    Spliced one leg and not the other. So ... I guess they spliced copper and aluminum together. Nice.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: main breaker cu/al

    As long as the breaker can accept the larger AL conductor I don't see what the issue would be. Split bolts and polaris type connections can handle a combination of conductor types as can breakers


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: main breaker cu/al

    John,

    Is that the main breaker? If so, it was back-fed and needed to be secured in place on the other end.

    Also, there are other taped-up wires there ... why are they taped-up? Insulation bad?

    Have any other photos of that panel?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: main breaker cu/al

    Jerry - That is the main. And it is backfed.
    This property had so many electrical problems it was mind boggling. Someone who clearly didn't have a clue did tons of things like:
    using #12 to wire a 220 receptacle with an electric range plugged into it.
    Fire hazards galore.