Results 1 to 35 of 35
Thread: Two bathroom sinks = 2 outlets?
-
02-06-2009, 12:45 PM #1
Two bathroom sinks = 2 outlets?
Master bathroom in a new house.
Similar Threads:
-
02-06-2009, 12:49 PM #2
Re: Two bathroom sinks = 2 outlets?
Looks like that one properly serves both sinks:
just calls for "a" receptacle, not a dedicated receptacle.
-
02-06-2009, 01:01 PM #3
Re: Two bathroom sinks = 2 outlets?
Providing it is a GFCI protected outlet, it is a compliant installation.
-
02-06-2009, 01:58 PM #4
Re: Two bathroom sinks = 2 outlets?
A left handed person using the left sink will have the cord draped across or around the sink bowl. I would have more than likely put one to the left of the left sink but not to the right of the right sink due to it being right next to the tub. Some one could have something plugged in and have it fall in the tub and then they would be the tester for the GFCI.
Last edited by Ted Menelly; 02-07-2009 at 09:26 PM.
-
02-06-2009, 02:23 PM #5
Re: Two bathroom sinks = 2 outlets?
Thanks guys....
Am I imagining things or did I hear about that one outlet per sink thing somewhere? Maybe the 2008 electric code?
-
02-06-2009, 02:58 PM #6
Re: Two bathroom sinks = 2 outlets?
Maybe if you could only plug one appliance of sorts into that receptacle then the other sink would not have a recptacle to plug anything into.
-
02-06-2009, 05:38 PM #7
-
02-06-2009, 06:40 PM #8
Re: Two bathroom sinks = 2 outlets?
Imagining it, probably because 'it would be the right thing to do', but code does not require one 'to do the right thing'.
210.52
- (D) Bathrooms. In dwelling units, at least one receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop, or installed on the side or face of the basin cabinet not more than 300 mm (12 in.) below the countertop.
-
02-06-2009, 06:52 PM #9
Re: Two bathroom sinks = 2 outlets?
Ah, but there is an outlet within 3 ft of each basin.
Interpretation, interpretation, interpretationIt says one outlet within 3 feet of each basin. It does not say there that each basin had to own their own.
I would have put one, as I said, to the left of the left sink
-
02-06-2009, 07:00 PM #10
Re: Two bathroom sinks = 2 outlets?
I know that, that's what I said. You can read it right in the code I posted.
Not sure what the "Ah, but there is an outlet within 3 ft ... " is about???
Interpretation, interpretation, interpretationIt says one outlet within 3 feet of each basin. It does not say there that each basin had to own their own.
Please show me where I said it was not right.
-
02-06-2009, 07:35 PM #11
Re: Two bathroom sinks = 2 outlets?
I have just been reading all the other threads and posts.
I did not say you were wrong or did not post it right.
Just saying that the particular code could be interpreted as each basin needs its own outlet.
I read the codes all the time and always ask myself.
"Is that what that means"
Just as I inspect new homes and with the ground to the steel under the slab (rebar coming up and the ground wire connected to it in a junction box) (I am trying to find it now) You don't need a grounding rod. Of course there are many exceptions.
Same thing with the detached garage. I made the mistake for a some time of writing it up if if the panel in the detached garage also had a ground rod.
As you see all the time even with yourself it is a constant learning curve to keep up with what was not long ago to what it should be now.
The code is a constant rewrite of the local play and you have to keep seeing the play year after year to see what has changed.
I don't respond in depth about code because by the time I check on it to make sure I state things right someone has usually gone there already. I never did get all the code software to just pull it up and copy and paste.
I wasn't question you Jerry.
-
02-06-2009, 07:54 PM #12
Re: Two bathroom sinks = 2 outlets?
Nope, it can't, not unless some is reading words which are not there.
Just as I inspect new homes and with the ground to the steel under the slab (rebar coming up and the ground wire connected to it in a junction box) (I am trying to find it now) You don't need a grounding rod. Of course there are many exceptions.
Which is why almost every area (all that I have been in) require the 'grounding electrode conductor' to go down into the "concrete encased electrode' - i.e., down into the concrete slab or footing.
I am sure the above will raise holly cain with some people reading it, but, if you are one of them, read it again, then read what the code says, then show me where that connection is allowed in the grounding electrode conductor and show me where rebar is an approved grounding electrode conductor.
I wasn't question you Jerry.I thought you were getting ready to become another Jeff, Rolland, Jim Port, or sometimes Fred.
I was beginning to think that maybe I was not typing the words I was typing, and that the words were not the words I was then reading afterward.
-
02-06-2009, 08:09 PM #13
Re: Two bathroom sinks = 2 outlets?
So you are saying that the rebar sticking up out of the concrete becomes the grounding conductor but you want the grounding conductor to go down into the concrete??????
Well then. If either one (Copper wire, or rebar) are both the conductors if they are not into the concrete (which they are). but if you run the conductor down into the concrete (you are) you are OK. Well. You just said the ground conductor (rebar) needs to go down in the concrete. It does.
The connection is accessible when you remove the junction box cover to check a proper connection. I am not sure what the problem is.
If you have the proper clamp connecting the copper to the rebar then it does become one piece and it is into the concrete. No matter how you look at it it is in the concrete.
Sorry with the ring around the rosy but it all comes out the same way.
-
02-06-2009, 08:22 PM #14
Re: Two bathroom sinks = 2 outlets?
Yep.
That's the way it is done everywhere I've been.
That is because the grounding electrode conductor "goes to" the "concrete encased electrode".
That rebar is no longer a "concrete encased electrode", it is a "stub up" grounding electrode conductor, to which the other part of the grounding electrode conductor gets spliced together.
Being as that is splicing the grounding electrode conductor, that clamp is not an approved splice.
But that is only part of it: that rebar is not an approved grounding electrode conductor material.
Well then. If either one (Copper wire, or rebar) are both the conductors if they are not into the concrete (which they are). but if you run the conductor down into the concrete (you are) you are OK.
You are using an approved conductor for the GEC with the copper GEC.
Well. You just said the ground conductor (rebar) needs to go down in the concrete. It does.
[quote]The connection is accessible when you remove the junction box cover to check a proper connection. I am not sure what the problem is.[/quote[
The problem is that the rebar is no longer a "concrete encased electrode" and the rebar is not an approved conductor material for use as a GEC.
If you have the proper clamp connecting the copper to the rebar then it does become one piece and it is into the concrete. No matter how you look at it it is in the concrete.
Sorry with the ring around the rosy but it all comes out the same way.
-
02-06-2009, 08:31 PM #15
Re: Two bathroom sinks = 2 outlets?
So the way you (Code) is stating it. If the grounding conductor burns off in , say, a lightening strike, one must bust up the concrete to reconnect the conductor to the electrode (rebar) and then pour concrete back over it?????
-
02-06-2009, 08:32 PM #16
Re: Two bathroom sinks = 2 outlets?
Oh, okay. I thought you were getting ready to become another Jeff, Rolland, Jim Port, or sometimes Fred.
-
02-06-2009, 08:42 PM #17
Re: Two bathroom sinks = 2 outlets?
That's not going to happen (not all the way back to the concrete encased electrode), but, yes, that is the way the code states it.
If the GEC were to be cut, damaged, etc., by a lightning strike or a lawn mower, all that would need to be done is use one of those "irreversible compression connectors" discussed on an earlier thread or by exothermic welding.
- 250.64 Grounding Electrode Conductor Installation.
- - (C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2):
- - - (1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
- - - (2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
Again, not me, the code.
-
02-06-2009, 08:47 PM #18
Re: Two bathroom sinks = 2 outlets?
Yep. And then you wonder how it is that those people can be so mis-informed, and eventually they come around, one-by-one, when they understand what the code says, what is being written, and what they thought they were reading. See, *I* was, at one time, on your mis-formed side of the fence, but, through knowledge gained, *I* have continued to learn and progress.
Time will come when you will too. Just wait, it will happen. And you will be a better person for it.
-
02-06-2009, 09:04 PM #19
Re: Two bathroom sinks = 2 outlets?
[quote=Jerry Peck;72350]Yep.
"That is because the grounding electrode conductor "goes to" the "concrete encased electrode".
That rebar is no longer a "concrete encased electrode", it is a "stub up" grounding electrode conductor, to which the other part of the grounding electrode conductor gets spliced together.
Being as that is splicing the grounding electrode conductor, that clamp is not an approved splice.
But that is only part of it: that rebar is not an approved grounding electrode conductor material.
The problem is that the rebar is no longer a "concrete encased electrode" and the rebar is not an approved conductor material for use as a GEC."
I thought I had heard all the crap and now there is more crap. Jerry you don't know what you are talking about. Certainly shows you cant read and discern meaning from simple material. You are all wet. AGAIN!
Last edited by Roland Miller; 02-06-2009 at 09:34 PM. Reason: clairity
"Get correct views of life, and learn to see the world in its true light. It will enable you to live pleasantly, to do good, and, when summoned away, to leave without regret. " Robert E. Lee
-
02-06-2009, 09:19 PM #20
Re: Two bathroom sinks = 2 outlets?
A 20' piece of properly rebar is being used as a CEE. The last 18" come out the top of the footer and will be bent downward and encased in concrete when the basement floor is poured.
A GEC is attached to the end of the rebar in question with a clamp that is listed and labeled for attachment to rebar and for both DB and concrete encasement.
Are any of you stating that this would not be a proper installation?
-
02-06-2009, 09:37 PM #21
Re: Two bathroom sinks = 2 outlets?
-
02-06-2009, 09:38 PM #22
Re: Two bathroom sinks = 2 outlets?
irc E3508.1.2 PARAPHRASED
20 foot rebar not less than #4 encased by at least 2 inches of concrete
-
02-06-2009, 09:57 PM #23
Re: Two bathroom sinks = 2 outlets?
Again, Jerry, simple question and does not matter the original post because we have way off that thread for quite some time now.
-
02-06-2009, 10:01 PM #24
Re: Two bathroom sinks = 2 outlets?
Jeff,
It was a simple question, HOWEVER, it was in response to a discussion about a different issue.
And I have no idea where you pulled up "original post" from ... I specifically stated "Go back and re-read what Ted was saying.", THAT is what Ted and I were discussing.
THEN we can address your question.
-
02-06-2009, 10:03 PM #25
Re: Two bathroom sinks = 2 outlets?
I understand
-
02-07-2009, 05:54 AM #26
-
02-07-2009, 10:34 AM #27
Re: Two bathroom sinks = 2 outlets?
Making the rebar available for an exposed connection does not change the fact that the CEE still exists and once a rebar always a rebar. This would be an accepted connection.
This is how it is in the real world..
"Get correct views of life, and learn to see the world in its true light. It will enable you to live pleasantly, to do good, and, when summoned away, to leave without regret. " Robert E. Lee
-
02-07-2009, 11:29 AM #28
Re: Two bathroom sinks = 2 outlets?
-
02-07-2009, 12:03 PM #29
Re: Two bathroom sinks = 2 outlets?
The people I have contact with in the State of Florida that are AHJs all allow it.. Jerry your real world must be very small..
"Get correct views of life, and learn to see the world in its true light. It will enable you to live pleasantly, to do good, and, when summoned away, to leave without regret. " Robert E. Lee
-
02-07-2009, 01:22 PM #30
Re: Two bathroom sinks = 2 outlets?
Must be North Florida Panhandle people, those where the same people who said that hurricanes do not blow very hard beyond 1 mile inland from the Gulf coastline, so they got the Legislature to make that into a law, which held until a few years ago, after people realized that mother nature does not follow directions.
Sorry, old buddy, you are not going to be able to sneak that one through.
Hmmm, wonder if they are the same people who "really understood the NEC" regarding the wording change from the 2002 NEC to the 2005 NEC regarding "available" and "present" ... Yep, probably.
-
02-07-2009, 02:59 PM #31
Re: Two bathroom sinks = 2 outlets?
Mostly it is a matter of being the reasonable, ordinary person on the street or being bazaar and on the fringes of insanity like Jerry.. Jerry you have picked up some very obscure ideas and promote them as mainstream and they are not. Do you bare-foot water ski??
"Get correct views of life, and learn to see the world in its true light. It will enable you to live pleasantly, to do good, and, when summoned away, to leave without regret. " Robert E. Lee
-
02-07-2009, 07:19 PM #32
Re: Two bathroom sinks = 2 outlets?
-
02-07-2009, 09:12 PM #33
Re: Two bathroom sinks = 2 outlets?
Simple question on post #1 was correctly answered by posts 2 & 3.
How did this turn into 32 posts when the correct answer was given initially?
Where is the value in this?
-
02-07-2009, 09:20 PM #34
Re: Two bathroom sinks = 2 outlets?
Education.
It happens here.
And it happens here in the strangest of ways.
Enjoy it.
The age old question: Is the glass half full or half empty?
-> The pessimist thinks the glass is half empty ... and is worried that they are losing even more due to evaporation.
-> The optimist knows the glass is half full ... and understands that, over time, condensation will finish filling the glass.
- Jerry Peck, 2009
-
02-08-2009, 06:06 AM #35
Re: Two bathroom sinks = 2 outlets?
And the Engineer thinks that the glass is twice as big as it needs to be!
-
Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
Find on Facebook at: https://www.facebook.com/B4UCloseInspections
Bookmarks