Thread: Restricted, crimped air ducts?
05-30-2007, 10:24 AM #1
Similar Threads:Last edited by Jeff Eastman; 12-19-2007 at 06:56 PM.
05-30-2007, 03:25 PM #2
Re: Restricted, crimped air ducts?
Jeff,
It wouldn't be a bad idea to recommend that they have the static pressure of the duct system tested to verify proper airflow.
Any equipment attached to a duct system like that is in for a rough run.
05-30-2007, 03:34 PM #3
If you need a contractor in Vegas that does performance testing I can hook you up Jeff.
One of the guys who mentored me lives in Vegas.
06-01-2007, 09:42 AM #4
As a rule, flexible ductwork should not be installed in lengths greater than 8 feet, and with a bend greater than 90 degrees. One could test for "static pressure", but where? Suggest testing for volume delivered at each outlet for a more definitive result.
Joseph D. Rago P.E.
A.E.G.
Yardley PA
06-01-2007, 02:46 PM #5
You could test the total external static pressure to see how much resistance the fan is seeing & you could also measure the static pressure drop of each suspect flex run out.
Most guys can afford a manometer or magnehelic, most don't have anyway of measuring air volume from the registers.
06-01-2007, 08:37 PM #6
06-01-2007, 09:00 PM #7
Why not install saddles below the ducts where the strap is restricting the air flow?