3 taps Cutler Hammer
Why would they have 3 taps on the breaker?
Cutler-Hammer Type CHAF - One Pole Arc Fault. 15 amp.
Best
Ron
Similar Threads:Last edited by Ron Bibler; 12-02-2008 at 01:00 AM.
-
12-02-2008, 07:04 AM #2
Re: 3 taps Cutler Hammer
Not sure what you are referring to as taps, but AFCI breakers, like GFCI breakers, have a terminal to which the hot conductors goes, a terminal to which the neutral conductor goes, and a white pigtail which goes to the neutral terminal bar.
-
12-02-2008, 08:19 AM #3
Re: 3 taps Cutler Hammer
Jerry they have 3 white wires in the lower back of this breaker?
and 1 Black in the breaker?
Best
Ron
Last edited by Ron Bibler; 12-02-2008 at 08:38 AM.
-
12-02-2008, 08:55 AM #4
Re: 3 taps Cutler Hammer
See if this diagram make sense.
From this site Arc Fault Circuit Interrupteurs AFCI
-
12-02-2008, 10:06 AM #5
Re: 3 taps Cutler Hammer
Ron,
From the photo, there are two AFCI breakers side-by-side, I think the "3rd" white wire is actually to the other AFCI breaker. If not, that AFCI breaker is missing its 2nd white wire.
-
12-02-2008, 10:20 AM #6
Re: 3 taps Cutler Hammer
Thanks Jerry. its was hard to see back behind everything and did not want to stick my hand back in there. I have other minor issue with this panel. will let sparky look at it.
Best
Ron