be.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  21. #21
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 3-wire dryer receptacle outlet

    The Dryer (and/ or oven) outlet are wired for a 3 prong cord, for added safety newer homes have been wired with outlets that use a 4 prong plug. If your appliance cord does not match the outlet, have a qualified appliance repairman install the correct cord.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  22. #22
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: 3-wire dryer receptacle outlet

    Quote Originally Posted by Rick Cantrell View Post
    The Dryer (and/ or oven) outlet are wired for a 3 prong cord, for added safety newer homes have been wired with outlets that use a 4 prong plug. If your appliance cord does not match the outlet, have a qualified appliance repairman install the correct cord.

    Yea, but the ground plug is faced down on the 3 prong cord.


  23. #23
    Join Date
    Feb 2008
    Location
    High Point, NC
    Posts
    97

    Default Re: 3-wire dryer receptacle outlet

    This question is along the same thread, I think.
    Is there any need to replace one 4-prong cord (outlet has 4 vertical blades with one round prong) for a dryer if the GE dryer, newly purchased by a client, requires a 4-prong cord that has 3 vertical blades with 1 L-shaped prong. The property was built in 1998 and is a condo within a building with 12 separate units. Apparently, the electrical contractor used the 3 blade and one round prong outlet throughout and my client is being told by a GE appliance tech that the outlet must be converted to match the cord supplied by the manufacturer. There is some question as to whether the installed outlet is intended for a range/oven appliance instead of a dryer.
    Is there a difference in the amperage rating between an oven and dryer that requires the different outlet/plug configuration for recognition?
    I have not found any reference to outlet prongs for appliance cording. The closest reference I have found in the IRC is Table 3809.2 regarding maximum loads per conductor size. Any help is appreciated.

    Last edited by Tom Edwards; 07-17-2009 at 06:15 AM. Reason: corrected 4 blade and one roung prong to 3 blade and one round prong

  24. #24
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 3-wire dryer receptacle outlet

    Tom,

    It is best to NOT post duplicate threads, that the best that spreads answers out between threads, at the worst they don't get answered.

    Here is the answer ... at your OTHER post: http://www.inspectionnews.net/home_i...r-circuit.html

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •