    Default Ventless gas log set or not?

    Inspected a masonry fireplace in the basement with gas log set. Chimney flue was blocked (plywood) and damper closed. Can't tell if the gas log set is ventless or not....help?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    RJDalga
    http://homeanalysts.com
    Kalamazoo, MI

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Ventless gas log set or not?

    Quote Originally Posted by Robert Dalga View Post
    Chimney flue was blocked (plywood) ...
    Robert,

    Regardless whether it was vented or not, that plywood is combustible ... but you already knew that.

    There will be some metal tags attached (usually by a chain) to it with information and warnings, and will state what it is (vented or ventless) ... no metal tags attached and it is "nothing" ... as in 'it is not listed or labeled nor suitable for use without those tags and that information'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Ventless gas log set or not?

    The wood is a giveaway that this is not right. As Jerry said, look for the tag on a chain or wire cable. Just looking at that unit I would say it is a ventless that will produce enough heat to cook that plywood.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Ventless gas log set or not?

    Looks like a typical ventless unit. Every unit I've seen always had the metal tags with info attached. If they are gone. Defect the unit. Plywood closure sounds like another DIY. Probably removed the tags because he didn't like the look of them.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Talking Re: Ventless gas log set or not?

    Just burn them for a little while and they will become vented logs....

    BTW, the listing on the tag would read ANSI Z21.11.2 for ventfree, Z21.84 for match lit vented and Z21.60 for regular vented logs.