    Default TPR Question

    I don't see this method used in my area, most TPR is piped to the exterior (when they are piped at all) excluding that the pipe runs uphill is this set-up allowable.

    Thanks in advance

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: TPR Question

    Quote Originally Posted by Eldon (Scooter) Holliday View Post
    I don't see this method used in my area, most TPR is piped to the exterior
    To the exterior?

    Looks like that is pipe to a vent pipe.

    No, that is not allowed.

    That is also PVC, which is not allowed for that use.

    That whole set up is wrong.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: TPR Question

    Is that foam insulation on the water pipes all the way next to the draft hood?
    How is B-vent attached to hood?
    As JP, that TPR all wrong.

    Keep the fire in the fireplace.

  4. #4
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: TPR Question

    The T&P valve is all wrong. Can not tie into the Vent system for the building drains and not allowed to use PVC. Also where is the vacuum relief valve? Any time you have a water heater installed with any fixtures below it you need a vacuum relief valve installed on the cold water side after the shut off valve.


  5. #5
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: TPR Question

    What about the duct tape (which is combustible) being that close to the draft hood? Is there a base to support the idea that that is wrong as well? I mean a base other than my own imagination.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: TPR Question

    John,

    The duct tape is on the foam which Bob H. pointed out.

    The best answer is "It's all wrong.", if one needs more detail then we could make a list of what is included in "all wrong".

    Jerry Peck