Results 1 to 17 of 17

Thread: What is this?

  1. #1
    Jim Hughes's Avatar
    Jim Hughes Guest

    Default What is this?

    Hey Gang:
    I saw this on an electrical panel located in the basement next to the well pump. This "transformer"? has stranded aluminum wires that is double tapped at the 220 v breaker for the well pump. What is this and what does it do?
    And how should it be properly wired in to the panel?
    Thanks,
    Jim

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: What is this?

    Looks like a "surge suppressor", but I don't recognize the brand. If it is a TVSS the manufacturer's instructions will control whether it can be connected to an existing breaker, BUT the breaker has to be listed from multiple connections of the wire types and size used. Also, the instructions may require twisting the leads (usually, at least 1/2 turn per 12").


  3. #3

    Default Re: What is this?

    It looks like a lightning supressor.


  4. #4
    Rob Thomas's Avatar
    Rob Thomas Guest

    Default Re: What is this?

    It's a lightning arrestor. It can be double-tapped on that Square D breaker as long as the conductors are the same size.

    Oddly, the instructions with many arrestors recommend placing them INSIDE the enclosure and connecting the conductors to any breaker (regardless of the terminal design). This helps sell arrestors but it doesn't necessarily meet the requirements of the NEC.

    I have seen instructions for one brand of arrestor that specify connection to a dedicated breaker.

    The installation in your photos is as good as any I have seen.

    RT



    Quote Originally Posted by Jim Hughes View Post
    Hey Gang:
    I saw this on an electrical panel located in the basement next to the well pump. This "transformer"? has stranded aluminum wires that is double tapped at the 220 v breaker for the well pump. What is this and what does it do?
    And how should it be properly wired in to the panel?
    Thanks,
    Jim



  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    However, the white is connected to a breaker instead to the neutral terminal bar, which means, I guess, that the black is connected to the neutral terminal bar - meaning ... it is wired backward.

    Plus, they are required to be installed mounted outside the enclosure, like that one is.

    They are also one time hit units - has that been hit already, does it offer any protection now? I'm not going to say it's any good.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: What is this?

    When wired properly, what all is it designed to protect?

    Is there some kind of visual indicator for when they're good and when they've taken a hit? I've never seen one. Thanks for the post.

    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  7. #7
    Jon Randolph's Avatar
    Jon Randolph Guest

    Default Re: What is this?

    Isn't it wrong to double tap a 220v circuit, regardless of the breaker style?


  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: What is this?

    Thom, I put one in at my house. GE panel and surge protector that installs just like a breaker. It has a green light that is visible as long as it is working. I put it in a year ago and so far so good (although that reminds me I need to go look at it). It is designed to protect the whole house.
    I bought mine at a big box store for less than $50.
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    Quote Originally Posted by Jon Randolph View Post
    Isn't it wrong to double tap a 220v circuit, regardless of the breaker style?
    Not if the breaker terminals allow it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    Quote Originally Posted by Thom Walker View Post
    When wired properly, what all is it designed to protect?
    IT is designed to take a major surge or voltage spike / lightning strike to ground. To protect everything downstream of it.

    Is there some kind of visual indicator for when they're good and when they've taken a hit? I've never seen one. Thanks for the post.
    On those types, no, unless they suffer a severe hit (like lightning), in which case many of them swell up, or even explode open ('explode' may be too strong of a word - 'pop' open).

    If they are swollen, they've taken their hit, if they are not swollen, you just don't know, could be yes, could be no.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Rob Thomas's Avatar
    Rob Thomas Guest

    Default Re: What is this?

    It looks to me like that white wire is the second ungrounded conductor on the circuit that is connected to that 240-volt breaker, which leads me to believe the arrestor is wired properly.

    RT

    Quote Originally Posted by Jerry Peck View Post
    However, the white is connected to a breaker instead to the neutral terminal bar, which means, I guess, that the black is connected to the neutral terminal bar - meaning ... it is wired backward.

    Plus, they are required to be installed mounted outside the enclosure, like that one is.

    They are also one time hit units - has that been hit already, does it offer any protection now? I'm not going to say it's any good.



  12. #12
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: What is this?

    Based upon the premise that these whole house supressors are supposed to protect all the circuits in the house, why are some installed further down in the panel and not on the main lugs? Seems to me that a downstream installation is only protecting part of the electrical system.


  13. #13
    Jim Hughes's Avatar
    Jim Hughes Guest

    Default Re: What is this?

    Thanks for all your help!


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    Quote Originally Posted by Rob Thomas View Post
    It looks to me like that white wire is the second ungrounded conductor on the circuit that is connected to that 240-volt breaker, which leads me to believe the arrestor is wired properly.
    Except that when they use white wires they intend it to go to ground. They will use two blacks for the two to go to the ungrounded conductors (bus bars) and one white to go to the neutral terminal bar.

    Last edited by Jerry Peck; 06-03-2007 at 06:14 PM.
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    Quote Originally Posted by Nick Ostrowski View Post
    Based upon the premise that these whole house supressors are supposed to protect all the circuits in the house, why are some installed further down in the panel and not on the main lugs? Seems to me that a downstream installation is only protecting part of the electrical system.
    Because you are not allowed to multiple tap the main lugs.

    Tapping off a breaker off the bus bar protects the bus bar, which in turn protects every thing downstream. But it should not share a breaker, it should have its own, and, in fact, should just use a molded case switch as you don't want the breaker it is attached to to trip off. That would remove the protection it is providing.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  16. #16
    Rob Thomas's Avatar
    Rob Thomas Guest

    Default Re: What is this?

    I can't follow what you are saying. The two black wires from the arrestor are connected to the breaker. The white wire is part of the well-pump circuit on that breaker.

    I outlined in red and yellow the two wires that I think originate from the arrestor.

    RT

    Quote Originally Posted by Jerry Peck View Post
    Except that when they use white wires they intend it to go to ground. They will use two blacks for the two to go to the ungrounded conductors (bus bars) and one white to go to the neutral terminal bar.


    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: What is this?

    Quote Originally Posted by Rob Thomas View Post
    I outlined in red and yellow the two wires that I think originate from the arrestor.
    I was looking at the other two wires as coming from the surge protector, the 'white one' and 'the other black one'.

    Sorry about that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •