Results 1 to 3 of 3
  1. #1
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,873

    Default Wire size question

    I know that 12AWG is okay with 15 amp breaker. But what if a 20 amp breaker is coupled with a 8AWG conductor? Generally speaking. What are the potential ramifications if any?
    Thank you

    Similar Threads:
    OREP Insurance

  2. #2

    Default Re: Wire size question

    There's nothing wrong with a 8 gauge wire being tied to a 20 amp breaker, as long as the breaker is listed for that size of wire (the ones I have looked at are).

    You need to be more careful on the other end, such as at receptacles. 15 and 20 amp receptacles are not rated for 8 gauge wires.


  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,873

    Default Re: Wire size question

    yes very good, thanks