Results 1 to 38 of 38
  1. #1
    daniel nantell's Avatar
    daniel nantell Guest

    Default RE; MOVING KITCHEN STOVE

    Just trying to get a consenus , does most inspectors pull kitchen stove out to check for gas shut off valves on Gas stoves and do you check for the anti -tip device to keep kids from turning stove over. What s the procedure for the anti-tip test. thanks

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by daniel nantell View Post

    does most inspectors pull kitchen stove out to check for gas shut off valves on Gas stoves
    Nope. ( but a Mirror & Flashlight will work for Ya.)
    do you check for the anti -tip device to keep kids from turning stove over.
    Yep.
    What s the procedure for the anti-tip test. thanks
    Open the Oven door to (insert thermometer ) grab the Back Splash & give a tug.
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: RE; MOVING KITCHEN STOVE

    In Texas, its the Law to do so.

    rick


  4. #4
    Clint White's Avatar
    Clint White Guest

    Default Re: RE; MOVING KITCHEN STOVE

    I bring my 7 year old son with me to stand on the open oven door.......kidding...just kidding....


  5. #5
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: RE; MOVING KITCHEN STOVE

    I usually demonstrate tipping the oven to the client and show them the warning label on the inside of the oven door.
    And I look behind for the proper gas connection, if gas.
    I do not measure the temp.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  6. #6
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by John Arnold View Post
    I usually demonstrate tipping the oven to the client and show them the warning label on the inside of the oven door.
    And I look behind for the proper gas connection, if gas.
    I do not measure the temp.
    ditto


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Rick Hurst View Post
    In Texas, its the Law to do so.

    rick

    Rick,

    To do which? Or both?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: RE; MOVING KITCHEN STOVE

    (d) Electric or gas ranges, cooktops, and
    ovens. The inspector shall report as Deficient:
    (1) inoperative unit(s);
    (2) the lack of a gas shut-off valve;
    (3) gas leaks; and
    (4) deficiencies in the:
    (A) controls and control panels;
    (B) thermostat(s) sensor support;
    (C) glass panels;
    (D) door gasket(s), hinges, springs,
    closure, and handles;
    (E) door latch;
    (F) heating elements or burners;
    (G) thermostat accuracy (within 25
    degrees at a setting of 350 °F);

    (H) drip pans;
    (I) lights and lenses;
    (J) clearance to combustible
    material;
    (K) anti-tip device;
    (L) gas shut-off valve(s) and
    location(s);
    (M) gas connector materials and
    connections; and
    (N) secure mounting of the unit.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Jim Luttrall View Post
    (d) Electric or gas ranges, cooktops, and
    ovens. The inspector shall report as Deficient:
    (1) inoperative unit(s);
    (2) the lack of a gas shut-off valve;
    (3) gas leaks; and
    (4) deficiencies in the:
    (A) controls and control panels;
    (B) thermostat(s) sensor support;
    (C) glass panels;
    (D) door gasket(s), hinges, springs,
    closure, and handles;
    (E) door latch;
    (F) heating elements or burners;
    (G) thermostat accuracy (within 25
    degrees at a setting of 350 °F);

    (H) drip pans;
    (I) lights and lenses;
    (J) clearance to combustible
    material;
    (K) anti-tip device;
    (L) gas shut-off valve(s) and
    location(s);
    (M) gas connector materials and
    connections; and
    (N) secure mounting of the unit.
    What! You don't have to report a dirty oven!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Scott Patterson View Post

    What! You don't have to report a dirty oven!
    .
    Or if The Self Cleaning feature is present ( if So How Clean were the Results After One Full Cycle.)

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: RE; MOVING KITCHEN STOVE

    This is what I was asking:

    Quote Originally Posted by daniel nantell View Post
    pull kitchen stove out
    Quote Originally Posted by Rick Hurst View Post
    In Texas, its the Law to do so.
    Quote Originally Posted by Jerry Peck View Post
    To do which? Or both?
    Pull the stove out to check for the gas valve?

    Pull the stove out to check for anti-tip?

    Still no answer to that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: RE; MOVING KITCHEN STOVE

    I gave you the law, that has the answer.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  13. #13
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Shoot, I even throw in an apple pie and bake it while I am inspecting. After the pie spills all over the oven I turn on the auto clean. When I cannot eat anymore pie I try out the garbage disposal and then of course the dish washer. After all that I need a cup of coffe and heat some water up in the micro wave. Of course I always drop some pie on my shirt and run the washing machine to see if the water drains down and does not over flow the pipe and in the mean time check the hot water temp and water pressure. Now after all that I have to use the facilities and try out a couple of the toilets and run the bath ceiling vents to see if I can get rid of the smell.

    Just another day of inspecting

    I forgot to add that while my clothes are drying I go up on the roof anf lift every shingle to check to make sure they are the proper fasteners and every shingle has the proper amout of fasteners. Now the cold is making me shiver and yeah know what happens next, I check that the gutters have the proper slope to drain water correctly and the down spouts are not clogged up.


  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Jim Luttrall View Post
    I gave you the law, that has the answer.

    Jim,

    Then I am blind and you will have to excuse me ... show me where it says you do, or do not, "have to move the stove".

    Thanks, and allow the blind man to see.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: RE; MOVING KITCHEN STOVE

    The inspector shall report as Deficient:
    (2) the lack of a gas shut-off valve;

    (4) deficiencies in the:

    (G) thermostat accuracy (within 25
    degrees at a setting of 350 °F);

    (K) anti-tip device;
    (L) gas shut-off valve(s) and
    location(s);

    No mention of moving anything but you must report.
    We are not required or expected to move furnishings.
    (a) Definitions.
    (1) Accessible--In the reasonable
    judgment of the inspector, capable of being
    approached, entered, or viewed without:
    (A) undue hazard to the inspector;
    (B) moving furnishings or large,
    heavy, or fragile objects;


    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  16. #16
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Shoot, I even throw in an apple pie and bake it while I am inspecting. After the pie spills all over the oven I turn on the auto clean. When I cannot eat anymore pie I try out the garbage disposal and then of course the dish washer. After all that I need a cup of coffe and heat some water up in the micro wave. Of course I always drop some pie on my shirt and run the washing machine to see if the water drains down and does not over flow the pipe and in the mean time check the hot water temp and water pressure. Now after all that I have to use the facilities and try out a couple of the toilets and run the bath ceiling vents to see if I can get rid of the smell.

    Just another day of inspecting

    I forgot to add that while my clothes are drying I go up on the roof anf lift every shingle to check to make sure they are the proper fasteners and every shingle has the proper amout of fasteners. Now the cold is making me shiver and yeah know what happens next, I check that the gutters have the proper slope to drain water correctly and the down spouts are not clogged up.
    .
    Well Ted,

    If Your only going to do Half of an Inspection Just Stay Home !

    * just over look those jack & plumbing boots. Not to mention No Mop & Glow in The Kitchen and Halls.

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Jim Luttrall View Post
    No mention of moving anything ...

    Jim,

    Thank you for the answer, no one gave that before, just posted the laws requirements and ignored the actual question.

    So the blind man was not blind after all. That is good.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    daniel nantell's Avatar
    daniel nantell Guest

    Default Re: RE; MOVING KITCHEN STOVE

    The gas range I have seen lately was impossible to see the gas line, shut off valve without moving the range out about 8 inches, I dont think its in our s.o.p to be moving ranges, I just state the line is not visible and cannot verify proper hook up, owner will have to follow up on moving the range to check for shut off valves and anti tip mech.

    Its impossible on a home inspection to know all applicance are working perfectly on a 2 or 3 hour inspection, example refrigarators dont go into a defrost cycle for another 6 hours, I guess we will wait till the defrost cycle occurs before we give the unit a all clear.


  19. #19
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: RE; MOVING KITCHEN STOVE

    Try removing the bottom drawer. On most newer stuff it is just and open cavity that gives you a pretty good view of the anti-tip bracket (or lack there of) and maybe if your lucky the gas line.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  20. #20
    Richard Stanley's Avatar
    Richard Stanley Guest

    Default Re: RE; MOVING KITCHEN STOVE

    You check refrigerators??
    I think Ted explained the appropriate procedure for appliance inspection.
    If you can't see the gas SO valve, it's not readily accessible.


  21. #21
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: RE; MOVING KITCHEN STOVE

    I always pull the bottom drawer also. Soemtimes it can be seen others it's not. But with all the crap under it I tell them to pull it out and clean it?

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  22. #22
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    I, myself, would NOT move any major kitchen appliance. Way to much liability if damage is caused to the floor!!

    Stove, if not visible by removing the bottom drawer, tag it as such.

    Would you "pull out" a refer with an ice maker to check for connections, shut off valve, or leaks in the line?

    If items to be checked are not eaisly visible, I consider what my liability would be before proceeding. And, note that in the report. The only other option is to get a release of liability when moving appliances.


  23. #23
    Jeff Mitchell's Avatar
    Jeff Mitchell Guest

    Default Re: RE; MOVING KITCHEN STOVE

    I would agree with Steven. Moving appliances is not really something an inspector should have to do and you must always consider the liability just in case. You never know if the client is going to call in later to report floor damage or something like that. And if the valves or line are not accessible, just note that.


  24. #24
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Jeff Mitchell View Post
    I would agree with Steven. Moving appliances is not really something an inspector should have to do and you must always consider the liability just in case. You never know if the client is going to call in later to report floor damage or something like that. And if the valves or line are not accessible, just note that.
    AND. have you ever seen what is "under" the appliance when it has not been moved if 30 years? YUCK!!!


  25. #25
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Checking the frig......Well, as Jerry does, I empty the frig of food and shelves....climb inside and close the door to see if the light goes off when the door is fully closed.


  26. #26
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Checking the frig......Well, as Jerry does, I empty the frig of food and shelves....climb inside and close the door to see if the light goes off when the door is fully closed.
    I empty the fridge, and take the good stuff home!!


  27. #27
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Checking the frig......Well, as Jerry does, I empty the frig of food and shelves....climb inside and close the door to see if the light goes off when the door is fully closed.
    I follow Ted and duct tape the frig. to prevent childeren from making the same mistake!!!


  28. #28
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Steven Meyer View Post
    I follow Ted and duct tape the frig. to prevent childeren from making the same mistake!!!
    If there are any kids handy, I make one of them stand on the open oven door to demonstrate the dangers of the range tipping. My advice: pick the heaviest kid. It makes for a more dramatic demonstration.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  29. #29
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Checking the frig......Well, as Jerry does, I empty the frig of food and shelves....climb inside and close the door to see if the light goes off when the door is fully closed.
    Same method for ovens??? Do you turn it to 350 to check the temp, or to self cleaning???


  30. #30
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Steven Meyer View Post
    Same method for ovens??? Do you turn it to 350 to check the temp, or to self cleaning???
    Again, make use of any kids that happen to be hanging around. I mean, be realistic. How many of us could fit in an oven?

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  31. #31
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Steven Meyer View Post
    Same method for ovens??? Do you turn it to 350 to check the temp, or to self cleaning???

    Only if I am looking a little to much on the white side. We Italian/Cherokee Indian/Irish folks have to have that combo of olive tan/red skin look to us or else we just don't look right. The self cleaning inside the oven is just a bit to much. Get kinda crispy looking thrying that one.


  32. #32
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Only if I am looking a little to much on the white side. We Italian/Cherokee Indian/Irish folks have to have that combo of olive tan/red skin look to us or else we just don't look right. The self cleaning inside the oven is just a bit to much. Get kinda crispy looking thrying that one.
    Thought maybe you were looking at the oven as a tanning booth.
    Being Irish we don't tan, we burn!!


  33. #33
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by John Arnold View Post
    Again, make use of any kids that happen to be hanging around. I mean, be realistic. How many of us could fit in an oven?
    A cat or small dog could work???


  34. #34
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by John Arnold View Post
    Again, make use of any kids that happen to be hanging around. I mean, be realistic. How many of us could fit in an oven?
    Of course, there is another option. Check the refer, pull out that T Bone steak, micro on defrost, broil it in the oven, enjoy a great lunch, and you have verified three appliances!!!

    And they say there are no benefits in this business!!

    Works, also, in "testing" that build in BBQ!!!

    Kinda like, "will work for food". one must think "out of the box"!!


  35. #35
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by Ted Menelly View Post
    Only if I am looking a little to much on the white side. We Italian/Cherokee Indian/Irish folks have to have that combo of olive tan/red skin look to us or else we just don't look right. The self cleaning inside the oven is just a bit to much. Get kinda crispy looking thrying that one.
    TED

    You are what is called a Kanardly! Can not hardly tell what you are!! Stay at a low oven temp!!!


  36. #36
    Steven Meyer's Avatar
    Steven Meyer Guest

    Default Re: RE; MOVING KITCHEN STOVE

    Quote Originally Posted by John Arnold View Post
    If there are any kids handy, I make one of them stand on the open oven door to demonstrate the dangers of the range tipping. My advice: pick the heaviest kid. It makes for a more dramatic demonstration.
    A bowling ball weighs more, the down side is the sucker has the tendancy to roll off on your foot!!


  37. #37
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: RE; MOVING KITCHEN STOVE

    I use the Ted approach. Put Ted in Frig close door, then write it up as *Failed while Teding* recommend replacement.

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  38. #38
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: RE; MOVING KITCHEN STOVE

    I used to pull on the back of the range to see if it lifted but then started to worry about breaking something or tearing off a piece of Formica. So I now pull the bottom drawer and look under as Jim said. I have found quite a few other problems while looking for the anti-tip. Sometimes there is a 240 outlet that is not fastened to the wall or floor, sometimes the leveling foot is on top of the 120v wire going to the controls, sometimes the anti-tip is fastened to the top of Pergo type flooring (my favorite), and sometimes you can find really neat toys!

    Use caution when removing the drawer as it can scratch wood or vinyl flooring when you set it to the side.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •