    Default TPR discharge pipe

    Tell me this is wrong. I'm refering to code check (IRC 2803.6.1 and UPC 608.5). AS you can see this was an approved installation.
    Rich

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: TPR discharge pipe

    " THIS IS WRONG" cannot be facing up. Must be able to see termination also. Could you?


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: TPR discharge pipe

    That NM cable is wrong too.

    Looks like that is in a closet, in which case it would also require a disconnect to disconnect the water heater from its supply. (There is an exception for the disconnect, but with what is shown in that photo, I doubt it applies.)

    Is that discharging into PVC in the corner behind the water heater? If so, that is not allowed either.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Joshua Hardesty's Avatar
    Joshua Hardesty Guest

    Default Re: TPR discharge pipe

    Wow. That's a whole lot of effort to do something completely wrong.

    The icing on the cake, though, are the two APPROVAL stickers on the side of that thing.