Results 1 to 12 of 12
  1. #1
    Kevin Luce's Avatar
    Kevin Luce Guest

    Default Copper and Galvized connection

    OK, I have a clear understanding why copper and galvanized pipe needs to be separated, but why can't galvanized hangers be used with copper pipe? Unlike a copper pipe connected to a galvanized pipe, the copper pipe and the galvanized pipe hanger do not come in contact with an acid solution. Without the acid solution there is no electro-galvanic action.

    Yes, I realized I mis-spelled galvanized in the title.

    Similar Threads:
    Last edited by Kevin Luce; 01-17-2009 at 10:45 PM. Reason: Added last sentence.
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Copper and Galvized connection

    It's unlikely that a steel strap on a copper pipe would ever lead to a problem. If the pipe is in a damp/cold area and there's some condensation the chances might be a bit elevated but it's still low.

    I've seen this setup more times than I could ever count on houses 30+ years old and have never seen any corrosion, let alone a leak.

    The code is written ultra-conservatively and that is likely why it specifies that straps must be the same material as the piping they support.

    You're right that it's much more likely at the joint of the piping due to the water. Even that is rare. I'd say for every 20 junctions I find 1 is corroded or leaking.... but I do write those up.... the straps - nope. I'm sure others here will yell and scream that I'm incompetent.


  3. #3
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Copper and Galvized connection

    Quote Originally Posted by Kevin Luce View Post
    OK, I have a clear understanding why copper and galvanized pipe needs to be separated, but why can't galvanized hangers be used with copper pipe? Unlike a copper pipe connected to a galvanized pipe, the copper pipe and the galvanized pipe hanger do not come in contact with an acid solution. Without the acid solution there is no electro-galvanic action.

    Yes, I realized I mis-spelled galvanized in the title.
    Hot,cold, sweating,,= electro-galvanic action

    Every other water heater I inspect has corroded connections. Almost always on the cold side. Sometimes on the hot side. Gees. The amount I write up percentage wise is huge. More than 50 percent of the time with out exageration. Some are just starting. Some are seriously corroded.


  4. #4
    Ron Bibler's Avatar
    Ron Bibler Guest

    Default Re: Copper and Galvized connection

    Every time copper pipes come in contact with other materials is starts the electro-galvanic action. it may not be at the areas that you see but at some point in the building there is that element to complete the action. if not at faucet then in connection with a drain pipe or a hanger or even something hanging across the pipe. I always make a note about the rust and corrosion. just a note. some may not.

    Best

    Ron

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  5. #5
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Copper and Galvized connection

    Quote Originally Posted by Ted Menelly View Post
    Hot,cold, sweating,,= electro-galvanic action

    Every other water heater I inspect has corroded connections. Almost always on the cold side. Sometimes on the hot side. Gees. The amount I write up percentage wise is huge. More than 50 percent of the time with out exageration. Some are just starting. Some are seriously corroded.
    I should ammend what I said.... I agree with Ted that at least 50% of the water heater junctions are corroded and/or leaking.

    My 1 in 20 statistic was related to junctions throughout the other areas.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Copper and Galvanized connection

    Quote Originally Posted by Matt Fellman View Post
    It's unlikely that a steel strap on a copper pipe would ever lead to a problem.
    That is highly likely that a galvanized strap on copper pipe will cause a problem. So likely that it is prohibited by code.

    Would you want to have a leak, cut into a wall, only to find that the pin hole is where the copper pipe was contacting the galvanized strap?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Kevin Luce's Avatar
    Kevin Luce Guest

    Default Re: Copper and Galvanized connection

    Thanks for the info everyone.


  8. #8
    Richard Moore's Avatar
    Richard Moore Guest

    Default Re: Copper and Galvized connection

    Took me a while to find this...

    1989 home. Most every strap in the crawl looked like the photo. I realize they're not galvanized straps. Draw your own conclusions. I reported it as follows...

    Investigate Further and Repair: Most of the copper plumbing in the crawl space has been secured with steel wire hangers. Galvanic action between these two dissimilar metals is causing significant corrosion in many areas. No active leaks were observed but it is possible that some of the piping may be sufficiently damaged to warrant repair. I recommend a licensed plumber replace all of the hangers with those suited for copper piping and, at the same time, clean and check the corroded areas for any damage requiring further repair or replacement.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Copper and Galvanized connection

    Quote Originally Posted by Richard Moore View Post
    1989 home. Most every strap in the crawl looked like the photo. I realize they're not galvanized straps.
    Richard,

    I realize we concentrated on the term "galvanized", so you did too , however, as your photo shows, it is the non-compatibility of materials which is the concern, be that "galvanized", plain steel, aluminum, or any other non-compatible material.

    Great photos of what non-compatible materials can do.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Fred Warner's Avatar
    Fred Warner Guest

    Default Re: Copper and Galvized connection

    Dissimilar metals cause problems for plumbers and electricians. No doubt about it.


  11. #11
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Copper and Galvized connection

    Depending on the chemical content of the potable water dielectric fittings don't always work so well.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry McCarthy
    Building Code/ Construction Consultant

  12. #12
    Join Date
    Mar 2007
    Location
    New Westminster, B. C., Canada
    Posts
    165

    Default Re: Copper and Galvized connection

    Hi there, All &

    * I ALWAYS call-out 'dissimilar metals' in contact with CU (doesn't matter what other type) & have seen many 'leakers' /corroded & 'about to spray'...

    Great pics, Guys !


    CHEERS

    -Glenn Duxbury, CHI

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •