Results 1 to 20 of 20
  1. #1
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Water-Resistive Barrier Installation

    Can someone give some information on if you can install water resistive barrier, i.e. Tyvek, by unrolling the material vertically or does it not have to be done horizontally? There is a three story building with the first floor going to have stone and the rest going to be EIFS. On the first floor they have installed the barrier by unrolling it applying it to the building horizontally. The other two floors they have began to unroll the barrier from the top of the building to a point that overlays the first floor layer 6". Is this correct?

    Similar Threads:
    Member Benefits1
    Dylan Whitehead

  2. #2
    Bob Spermo's Avatar
    Bob Spermo Guest

    Default Re: Water-Resistive Barrier Installation

    I believe Tyvek is supposed to be installed horizontally due to the fact that it has vertical groves for water to run down. Obviously if it is installed vertically the groves would run horizontally and may hinder any water resistent capabilities. Check the Dupont/Tyvek page.


  3. #3
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    Dupont / Tyveck Installation Guide:

    Start at the bottom of the structure to ensure proper shingling occurs throughout the installation. Proper shingling is required
    to provide for water shedding and to prevent water entering the wall system.


    Thanks Bob.


    Dylan Whitehead

  4. #4
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Water-Resistive Barrier Installation

    If the strips are being hung vertically then it is wrong.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  5. #5
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    I am still waiting on the builder to supply me the manufacturers installation instructions stating that the way he is doing is correct. I don't think I will be getting that phone call or fax. Thanks for the help guys.

    Dylan Whitehead

  6. #6
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Water-Resistive Barrier Installation

    There are two reports on Tyvek. The reports I read on the ICC ES Evaluation Reports indicated to "wrap the material around" the structure.

    http://www.icc-es.org/reports/pdf_fi...S/ESR-2375.pdf

    http://www.icc-es.org/reports/pdf_fi...S/ESR-1993.pdf




  7. #7
    Join Date
    Dec 2008
    Location
    Montreal, QC, Canada
    Posts
    63

    Default Re: Water-Resistive Barrier Installation

    Tyvek and other similar materials should be wrapped from bottom to top ensuring proper overlap as well as fastening and taping.

    usually contractors wrap completely over openings like doors and windows then cut into and wrapped around framing

    see Tyvek manual on their website. Linl below

    http://www2.dupont.com/Tyvek_Weather...WRB_K16282.pdf


  8. #8
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Water-Resistive Barrier Installation

    Quote Originally Posted by Joe Laurieri View Post
    Tyvek and other similar materials should be wrapped from bottom to top ensuring proper overlap as well as fastening and taping.

    usually contractors wrap completely over openings like doors and windows then cut into and wrapped around framing

    see Tyvek manual on their website. Linl below

    http://www2.dupont.com/Tyvek_Weather...WRB_K16282.pdf
    Thats all pretty funny stuff I have not had to or needed to look at the installation instructions in a long time. I write tyvek installations up all the time because I have never seen it applied properly.

    Don't you just love the tyvex wrap caps. Never once seen them on a building, just in a box.


  9. #9
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    The builder of this particular project is trying to make the argument that he is only using house wrap and that it is much faster for them to install it this way instead of wrapping the building from the bottom up.

    Wayne- Does the reports you posted only pertain to the Tyvek brand of WRB? The builder is using a similar product that he purchased from Lowes. I have asked him to have that manufacturer send me some of there installation instructions and documents showing that the way he is installing it is okay.

    My next question is, can they use "house wrap" under EIFS?
    Does it not have to be the "Stucco Wrap" or the "Drain Wrap" or does the fact that they will be installing EPS on top of the WRB?

    Dylan Whitehead

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Water-Resistive Barrier Installation

    Quote Originally Posted by Dylan Whitehead View Post
    My next question is, can they use "house wrap" under EIFS?
    Does it not have to be the "Stucco Wrap" or the "Drain Wrap" or does the fact that they will be installing EPS on top of the WRB?
    If they are installing it under EIFS, the newer drainable EIFS, then the "house wrap" *is* the WRB and *is* the drainage plane and *must* be installed horizontally "around" the house, with those grooves running vertically and not horizontally.

    Sounds to me as though the builder as *no idea what he is doing, nor why it is to be done*.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Water-Resistive Barrier Installation

    The reports are Dupont Tyvek specific. Each manufactuer must get their own product tested and approved for the installation of their product.

    What brand/type are they using.

    As far as EIFS, you still have to apply some type of barrier so it all comes back on the material installed. Is it an approved material for what the use is intended?

    PS There's a one day class coming up in Grand Prairie I believe on March 19.... wood framing and steel framing in the 2006 IRC/IBC


  12. #12
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    Wayne- I will be attending the class on the 19th and I look forward to meeting you.
    I recieved a call from the Lowes representative this morning and he was telling me that he has the manufacturers information and is going to fax it to me. I am going to wait and see exactly what the manufacturer sends?
    I still question the installation as it is. I will post what I find out from their information.

    Dylan Whitehead

  13. #13
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    Okay, I recieved a letter from a Dupont Tyvek Proffesional and they are telling me that it is correct to install the wrap vertically if they follow two steps.
    1: All seams must overlap by a minimum of 6"
    2: All seams must be taped
    They said that even though this procedure is not on the installation instructions that it is acceptable with these two requirements.

    I also called them directly to discuss the use of "house wrap" versus "stucco / drainage wrap" under EIFS and they told me that "house wrap" would work just fine and still meet the requirments of the IBC. I got all this in writting and filed away for any future issues.

    Dylan Whitehead

  14. #14

    Default Re: Water-Resistive Barrier Installation

    Okay, I recieved a letter from a Dupont Tyvek Proffesional and they are telling me that it is correct to install the wrap vertically if they follow two steps.
    1: All seams must overlap by a minimum of 6"
    2: All seams must be taped
    I'd love to see a study showing how long that tape lasts..........
    I have an issue with a 6" lap as well. Water will not only travel vertically, and the longer that vertical run is, the further sideways the water can travel.

    Was this letter from the company rep, or their technical dept.?
    You very well may get varying answers from each, as I have had happen.


  15. #15
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    The letter was from a Certified Tyvek Specialist w/ Weatherization Partners LTD.

    I am doing more research on this company.

    Dylan Whitehead

  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Water-Resistive Barrier Installation

    Quote Originally Posted by Dylan Whitehead View Post
    The letter was from a Certified Tyvek Specialist w/ Weatherization Partners LTD.

    I am doing more research on this company.
    If the letter is not from Dupont itself and their technical department, on their letter head, I would not accept it. Only from the manufacturer themselves, and only from their engineering department.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17

    Default Re: Water-Resistive Barrier Installation

    I'm with Jerry on this one. Being "certified" does not mean much these days.


  18. #18
    Join Date
    May 2008
    Location
    Burleson, Texas
    Posts
    90

    Default Re: Water-Resistive Barrier Installation

    That is why I am doing more research on this company. The letter I received has both their company logo as well as Dupont's Logo. I have just sent a email to the Dupont web site directly asking about this particular application and I will post what they respond as soon as I get an answer.

    Dylan Whitehead

  19. #19
    Christopher Gorton's Avatar
    Christopher Gorton Guest

    Default Re: Water-Resistive Barrier Installation

    Using vertical joints was permitted for the Tyvek house wrap we used on our project with the 6 inch overlap and their brand of tape. The tape that was supplied has the same moisture resistant properties as the wrap and when installed with an overlap on both pieces forms a bond that is impossible to remove without tearing or cutting.
    That said this method was just done for simplicity of installing the top triangle of the gable ends.
    It should be noted and probably is somewhere in all the links supplied that the headers are never wrapped. The house wrap is cut off at the exterior sheathing to avoid trapping water.
    Found one installed the wrong way once and discovered that it held 10 gallons of water for 2 weeks without dripping. That means the tape joints held water also.


  20. #20
    Stephen Meyer's Avatar
    Stephen Meyer Guest

    Default Re: Water-Resistive Barrier Installation

    Dylan,

    Reading an old post, caught my attention since I am an EIFS inspector.

    If you look at the testing reports on Tyvek as a weather barrier, the minimum is the Tyvek Stucco Wrap. It is a heavier material, has channels for drainage and must be applied according to the manufacturers "Tested" practice, which is horizontal. There is also an anchor pattern and special staple/anchor to be used. This is to get the Tyvek warranty.
    These methods are specific for an EIFS application as outline in the ES reports.

    The problems with the mixing of the eifs and other WRB is that if there are problems, each will defer warranty due to the other. I see this all the time and try to get the Tyvek specialist involved for the warranty. The 2009 code is making a further attempt in the requirements for inspection, but I do not see it being that much of an improvement.

    I would like to see the end result of what you inspected

    Steve Meyer


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •