    Default Metal conduit grounding

    Is metal conduit considered a ground between a main panel and a sub panel?

    My thought is no but am questioning myself.

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal conduit grounding

    Quote Originally Posted by Mark Muehleisen View Post
    Is metal conduit considered a ground between a main panel and a sub panel?
    Well, the metal conduit is considered the grounding path between the service equipment and whatever the metal conduit is connected to.

    The same goes for metal conduit connected between two panel.

    When connected to a sub, through a marine cord, its panel, that metal conduit is typically rusted out due to the proximity to water.

    Now, though, there are conditions with regard to connecting metal conduit to the enclosures, typically this requires a grounding bushing, especially when the metal conduit is in a smaller concentric knock out located within large concentric knock outs. I even like to see grounding bushings used for eccentric knock outs as those only leave a small portion of the eccentric knock out contacting the enclosure. With 'punched' knock outs or full size knock outs, where the conduit lock nuts make contact with the enclosure all the way around the conduit at the lock nuts bent down locking tabs, well, I've even seen those with arc marks at the contact points.

    Use grounding type lock nuts and bushings so the ground terminals in the enclosure can be jumped (bonded) to the grounding lock nuts and bushings on the conduit.

    Getting back to your question, though, not many inspectors are lucky enough to inspect a house with a sub docked out back, much less get to go inside and see its panel.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Metal conduit grounding

    Attached

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Eric Barker, ACI
    Lake Barrington, IL

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Metal conduit grounding

    Eric,

    Excellent photo of why grounding type lock nuts and bushings are required for that.

    With a grounding type lock nut or bushing, there would be a bonding jumper connecting it to ground, to it would still be grounded (not that that would solve the mechanical problem, but at least it would still be electrically grounded).