	05-24-2007, 01:50 PM #1 Indirect waste lines... Indirect waste lines...Hello to all, 
 
 Can someone point me to the section in the 2006 IRC that covers/addresses indirect waste situations (e.g. bar sink drained to nearby floor drain, etc.) and what is or is not allowed?
 
 Thanks!
 Similar Threads:
 
- 
	05-24-2007, 06:57 PM #2 Re: Indirect waste lines... Re: Indirect waste lines...A bar sink is not, should not be, an indirect waste. 
 
 It should be connected into the sanitary drainage system.
 
 
- 
	05-24-2007, 07:17 PM #3 Re: Indirect waste lines... Re: Indirect waste lines...10-4. 
 
 Is there a section of the IRC that addresses this specifically? I was trying to find it, and cannot.
 
 Maybe a UPC section?
 
 
- 
	05-24-2007, 07:44 PM #4 Re: Indirect waste lines... Re: Indirect waste lines...From the IRC. 
 - P2601.2 Connection. Plumbing fixtures, drains and appliances used to receive or discharge liquid wastes or sewage shall be connected to the sanitary drainage system of the building or premises in accordance with the requirements of this code. This section shall not be construed to prevent indirect waste systems.
 
 INDIRECT WASTE PIPE.A waste pipe that discharges into the drainage system through an air gap into a trap, fixture or receptor.
 
 To find out more about "indirect wastes", you must go to the IPC.
 SECTION 802
 INDIRECT WASTES802.1 Where required.Food-handling equipment and
 clear-water waste shall discharge through an indirect waste
 pipe as specified in Sections 802.1.1 through 802.1.7. All
 health-care related fixtures, devices and equipment shall discharge
 to the drainage system through an indirect waste pipe by
 means of an air gap in accordance with this chapter and Section
 713.3. Fixtures not required by this section to be indirectly connected
 shall be directly connected to the plumbing system in
 accordance with Chapter 7.
 802.1.1 Food handling.Equipment and fixtures utilized for
 the storage, preparation and handling of food shall discharge
 through an indirect waste pipe by means of an air
 gap.
 802.1.2 Floor drains in food storage areas.Floor drains
 located within walk-in refrigerators or freezers in food service
 and food establishments shall be indirectly connected
 to the sanitary drainage system by means of an air gap.
 Where a floor drain is located within an area subject to
 freezing, the waste line serving the floor drain shall not be
 trapped and shall indirectly discharge into a waste receptor
 located outside of the area subject to freezing.
 Exception:Where protected against backflow by a
 backwater valve, such floor drains shall be indirectly
 connected to the sanitary drainage system by means of an
 air break or an air gap.
 802.1.3 Potable clear-water waste.Where devices and
 equipment, such as sterilizers and relief valves, discharge
 potable water to the building drainage system, the discharge
 shall be through an indirect waste pipe by means of an air
 gap.
 802.1.4 Swimming pools.Where wastewater from swimming
 pools, backwash from filters and water from pool deck
 drains discharge to the building drainage system, the discharge
 shall be through an indirect waste pipe by means of
 an air gap.
 802.1.5 Non potable clear-water waste.Where devices
 and equipment such as process tanks, filters, drips and boilers
 discharge non potable water to the building drainage system,
 the discharge shall be through an indirect waste pipe by
 means of an air break or an air gap.
 802.1.6 Domestic dish washing machines.Domestic
 dish washing machines shall discharge indirectly through an
 air gap or air break into a standpipe or waste receptor in
 accordance with Section 802.2, or discharge into a
 wye-branch fitting on the tailpiece of the kitchen sink or the
 dishwasher connection of a food waste grinder. The waste
 line of a domestic dish washing machine discharging into a
 kitchen sink tailpiece or food waste grinder shall connect to
 a deck-mounted air gap or the waste line shall rise and be
 securely fastened to the underside of the sink rim or counter.
 802.1.7 Commercial dish washing machines.The discharge
 from a commercial dish washing machine shall be
 through an air gap or air break into a standpipe or waste
 receptor in accordance with Section 802.2.
 802.2 Installation.All indirect waste piping shall discharge
 through an air gap or air break into a waste receptor or
 standpipe.Waste receptors and standpipes shall be trapped and
 vented and shall connect to the building drainage system. All
 indirect waste piping that exceeds 2 feet (610 mm) in developed
 length measured horizontally, or 4 feet (1219 mm) in total
 developed length, shall be trapped.
 802.2.1 Air gap.The air gap between the indirect waste
 pipe and the flood level rim of the waste receptor shall be a
 minimum of twice the effective opening of the indirect
 waste pipe.
 802.2.2 Air break.An air break shall be provided between
 the indirect waste pipe and the trap seal of the waste receptor
 or standpipe.
 802.3 Waste receptors.Every waste receptor shall be of an
 approved type. A removable strainer or basket shall cover the
 waste outlet of waste receptors. Waste receptors shall be
 installed in ventilated spaces. Waste receptors shall not be
 installed in bathrooms or toilet rooms or in any inaccessible or
 unventilated space such as a closet or storeroom. Ready access
 shall be provided to waste receptors.
 802.3.1 Size of receptors.A waste receptor shall be sized
 for the maximum discharge of all indirect waste pipes
 served by the receptor. Receptors shall be installed to prevent
 splashing or flooding.
 802.3.2 Open hub waste receptors.Waste receptors shall
 be permitted in the form of a hub or pipe extending not less
 than 1 inch (25.4 mm) above a water-impervious floor and
 are not required to have a strainer.
 802.4 Standpipes.Standpipes shall be individually trapped.
 Standpipes shall extend a minimum of 18 inches (457 mm) and
 a maximum of 42 inches (1066 mm) above the trap weir.
 Access shall be provided to all standpipes and drains for
 rodding.
 
 
 
- 
	05-24-2007, 08:42 PM #5 Re: Indirect waste lines... Re: Indirect waste lines...Thank you! 
 
 


 
 
						
					
 
				
				
				