    What kind of fire separation is required in a residential stairway?

    Same thing for the elevator except that you have a box inside carrying you up and down.

    I.e., if you walked up a stairway and could look into the floor system because the floor system was open to the stairway, that would not be good, neither is it when you are in an elevator.

    I thought I had a photo of what I was referring to, but I cannot find it.

    When looking into the elevator shaft, the shaft should be lined, just like a stairway.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Residential Elevator Shaft

    Quote Originally Posted by Jerry Peck View Post
    What kind of fire separation is required in a residential stairway?

    Same thing for the elevator except that you have a box inside carrying you up and down.

    I.e., if you walked up a stairway and could look into the floor system because the floor system was open to the stairway, that would not be good, neither is it when you are in an elevator.

    I thought I had a photo of what I was referring to, but I cannot find it.

    When looking into the elevator shaft, the shaft should be lined, just like a stairway.
    JP: The shaft in question begins in a sub-grade or basement wine cellar and then services two floors above. I understand that it must be "lined", but with Type-X or standard 1/2" drywall? No other provisions apply?


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Residential Elevator Shaft

    1/2" gypsum is all it needs.

    It's not like it is an elevator shaft in a non-dwelling unit, where all the other fire resistance ratings also apply and then the elevator wall would need to be 1-2-3 hour fire resistance rated.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Residential Elevator Shaft

    Consider it a draft stop between floors and ceilings.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Residential Elevator Shaft

    Quote Originally Posted by Wayne Carlisle View Post
    Consider it a draft stop between floors and ceilings.
    Wayne,

    Huh?

    What is "it"?

    How would you draft stop the elevator shaft at the floor/ceiling locations?

    Are you referring to the 1/2" gypsum board lining the elevator shaft as the draft stop?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Sep 2008
    Location
    Texas
    Posts
    745

    Default Re: Residential Elevator Shaft

    "It" being the elevator shaft penetrates the floor and ceiling cavities. The elevator shaft in my opinion would need to be lined (1/2" sheetrock) where the shaft is open to keep a fire from traveling from the elevator shaft into a floor or ceiling cavity.

    You asked; Are you referring to the 1/2" gypsum board lining the elevator shaft as the draft stop?

    Yes

    This is the same thing as draftstopping. Stopping the fire from traveling into the floor/ceilng via the elevator shaft.


  8. #8
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Residential Elevator Shaft

    Same house, different question. The basement is about 900 s.f. Other than the elevator there will be a minimally-sized spiral stair unit. Are there certain restrictions regarding the spiral stair unit as regards emergency egress?


  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Residential Elevator Shaft

    Quote Originally Posted by A.D. Miller View Post
    Same house, different question. The basement is about 900 s.f. Other than the elevator there will be a minimally-sized spiral stair unit. Are there certain restrictions regarding the spiral stair unit as regards emergency egress?
    A spiral stair much meet the requirements for "Special Stairs" "Spiral Stairs".

    R311.5.8 Special stairways.
    Spiral stairways and bulkhead
    enclosure stairways shall comply with all requirements of
    Section R311.5 except as specified below.

    R311.5.8.1 Spiral stairways.
    Spiral stairways are permitted,
    provided the minimum width shall be 26 inches
    (660 mm) with each tread having a 7
    1/2-inches (190 mm)
    minimum tread depth at 12 inches from the narrower
    edge. All treads shall be identical, and the rise shall be no
    more than 9
    1/2 inches (241 mm). A minimum headroom
    of 6 feet 6 inches (1982 mm) shall be provided.

    R311.5.8.2 Bulkhead enclosure stairways.
    Stairways
    serving bulkhead enclosures, not part of the required
    building egress, providing access from the outside grade
    level to the basement shall be exempt from the requirements
    of Sections R311.4.3 and R311.5 where the maximum
    height from the basement finished floor level to
    grade adjacent to the stairway does not exceed 8 feet
    (2438 mm), and the grade level opening to the stairway is
    covered by a bulkhead enclosure with hinged doors or

    other approved means.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Residential Elevator Shaft

    So then, the owners have just finished off their 3rd bottle of Napa Zinfandel in the wine cellar when the fire sprinklers go off. They can't take the elevator during a fire, so they must run up a spiral stair unit with 26" wide treads and 9.5" risers only to end up in the center of the house where the fire is?


  11. #11
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Residential Elevator Shaft

    An elevator sgaft is no more than a staiway in a home. It can be open on each floor just as a staiway. Yes the floor cavities have to be sealed but the elevator needs nothing but a caged type enclosure for safety. The walls next to it on the first and second floor need drywall on them as a stairway.

    The door no matter what it is needs to be able to be secured while in operation. Again, no different than a starway other than safety measures.


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Residential Elevator Shaft

    Quote Originally Posted by A.D. Miller View Post
    So then, the owners have just finished off their 3rd bottle of Napa Zinfandel in the wine cellar when the fire sprinklers go off. They can't take the elevator during a fire, so they must run up a spiral stair unit with 26" wide treads and 9.5" risers only to end up in the center of the house where the fire is?
    Aaron,

    Ahhh ... but you did not ask the right question.

    You asked:
    The basement is about 900 s.f. Other than the elevator there will be a minimally-sized spiral stair unit. Are there certain restrictions regarding the spiral stair unit as regards emergency egress?
    I now see what you should have asked:
    'The basement is about 900 s.f. Other than the elevator there will be a minimally-sized spiral stair unit. Are there certain restrictions regarding emergency egress?'

    See the difference?

    - R310.1 Emergency escape and rescue required. Basements and every sleeping room shall have at least one operable emergency and rescue opening. Such opening shall open directly into a public street, public alley, yard or court. Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Where emergency escape and rescue openings are provided they shall have a sill height of not more than 44 inches (1118 mm) above the floor. Where a door opening having a threshold below the adjacent ground elevation serves as an emergency escape and rescue opening and is provided with a bulkhead enclosure, the bulkhead enclosure shall comply with Section R310.3. The net clear opening dimensions required by this section shall be obtained by the normal operation of the emergency escape and rescue opening from the inside. Emergency escape and rescue openings with a finished sill height below the adjacent ground elevation shall be provided with a window well in accordance with Section R310.2. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.
    - - Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2).

    That basement does not meet the exception, thus it requires EERO.

    All you have to do is ask what you really want to know.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Residential Elevator Shaft

    JP: I did ask the right question. You just answered the one I did not ask.