  1. #1
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Lightning Protection System quesion

    While at a home performing an exterior inspection as part of an indoor air quality investigation, I noted this curious connection of the LPS.

    The attached photo shows a part of the LPS bonded to the liquid line of the A/C system.

    Would this be a typical set up?
    Of the few LPS's I've observed I've never seen this connection.

    Thoughts?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Lightning Protection System quesion

    Quote Originally Posted by Dave Hahn View Post
    While at a home performing an exterior inspection as part of an indoor air quality investigation, I noted this curious connection of the LPS.

    The attached photo shows a part of the LPS bonded to the liquid line of the A/C system.

    Would this be a typical set up?
    Of the few LPS's I've observed I've never seen this connection.

    Thoughts?
    Man, that is way outside the scope of a normal home inspection. Unless you are very familiar with such a system I would not even offer an opinion on it. I would note that the home has it and that I don't know anyting about this and that they need to contact a person who is knowledgeable about lighting protection systems for any additional information.

    I'm working as an EW right now on a case for the plaintiff in which their home inspector did not know anything about a system in/on their new home and described it as being in excellent condition when in fact it was improperly installed and in very poor condition!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Re: Lightning Protection System quesion

    Scott...

    While I agree that evaluating something like this is WAY outside of a normal home inspection, if you would have read my post I was NOT performing a "home inspection."

    Having seen something during the course of a "non-home inspection" I took note of something I'm unfamiliar with. I made no mention of "reporting" it.

    Wanting to learn something, I thought I'd post my observation here.

    Anyone with info on LPS systems, your feedback is welcome.

    Dave


  4. #4
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Lightning Protection System quesion

    I don't know about LPS but grounding the refrigerant line set, makes as much sense as grounding CSST. Both are metal tubeing running thru the attic! Sounds like a good idea to me.


  5. #5
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Re: Lightning Protection System quesion

    Vern...

    Don't see that you're a member of the North Carolina Licensed Home Inspector Assocation (NCLHIA), but just two months ago we (the Charlotte Chapter) had a good speaker on the "bonding" of CSST. You might have considered changing your tune if you werre in attendance.

    We have varying guest speakers from month-to-month (second Tuesday night ea. month) covering a variety of topics. That, and the continuiing ed. credit seminars put on by NCLHIA make it worth while joining (www.NCLHIA.com).

    Dave


  6. #6
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Lightning Protection System quesion

    just two months ago we (the Charlotte Chapter) had a good speaker on the "bonding" of CSST. You might have considered changing your tune if you werre in attendance.
    So what did they say that would make me think bonding (grounding) CSST or a metal lineset is a bad idea?


  7. #7
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Lightning Protection System quesion

    Two questions Just curious

    First (both questions to Dave Hahn)

    "So what did they say that would make me think bonding (grounding) CSST or a metal lineset is a bad idea?

    Second

    North Carolina Licensed Home Inspector Assocation

    If you are all licensed why have the "Licensed" in your associations name?Does your association have anything to do with the actuall licensing?

    Just curious with both questions

    Ted


  8. #8
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Lightning Protection System quesion

    Quote Originally Posted by Dave Hahn View Post
    Vern...

    Don't see that you're a member of the North Carolina Licensed Home Inspector Assocation (NCLHIA), but just two months ago we (the Charlotte Chapter) had a good speaker on the "bonding" of CSST. You might have considered changing your tune if you werre in attendance.

    We have varying guest speakers from month-to-month (second Tuesday night ea. month) covering a variety of topics. That, and the continuiing ed. credit seminars put on by NCLHIA make it worth while joining (www.NCLHIA.com).

    Dave
    .
    This one works.
    North Carolina Licensed Home Inspectors Association - NCLHIA
    .
    Would not want this Set-Up.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Billy Stephens; 06-17-2008 at 07:29 PM. Reason: Phtos