Results 1 to 11 of 11
  1. #1
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,153

    Default DO I NEED A LANDING HERE OR PARACHUTE

    hey all

    does this fall off need a landing, two steps or a parachute and what is the code for this ???

    thanks
    charlie

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Yes, a landing is required there, and not just a landing, but a proper stairway too.

    From the 2006 IRC.
    R311.4.3 Landings at doors.
    There shall be a floor or landing
    on each side of each exterior door. The floor or landing
    at the exterior door shall not be more than 1.5 inches (38
    mm) lower than the top of the threshold. The landing shall
    be permitted to have a slope not to exceed 0.25 unit vertical
    in 12 units horizontal (2-percent).

    Exceptions:
    1. Where a stairway of two or fewer risers is located
    on the exterior side of a door, other than the
    required exit door, a landing is not required for the
    exterior side of the door provided the door, other
    than an exterior storm or screen door does not
    swing over the stairway.
    2. The exterior landing at an exterior doorway shall
    not be more than 7
    3/4 inches (196 mm) below the
    top of the threshold, provided the door, other than
    an exterior storm or screen door does not swing
    over the landing.
    3. The height of floors at exterior doors other than the
    exit door required by Section R311.4.1 shall not be
    more than 7
    3/4 inches (186 mm) lower than the top
    of the threshold.
    The width of each landing shall not be less than the door
    served. Every landing shall have a minimum dimension of

    36 inches (914 mm) measured in the direction of travel.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    May 2008
    Location
    Atlanta
    Posts
    120

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    That door appears to swing in, so a landing is not necessary, right? Could just use steps I think, based on exception #1, as long as it does not require more than 2 steps.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Quote Originally Posted by Brent Crouse View Post
    That door appears to swing in, so a landing is not necessary, right? Could just use steps I think, based on exception #1, as long as it does not require more than 2 steps.
    And that one in the photo has three, and probably needs four to make then equal, all depending on the height of the top of the threshold down to the patio.

    However, *as shown* in the photo, there are THREE risers, which is "more than two risers" which means it needs a landing.



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Jerry,
    Do you ref. codes in your reports or just say items are required to be fixed or installed.

    Mat


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Quote Originally Posted by mathew stouffer View Post
    Jerry,
    Do you ref. codes in your reports or just say items are required to be fixed or installed.

    Mat
    I referenced codes in my reports at the end, say during the last 10+ years or so, getting more and more into codes each year as I learned more and more about codes.

    During the last 4+ years almost everything had a code reference, however, I was also almost exclusively doing new construction (phase inspections, new home walkthroughs, warranty inspections, quality control inspections for builders, those types of inspections, high end at that.

    I still referenced codes on the few resale inspection I did during that time. Drove agents and sellers nuts, but that was why my clients hired me, because they now had the backup they needed to get things addressed (not that "addressed" meant "corrected" but that "addressed" meant "money to them at closing" for the work which was needed).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    May 2008
    Location
    Atlanta
    Posts
    120

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    JP, I was basing my statement on the solution being to add "real" steps here, and not using the make-shift steps of patio stones. Just wanted to make sure my understanding of the exceptions was correct, and that, a landing would not be necessary if 2 steps were used.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Quote Originally Posted by Brent Crouse View Post
    JP, I was basing my statement on the solution being to add "real" steps here, and not using the make-shift steps of patio stones. Just wanted to make sure my understanding of the exceptions was correct, and that, a landing would not be necessary if 2 steps were used.
    Brent,

    Correct, but ...

    You must also count the riser to the interior floor from the top step.

    Like this: ground/patio - riser - tread - riser - tread - riser - interior floor = 3 risers = 3 steps

    Now, it may be possible that the height will allow for only 2 risers, but it sure looks higher than that to me.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Thomas Kirchner's Avatar
    Thomas Kirchner Guest

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Hmm, just a guesstimate here, but it looks like those blocks are approx. 1-1/2" thick. If that's the case, the owner might just be able to put 2 bonafide steps in, with the second step at or above the 1-1/2" below the threshold point.(thus 2 risers)
    That 'patio' looks thrown down just to get done and out, though, so the steps need to be independent of the patio.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    Quote Originally Posted by Thomas Kirchner View Post
    Hmm, just a guesstimate here, but it looks like those blocks are approx. 1-1/2" thick. If that's the case, the owner might just be able to put 2 bonafide steps in, with the second step at or above the 1-1/2" below the threshold point.(thus 2 risers)
    That 'patio' looks thrown down just to get done and out, though, so the steps need to be independent of the patio.
    Most of those are, I believe, 2" thick, that makes the taller stack 8" high, the siding is probably 6"+/-, with another 2" below the trim under the door, and another 2" for the trim under the door itself.

    That makes it (just guessing) 8" + 6" + 2" + 2" = 18" high to the underside of the door sill.

    To make two risers work the maximum height would need to be limited to 7-3/4" + 7-3/4" = 15-1/2" and that would be to the interior floor level, which I am presuming is the underside of the door sill.

    My best guess, then, is that it will take 3 risers to make those riser heights equal and legal in height.

    Charlie, did you measure the height to the underside of the sill, or to the top of the sill or to where (if anywhere)?

    Additionally, that top tread/landing needs to be as wide as the opening for both leaves of that door. The one shown is not even as wide as the one active leaf, but it needs to be as wide as both the active and the inactive leaves.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,153

    Default Re: DO I NEED A LANDING HERE OR PARACHUTE

    jp

    i did not measure, it was obvious, a landing or steps or parachute. recommended they get someone in to evaluate and repair. i also included my picture of landing and or steps in reportfrom home illustrated.

    charlie


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •