    Hello, I have a question. If the lable plate on the ac compressor states max amp 30, is it acceptible to install a 40 amp breaker in the breaker panel? The builder says its okay to do so. Anyone have any thoughts on this. Thanks, BigCid

    Similar Threads:
    Member Benefits1

  2. #2
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: a/c compressor max Amp rating

    Breakers trip at about a 30 percent draw over the rated breaker. If it is already 10 amp over some serious damage could come to the unit No it is not alright. They don't list max breakers just to have a number on there. It is to protect the unit and system. Tell the builder politely to get a clue and do what is right.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Alan Miles View Post
    If the lable plate on the ac compressor states max amp 30,

    Alan,

    Ask the builder to explain to you what "maximum" means, as related to something they should understand.

    Start with something simple like: What is the maximum amount of liquid you can put into a one gallon jug?

    Then proceed to something more complicated, such as: What is the maximum you can build your building to if restricted to a 35 foot maximum height?

    Then ask him to read the label and explain what it means when it says "max amp 30".

    See if he gets it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: a/c compressor max Amp rating

    This is one of the most common electrical defects here in GA. New homes or existing. There was only one time I that I can recall that the breaker did not meet the minimum size requirement on the AC nameplate.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Hank Spinnler View Post
    This is one of the most common electrical defects here in GA. New homes or existing. There was only one time I that I can recall that the breaker did not meet the minimum size requirement on the AC nameplate.
    Typically, there is no "minimum size" for the breaker.

    There is, however, a "minimum size" for the conductors.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Jerry Peck View Post
    Typically, there is no "minimum size" for the breaker.

    There is, however, a "minimum size" for the conductors.
    With out thinking to hard I cannot remember the last time I did not see a minimum and maximum breaker listed on an AC unit. Evryone That I ever recall (maybe) have listed min and max. Min being the smallest rating to operate the unit


  7. #7
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: a/c compressor max Amp rating

    This is typically what I see.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    John,

    That's what I usually see too:

    Minimum circuit ampacity

    Maximum fuse or HACR breaker ampacity

    I do recall, vaguely, having seen one or two which did state a minimum breaker size ... I think ... but cannot swear to it ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: a/c compressor max Amp rating

    Alan, your original question was a simple question. Now, we are discussing minimum ampacity rating vs. minmum circuit breaker rating on an AC unit. I looked back at photos of nameplates my most recent inspections and could not find any minimum circuit breaker rating listed, just minimum ampacity. I delved a little further onto a couple websites and found some interesting information to help in our understanding:

    July-August 1999: Air Conditioning & Heat Pump Equipment

    A/C Electrical [Archive] - DoItYourself.com Community Forums


  10. #10
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: a/c compressor max Amp rating

    The IAEI article as a .pdf for anyone who want a reference copy for thier PDA/Tablet/PC:

    Attached Files Attached Files
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  11. #11
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: a/c compressor max Amp rating

    Hi Michael. I was not able to open it. There was an error on the pages. Can anyone else see it?


  12. #12
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Hank Spinnler View Post
    Hi Michael. I was not able to open it. There was an error on the pages. Can anyone else see it?
    I had no problem downloading it with Firefox.


  13. #13
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: a/c compressor max Amp rating

    I would like to correct what Istated above. Most of the newer units I inspect have a max and min breaker listed. The older units have max breaker and min circuit amps.


  14. #14
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: a/c compressor max Amp rating

    Opens for me in the Foxit .pdf reader from within IE 8 Beta.

    Last edited by Michael Thomas; 10-26-2008 at 03:43 PM.
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  15. #15
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: a/c compressor max Amp rating

    Here's an example from an inspection a few weeks ago that listed the Minimum Fuse or Circuit Breaker size in addition to the other information.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  16. #16
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: a/c compressor max Amp rating

    It acceptable by NEC IF. At the unit if there is a fusible disconnect in the rating range per the nameplate .If there is only a disconnect at the unit it a violation.


  17. #17
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: a/c compressor max Amp rating

    Richard, care to post references and explanation about what "it" is that you are talking about?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    Richard,

    I'm with Jim, I have no idea what you are saying is right, wrong, allowed or not allowed in your post.

    The label Hank posted shows the following *requirements*:
    - *MINIMUM* circuit ampacity is required to be at least 19 amps
    - *MAXIMUM* overcurrent protection allowed is 30 amps
    - *MINIMUM* overcurrent protection size is 35 amps

    That label Hank posted also shows the following *allowances*:
    - *ANY* circuit ampacity over 19 amps is allowed
    - *ANY* overcurrent protection size between, and including, 25 amps to 30 amps is allowed

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: a/c compressor max Amp rating

    over current device is fuse or breaker or both.. so when I see both , and the lower rated breaker or fuse is the maximum allowed.. I accept that .the AC is protected..
    It's easy to miss because some fused disconnects have fuses behind a plastic panel that is screwed shut. I have found out you can't just look at them and tell.


  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Richard Pultar View Post
    It's easy to miss because some fused disconnects have fuses behind a plastic panel that is screwed shut. I have found out you can't just look at them and tell.
    Hopefully we are all taking those plastic covers off to look inside.

    Also, most of those have no fuses, they are simply "disconnects", *not* "fused disconnects".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: a/c compressor max Amp rating

    Richard, I think I understand... maybe.
    Are you cautioning to make sure there is both a disconnect AND an over current protection device as called for on the unit name plate, not just a disconnect switch?

    To clarify my understanding of the code, there must be a disconnect switch at the unit but the properly sized over current device can be either at the unit as part of the required disconnect or in the main panel.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  22. #22
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: a/c compressor max Amp rating

    exactly


  23. #23
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: a/c compressor max Amp rating

    Quote Originally Posted by Jim Luttrall View Post
    Richard, I think I understand... maybe.
    Are you cautioning to make sure there is both a disconnect AND an over current protection device as called for on the unit name plate, not just a disconnect switch?

    To clarify my understanding of the code, there must be a disconnect switch at the unit but the properly sized over current device can be either at the unit as part of the required disconnect or in the main panel.
    Quote Originally Posted by Richard Pultar View Post
    exactly

    Richard,

    "exactly" to which?

    While both of Jim's statements are correct, the first statement is only correct as far as it goes, the latter statement is fully correct.