Results 1 to 25 of 25
  1. #1
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default shake roof/ no drip edge

    Florida house
    no drip edge metal; 24 in shake with 10 in. exposure; felt paper layered at each row of shakes; 5/8 plywood decking.

    my question is the amount of overhang of the shakes at the rakes and eaves? as far as i know edge metal is not a requirement?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: shake roof/ no drip edge

    In my opinion and geographic location, I have never seen a drip edge on shake roof. There is plenty of overhang.

    Cheers,


  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Jerome W. Young View Post
    Florida house
    no drip edge metal; 24 in shake with 10 in. exposure; felt paper layered at each row of shakes; 5/8 plywood decking.

    my question is the amount of overhang of the shakes at the rakes and eaves? as far as i know edge metal is not a requirement?

    Well for one thing a 10" exposure is wrong. Depending on the grade of shingle and the slope of the roof you should not have more than a 71/2" exposure on a 24" shake.

    The main purpose of a metal drip edge is to support the shingles so that the water "drips" off the edge. We have all seen roofs without a metal drip edge and how those composition shingles droop and the water then runs down the fascia, etc. With shake shingles they don't need this type of support, they are not flexible like a composition shingle.

    In FL, you might have a requirement for a metal drip edge as this is part of the wind resistance system for the room.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default Re: shake roof/ no drip edge

    Scott
    thanks

    24 in = 10 in. exposure according to what i have researched
    18in= 7in exposure


  5. #5
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: shake roof/ no drip edge

    The species and type of wood and thickness composing the shake roof will also factor in as to exposure. Is this shake or simply wood shingles?

    The fact the wood shingles are laid on plywood decking will shorten the life in half.


  6. #6
    David Banks's Avatar
    David Banks Guest

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Raymond Wand View Post
    The species and type of wood and thickness composing the shake roof will also factor in as to exposure. Is this shake or simply wood shingles?

    The fact the wood shingles are laid on plywood decking will shorten the life in half.
    I would think the sun in Florida would shorten the life in half? Maybe down to one quarter.


  7. #7
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: shake roof/ no drip edge

    I understand that some insurers are also kicking up a fuss about wood roofs due to fire issues?


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Jerome W. Young View Post
    24 in = 10 in. exposure according to what i have researched
    18in= 7in exposure
    Depends on the wood species.

    From the 2004 FBC-Residential, Table R905.8.6

    Shakes of naturally durable wood - 24" length, No. 1 grade = 10" exposure
    Shakes of naturally durable wood - 24" length, No. 1 grade = 7-1/2" exposure for 3/8" hand split shakes

    Preservative-treated taper sawn shakes of SYP - 24" length, No. 1 grade = 10" exposure
    Preservative-treated taper sawn shakes of SYP - 24" length, No. 2 grade = 7-1/2" exposure

    Taper-sawn shakes of naturally durable wood - 24" length, No. 1 grade = 10" exposure
    Taper-sawn shakes of naturally durable wood - 24" length, No. 2 grade = 7-1/2" exposure

    Wood shingles are another matter, with 24" shingles having an allowed exposure between 5" (No. 3 grade) to 5-1/2" (No. 2 grade) to 5-3/4" (No. 1 grade) on 3/12 to >4/12 slopes, and an allowed exposure between 5-1/2" (No. 3 grade) to 6-1/2" (No. 2 grade) to 7-1/2" (No. 1 grade) on 4/12 and greater slopes.

    Quote Originally Posted by Raymond Wand View Post
    The species and type of wood and thickness composing the shake roof will also factor in as to exposure. Is this shake or simply wood shingles?
    Correct - see above table.

    The fact the wood shingles are laid on plywood decking will shorten the life in half.
    In Florida, most of Florida requires solid sheathing, structural panel sheathing, for sufficient strength to resist the wind loading from those high wind events Florida gets.

    Not sure if it reduces the life of them or not.

    Quote Originally Posted by David Banks View Post
    I would think the sun in Florida would shorten the life in half? Maybe down to one quarter.
    Maybe even less than 1/4. The sun really kills them in South Florida. Jerome is just north of the north end of what is considered 'South Florida', the sun is not as brutal there, but I would still imagine a greatly reduced life expectancy, maybe reduced by half.

    Wood shingles and shakes are definitely NOT the best choice for roofing material in Florida, especially in the southern half of the state, and critically so in the lower 1/4 of the state. Florida spans from Tropical to Temperate zones with the lower Keys being in the Tropical Zone, South Florida being in the Sub-Tropical zone, North Florida being in the Temperate Zone, and Central Florida spanning the vague change over from Sub-Tropical to Temperate.

    Wood shingles and shakes may do well in North Florida, they do very poorly in South Florida, and mixed results between the two - Jerome inspects around where the north end of South Florida and the south end of Central Florida meet.

    Back to the drip edge, or lack thereof ...

    Unless it is stated in the manufacturer's installation instructions, I don't see it in the code, however, those manufacturer's installation instructions would need to be approved for the wind speed zone you are in, which would 'most likely be' either 130 mph or 140 mph. I'm not sure that wood shingles or shakes are rated and approved for those wind speeds. You would need to check the product approvals on them.

    Nothing is easy in Florida, is it?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: shake roof/ no drip edge

    What a waste of resources not to mention the cost.

    For wood shingles to last, they have to breath. If placed on plywood sheathing they never dry out as well as those placed on purlins which allow the two sides to dry equally. However considering Florida is hurricane territory I can see the reason for solid sheathing.

    Also the steeper the roof pitch the greater the exposure can be.


  10. #10
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: shake roof/ no drip edge

    I'm for a Thatched Roof! Now that would be fun in Florida!

    Might work well in some parts of the country. Heck, they have worked well in many parts of Europe for hundreds of years!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  11. #11
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: shake roof/ no drip edge

    Like this one? It must take a while to learn how to do this.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jim Robinson
    New Mexico, USA

  12. #12
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Jim Robinson View Post
    Like this one? It must take a while to learn how to do this.
    When houses had thatched roofs, thick straw-piled high, with no wood underneath. It was the only place for animals to get warm, so all the cats and other small animals (mice, bugs) lived in the roof. When it rained it became slippery and sometimes the animals would slip and fall off the roof. Hence the saying . It's raining cats and dogs.



  13. #13
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: shake roof/ no drip edge

    Thatched roofs are a perfect example of how the blind allegiance to almighty code is over kill. If you don't like like the idea that the roof is not code proper don't buy the house. For the code to prohibit such a wonderful roof is a shame.


  14. #14
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: shake roof/ no drip edge

    When installing wood shingles or shakes over plywood use a breather underlayment. Example of one type of alternative system

    Cedar Breather Underlayment from Benjamin Obdyke


  15. #15
    Christopher Gorton's Avatar
    Christopher Gorton Guest

    Default Re: shake roof/ no drip edge

    Direct from the cedar council on the installation of cedar shingles is, use no field underlayment. This is on a new home in the south east US
    Mount it straight to the plywood with a run of paper over the eaves and one up the rake.
    I looked at that breather product as well, before I contacted the cedar representatives, as it seemed to make sense to keep some kind of airflow underneath the wood. The install directions said no.
    I would imagine there are very specific nailing patterns for higher wind zones, if that is in fact an acceptable roof covering at all in those areas.


  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Richard Pultar View Post
    Thatched roofs are a perfect example of how the blind allegiance to almighty code is over kill. If you don't like like the idea that the roof is not code proper don't buy the house. For the code to prohibit such a wonderful roof is a shame.
    Richard,

    I find it hard that a home inspector says the things you do.

    I can only imagine the houses your clients buy and the condition they are likely in.

    It is a disgrace to the home inspection profession to have such an attitude.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: shake roof/ no drip edge

    Jerry,

    I'm not sure what code thatched roofs violate???

    We have a large retail store with a wonderful thatched roof. The owner flew tradespeople from Ireland along with thatching for this project. It was built approx. 7+/- years ago. There was no problem building this one.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: shake roof/ no drip edge

    Ken,

    This was the part of Richard's post I was referring to. He has made a few posts with the same 'screw the code, do what you want' attitude.

    Quote Originally Posted by Richard Pultar View Post
    allegiance to almighty code is over kill.
    In one electrical post he suggested something truly absurd, which I do not remember right now.

    Quote Originally Posted by Ken Amelin View Post
    I'm not sure what code thatched roofs violate???
    Basically all code sections except this one:
    From the 2006 IBC. (not posting the entire sections)
    - 104.11 Alternative materials, design and methods of construction and equipment.
    - - 104.11.1 Research reports.
    - - 104.11.2 Tests.

    If the above is followed, then it "meets code" without actually "meeting code".

    Last edited by Jerry Peck; 11-21-2008 at 07:13 PM. Reason: speelin': I had "note" instead of "not"
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    christopher bittner's Avatar
    christopher bittner Guest

    Default Re: shake roof/ no drip edge

    to all: those thatched roofs are splendid indeed. I don't
    think that there is any issue with the roof and and as Richard said if the client likes it why not. I do some simple quick homework for the client. Simple. All this stuff is not that complicated. Wood shingles use a starter course which is suitable and durable without need for a drip edge. ( they been putin' em up along time before i was around). A rake moulding can be installed on what appears to be a 1x10 rake. Often a simple piece of 1x2. Other mouldings are more pleasing to the eye- My favorite is "Whale Back".
    My friend from Cap Cod certainly has an idea about Mass. requirements for shingled roofs as well as my friend from Canada. Chris Bittner


  20. #20
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: shake roof/ no drip edge

    RE: wood shake roof covering. I have never figured out why anyone in their right mind would have kindling installed on their roof tops? Many of our local jurisdictions have outlawed such by passing city ordinances. Thatched roofs? I'm not even going there.

    Jerry McCarthy
    Building Code/ Construction Consultant

  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Jerry McCarthy View Post
    RE: wood shake roof covering. I have never figured out why anyone in their right mind would have kindling installed on their roof tops?

    Thatched roofs? I'm not even going there.
    WC Jerry,

    Well, apparently several inspectors here think that thatched roofs are okay ... ... I look at thatched roofs as the 'easily ignitable matter' used to light off your kindling wood shake roofs.

    First, you get a spark glowing in the 'easily ignitable matter', then blow on it until it becomes a flame, then add some kindling ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Jerry McCarthy
    RE: wood shake roof covering. I have never figured out why anyone in their right mind would have kindling installed on their roof tops? Many of our local jurisdictions have outlawed such by passing city ordinances. Thatched roofs? I'm not even going there.


    [COLOR=#000080]
    Quote Originally Posted by [/COLOR
    Jerry Peck]Well, apparently several inspectors here think that thatched roofs are okay ... ... I look at thatched roofs as the 'easily ignitable matter' used to light off your kindling wood shake roofs.

    First, you get a spark glowing in the 'easily ignitable matter', then blow on it until it becomes a flame, then add some kindling ...


    To the Jerry's - What are you both thinking about???
    I agree that thatched roofs are a thing of the past, but wood roofs are here to stay. They've been around for century's. They are durable, energy efficient, have visual appeal and they are green.

    DO YOU THINK THAT ASPHALT ROOF ARE LESS FLAMMABLE??? -- HELLO!!

    or are you both just trying to pass the time away and complain about something?

    Come on now folks.


  23. #23
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: shake roof/ no drip edge

    Interior and exterior sprinklers, no problemo. Well, maybe a little bug killer would be in order

    Can you see all those wonderfull big roaches and tree rats living in them.


  24. #24
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: shake roof/ no drip edge

    Quote Originally Posted by Ken Amelin View Post
    I agree that thatched roofs are a thing of the past, but wood roofs are here to stay. They've been around for century's.
    Thatched roofs and mud huts have been around longer than wood roofs ... what is your problem with them, why are you not saying that "They've been around for century's." and that they "are here to stay"?

    Surely you are not deriding one very old method which has been around longer (thatched roofs) to justify accepting a much younger and newer roofing method (wood shake) ... are you?

    Also, in case you have not read the posts above, wood roofs *DO NOT LAST* long in some environments, such as South Florida.

    Yes, asphalt shingle roofs burn, but they do not ignite as quickly, and go up as quickly, as wood and thatched roofs do. Then again, most roofing materials burn, heck, get a concrete tile roof hot enough and the underlayment will burn, same with metal roofs.

    In case you have not noticed, we has s-t-r-a-y-e-d w-a-y off the topic as posted.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  25. #25
    Frank Suchodolski's Avatar
    Frank Suchodolski Guest

    Default Re: shake roof/ no drip edge

    [quote=Scott Patterson;63042]Well for one thing a 10" exposure is wrong. Depending on the grade of shingle and the slope of the roof you should not have more than a 71/2" exposure on a 24" shake.

    7 1/2" exposure on 24" cedar "shingle" and 10" exposure on 24" cedar "shake", that's up here in the Great White North anyway.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •