Results 1 to 21 of 21
  1. #1
    Edgar Abrego's Avatar
    Edgar Abrego Guest

    Default Location of water heater

    I did an inspection on a condo yesterday and the water heater was located in the laundry area. This in itself did not raise my curiosity. But the fact that I say laundry area and not room is the issue. The area is in the kitchen and is about 8ft wide by 4ft deep, it has accordian style doors and holds the water heater, a washer and dryer; as well as the location of the sub panel. I could barely get to the water heater not to mention get behind the washer and dryer ( I did a limited inspection of that area do to the access restraints) So my question is; is this a safety issue? I am going to recommend they move the water. Should I do this?

    Also the TPR valve in my opinion has too many bends ( see photo)? And let me know what you think.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    James Duffin's Avatar
    James Duffin Guest

    Default Re: Location of water heater

    I don't think the bends are a problem as long as the pipe is running downhill. My question would be where does the pipe discharge? It has to discharge in the room the heater is located and through a air gap if it is run out of the room.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Location of water heater

    Watts allows up to 4 elbows, there are 3 visible and likely at least 1 more.

    Being as this is a condo, that may be it as that 4th elbow *may* (or may not) take the discharge line to the riser into which it drains. I would not write it up unless I was convinced that there were more.

    Sounds like the submarine panel may have access and clearance problems, but then, it's only an 8 foot long submarine, so it might be okay.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    David R2's Avatar
    David R2 Guest

    Default a few questions.

    May not be a problem. Not too many elbows.

    Depending on a lot of factors, there may be a problem. Heater: electric? Condo: small wood structure, or big concrete structure? I don't know if that difference only applies where I am and not everywhere. Subpanel: facing towards or away or sideways? Under heater: pan? Etc.

    David


  5. #5
    Edgar Abrego's Avatar
    Edgar Abrego Guest

    Default Re: Location of water heater

    thanks for the reply's guys.

    David to answer you questions.

    1. Heater is natural gas

    2. Condo is single story wood frame.

    3. The Subpanel is facing the water heater directly, this is my main concern.

    4. No pan under water heater.


  6. #6
    David Banks's Avatar
    David Banks Guest

    Default Re: Location of water heater

    Quote Originally Posted by Jerry Peck View Post
    Watts allows up to 4 elbows, there are 3 visible and likely at least 1 more.

    Being as this is a condo, that may be it as that 4th elbow *may* (or may not) take the discharge line to the riser into which it drains. I would not write it up unless I was convinced that there were more.

    Sounds like the submarine panel may have access and clearance problems, but then, it's only an 8 foot long submarine, so it might be okay.
    Jerry are you saying the TPR valve can be discharged where it is not readily observable by the building occupants? How is it observable if to riser?
    I have done some condos and always called this out as how would people know they had a problem is they can not see it dripping?


  7. #7
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Location of water heater

    Edgar,
    If there is working space 36" in front of the heater and 30 inches wide, it's okay. If not, call it out, but don't expect that anything will change.

    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  8. #8
    David R2's Avatar
    David R2 Guest

    Default a bit scary. Code?

    edgar,

    this situation is too far from my experience to comment on. Condos in concrete highrises follow commercial regulations, in terms of where to place water heaters and also requiring the pressure release pipe to be piped (hardwired) into drain plumbing but separated far from bathroom groups drain plumbing. You don't want to "see" when water leaves the tank through this valve. (then the water damage repairs might have to be paid for by the entire condo association, depending on where water got to: even if it stayed inside your exclusive use living areas, some areas are deemed common property although exclusive for you to use.)

    sorry can't help more. Am curious as to whether or not condo buildings ever have to follow different building code rules. In California. In concrete structures. In wood structures. Etc.

    seems to me this info will determine whether or not the configuration is deemed one way or the other, acceptable or not.

    david


  9. #9
    Join Date
    Mar 2007
    Location
    Mustang
    Posts
    215

    Default Re: Location of water heater

    How do you post a new message on here?


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: a bit scary. Code?

    Quote Originally Posted by David R2 View Post
    Am curious as to whether or not condo buildings ever have to follow different building code rules. In California. In concrete structures. In wood structures. Etc.
    Regardless of the type of construction, condos are the same as apartment houses as far as occupancy goes and thus follow the 'building code'. If the code in that area also has a 'residential code', condos and apartment houses *do not* follow that 'residential code', they follow the 'building code'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    David R2's Avatar
    David R2 Guest

    Default Re: a bit scary. Code?

    Quote Originally Posted by Jerry Peck View Post
    Regardless of the type of construction...
    got it; then townhouse wood structure condos are 'building code', like apartment buildings. So that code applies here in Edgar's situation. It's not treated residential code even though it looks like the same frame and use as residential. Different rules apply.

    david


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Location of water heater

    Quote Originally Posted by David Banks View Post
    Jerry are you saying the TPR valve can be discharged where it is not readily observable by the building occupants? How is it observable if to riser?
    I have done some condos and always called this out as how would people know they had a problem is they can not see it dripping?
    The T&P discharge line can be piped to an air gap to the riser (some how or another it must eventually get to that riser), it's just a matter of locating the air gap where it can be seen by the occupants.

    Remember, water heaters *are not* designed nor intended to set in water, so if the water heater is set in a pan, the water heater needs to be raised up so that the bottom of the water heater is above the flood level rim of the pan - to keep the water heater dry and from rusting out (either that or provide documentation showing that the water heater is allowed to be installed partially submerged ).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    David Banks's Avatar
    David Banks Guest

    Default Re: Location of water heater

    (either that or provide documentation showing that the water heater is allowed to be installed partially submerged ).
    Can it be submerged with the Subpanel?


  14. #14
    Join Date
    Apr 2007
    Location
    state of jefferson
    Posts
    522

    Default Re: Location of water heater

    jerry,
    pans are required to have drains sooo wouldn't this prevent water heaters from being submerged in h20? duh!


  15. #15
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Location of water heater

    Not Jerry, but.... not until that hole is in the bottom of the pan and the pan elevated. Until then, the heater will be sitting in water. duh-duh.

    Last edited by Thom Walker; 06-11-2007 at 12:08 PM. Reason: dyslexic typing
    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: a bit scary. Code?

    Quote Originally Posted by David R2 View Post
    got it; then townhouse wood structure condos are 'building code', like apartment buildings.
    Nope.

    "Townhouses", i.e., which are owned fee simple from the ground below to the sky above, are considered 'attached single-family', and the IRC may be applied to them.

    However, as soon as the structure become "common property", then they are no longer "townhouses", but are "condos". To make this even more confusing, sometimes the ownership is set up such that each unit is a "townhouse", and each building is a group of "townhouses", but each building is part of a "condominium association" in that the common properties (pool, parking lots, etc.) are "condominium owned" by all of the townhouse home owners associations.

    Sounds complicated and weird? It is.

    So that code applies here in Edgar's situation. It's not treated residential code even though it looks like the same frame and use as residential. Different rules apply.
    He referred to it as a 'condo', thus I would suspect that they are indeed 'condos', in which case the IRC does not apply, the IBC and other I codes do (IPC, IMC, etc.)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Location of water heater

    Quote Originally Posted by Thom Walker View Post
    Not Jerry, but.... not until that hole is in the bottom of the pan and the pan elevated. Until then, the heater will be sitting in water. duh-duh.
    EVEN THEN ... the water heater is setting in water, ... unless the drain in the bottom of the pan is lower than the bottom of the pan and does not project up into the pan, i.e., a brazed on fitting projecting down from the bottom of the pan.

    As soon as you run a fitting up into ... duh! ... "INTO" ... the pan, the pan will hold water to the level of the top of the fitting.

    Double Duh-duh!

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Location of water heater

    Quote Originally Posted by David Banks View Post
    Can it be submerged with the Subpanel?
    Yeah, but that's what I would call really SUBmerged ... how deep is that pan?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  19. #19
    Join Date
    Nov 2010
    Location
    New Westminster BC
    Posts
    55

    Default Re: Location of water heater

    Remember, water heaters *are not* designed nor intended to set in water, so if the water heater is set in a pan, the water heater needs to be raised up so that the bottom of the water heater is above the flood level rim of the pan - to keep the water heater dry and from rusting out (either that or provide documentation showing that the water heater is allowed to be installed partially submerged ).[/QUOTE]

    if there is a pan direcly under the water heater, isn't its main purpose to collect water and safely drain it out after the tank has rusted out and is leaking water? If so why would we be concerned about the tank rusting because it's not raised above the pan? All the pans I have seen with electric water heaters are sitting directly on the bottom of the pan. Wht am I missing?


  20. #20
    tom daley's Avatar
    tom daley Guest

    Default Re: Location of water heater

    FWIW: The San Jose Ca. city code requires that 18" w/h stands in garages etc. must be secured to fixed points eg. framing, presumably as a seismic and/or bump precaution.

    In short, they require that:
    1. the w/h is strapped.
    2. that the w/h is braced tight against framing.
    3. any in-situ w/h stand be fixed.

    It's interesting that other appliances, similarly located, with ignition potential must also be raised 18", but no mention is made ref. the above three conditions.
    I have never seen an in-situ raised, or strapped, clothes dryer for instance!


  21. #21
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Location of water heater

    What a Thread over 5 years old and still ( what's it doing now ? )
    .

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •