Results 1 to 4 of 4
Thread: Distribution Panel
-
06-30-2009, 06:26 PM #1
Distribution Panel
There was a 600 service and this panel had three 200amp breakers. But my question is regarding the penetration into the lower left of the panel, it appears to be a get er done type of installatoin. Is it acceptable.
Similar Threads:
-
06-30-2009, 06:39 PM #2
Re: Distribution Panel
Mat,
Just to clarify your title - that is a distribution panel and not the service equipment, right?
If so, then am I correct to presume that the 200 amp breakers feed other distribution panels?
That is a (should be a) cable clamp and someone knocked out a small 1/2" knock out when cutting in the larger knock out. It looks like a cable clamp, so that would be okay (other than the opening left behind).
That smaller, missing, knock out opening now needs to be covered.
The question that I have and do not see in those photo is: Where are those larger neutrals for those feeders attached to at the neutral terminal bus? Are there that many large terminals present for those three large neutral conductors?
I see where they are connected, but cannot tell if the terminals they are in are the proper sized ones - especially the one hanging off the neutral terminal bus.
-
06-30-2009, 07:26 PM #3
-
06-30-2009, 08:05 PM #4
Re: Distribution Panel
I saw those, but still concerned about their sizes, however, mainly the add-on lug is what my question was about.
This is what I said about them:
I see where they are connected, but cannot tell if the terminals they are in are the proper sized ones - especially the one hanging off the neutral terminal bus.



Reply With Quote

Bookmarks