GE 30 amp slim type breaker
I inspected a GE panel yesterday that had a single 30 amp slim type breaker supplying a standard 3 prong 4 receptacle outlet. I was unable to locate anything in the NEC and have never seen this before except to a dedicated single outlet for an appliance or tool.
Any help is appreciated!
Similar Threads:
-
07-23-2008, 07:35 AM #2
Re: GE 30 amp slim type breaker
Phil,
I suspect you are referring to double-gang duplex grounded receptacle outlets (3 prong = grounding type and 4 receptacle = 2 duplex).
There is nothing wrong with that provided that the breaker is in the appropriate space in the panel. Typically, they manufacturer specifies which spaces are allowed to have those breakers installed, and it could be any of all the spaces, or it could be limited to just certain spaces.
You would need to look at the wiring schematic on the panel (typically on the cover) and read what it states.
-
07-24-2008, 07:01 AM #3
Re: GE 30 amp slim type breaker
Sounds like overfusing if wire is 12 or 14 gauge. And regular 120v receptacle is rated only for 15 or 20 amps.
-
07-24-2008, 09:14 AM #4
Re: GE 30 amp slim type breaker
-
07-24-2008, 02:34 PM #5
Re: GE 30 amp slim type breaker
The only time I see a 120v 30 amp receptacle is for a window AC that was rated as such and is long gone. On 10 ga.
NEMA chart:
VOLTEC INDUSTRIES - Nema Chart
-
07-24-2008, 03:22 PM #6
Re: GE 30 amp slim type breaker
Good catch Phil...
A 30 amp breaker needs 30 amp wire and a 30 amp receptacle. The receptacle also needs to be the correct voltage configuration.