Buried ground wire
Found this on an inspection today. I pulled on the ground wire to make sure it was properly secured to the ground rod and found there was no ground rod. I pulled up about 5 feet of wire before I gave up and decided to stop trenching the yard. I'm still courious to know how much wire is buried. Anybody seen anything like this? If so, how is it written up? Thanks in advance for the help.
Similar Threads:
-
05-22-2008, 07:05 PM #2
Re: Buried ground wire
Come on Scott, what did you do to their electrical system, it was fine until YOU showed up!
Seriously, Just tell them the wire is supposed to be connected to a ground rod and get a real electrician to fix it.
By the way, if you plan on doing that, keep your life insurance paid up, you might become the ground electrode.
-
05-22-2008, 07:07 PM #3
Re: Buried ground wire
Umm... ground ring?
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
05-22-2008, 07:29 PM #4
Re: Buried ground wire
Scott,just a note I quit pulling on ground wires years ago;that connection should be abve grade anyway,so if it is not report it as so.

-
05-22-2008, 07:33 PM #5
Re: Buried ground wire
Hey Jim,
I'm sure my wife would love that insurance check! I know 20 feet of #4 Cu wire in the foundation footing will serve, but this looked like it was just buried out in the yard. Just curious if anyone else had seen this. Thanks for the help.
-
05-22-2008, 07:38 PM #6
Re: Buried ground wire
Hey Randy,
Thanks. O.k., no more pulling ground wires- I promise. I did test it with the hot-stick first, but I see your point. Thanks again.
-
05-22-2008, 08:22 PM #7
Re: Buried ground wire
Scott,
It is quite possible that where you stopped is where it goes down to a ground rod.
Gunnar brings up the interesting, and seldom understood, "ground ring".
Here is the code on it:
(4) Ground Ring. A ground ring encircling the building or structure, in direct contact with the earth, consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 2 AWG.
What is the minimum length of wire needed for the ground ring?
-
05-22-2008, 10:08 PM #8
-
05-23-2008, 06:01 AM #9
Re: Buried ground wire
Brandon,
Correct, but do you know how many inspectors and electricians miss that first part ... "encircling the building or structure" ... most.
Okay, let's back this up to the "consisting of at least 6.0 m (20 ft) of" part, what size "building or structure" could fit within that 20 feet of ground ring? Assuming that it is laid out in a circle (which gives the most area for the perimeter), that 20 feet would only encircle a round building or structure just over 6 feet in diameter.
Thus, most will say that it only needs to be 20 feet long.
-
05-23-2008, 08:22 AM #10
Re: Buried ground wire
Yep. I figured that was where you were headed with that question.
The loop has to go around the entire building. That 20 foot minimum would only work on a tiny building ... about 5' x 5' square or 6' round ... maybe something like a pumphouse.
-
05-23-2008, 05:20 PM #11
Re: Buried ground wire
Seems to me that a ground rod would be cheaper than 20' of 2 AWG, not to mention the amount that it would take to encircle the structure.
I guess that there are applications for it though (shallow bedrock, rocky soil, etc.).
-
05-25-2008, 04:55 AM #12
Re: Buried ground wire
Be careful pulling up copper wires. You might get mistaken for being a thief! In my jurisdiction houses under construction are having the copper cut out of them, as well as having the HVAC compressors stolen.
Travis Grubbs
-
05-27-2008, 12:56 PM #13
Re: Buried ground wire
Or as I tell my ECs " If I can't see the connection then it must not be there". After all who wants to see an inspector digging around in the mud looking for the end of a ground rod? All you contractors just keep quiet!

-
05-27-2008, 02:19 PM #14
Re: Buried ground wire
Shannon,
That's what we did in South Florida and I did up here ... "I can't tell you *how* to do it, but *if it were me* ... *I* ... would cut off about a 6" long piece of 4" pvc, dig out around the ground clamp at the ground rod, and drive that piece of pvc in so it is flush with the top of the sod, that way, *I as the inspector* could see the connection when you call in for the inspection.".
Works too.