Results 1 to 4 of 4
Thread: vehicle door opener needs GFCI?
06-08-2009, 01:22 PM #1
New construction. No vehicle door opener installed, but there is a receptacle outlet in the garage ceiling, marked "GFCI protected", but it isn't.
Is it not required to be because it isn't readily accessible?
Similar Threads:"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
06-08-2009, 01:35 PM #2
Re: vehicle door opener needs GFCI?
In the 2008 National Electrical Code Every Receptacle in the garage must be GFCI protected.
If the jurisdiction is still on the 2005 or earlier NEC then it is not a code requirement,just a good idea
06-08-2009, 02:42 PM #3
Ken - Thanks.
06-08-2009, 04:53 PM #4
And the supporting documentation for the removal of those GFCI exceptions was two-fold:
1) Because the appliance (the garage door opener) has been required to be made to a very low ground fault leakage for the past 20+ years.
2) Because, no fooling, it was improper *not to protect* tall people with GFCI protection when it is installed to protect all others, or when other-than-tall-people could not reach something it was okay to not protect it ... that argument no longer flies with the good technologies of today for GFCI and low ground fault leakage of appliances.