Results 1 to 59 of 59

Thread: Media rooms

  1. #1
    Join Date
    Mar 2007
    Location
    Houston, Texas
    Posts
    294

    Default Media rooms

    I got into an interesting debate with another inspector recently about media rooms. He came to me with a code perspective question regarding the need for a window (emergency escape and rescue opening ) and a smoke detector in a media room JUST IN CASE the room should ever be used as a spare bedroom by some future occupant.

    My perspective was that if the plans for the dwelling are approved by the local code authority without a window and smoke detector in the designated media room that dwelling is indeed in code compliant in that regard.

    My one caveat was that I would warn my client in the written report that the media room should never be used as a spare bedroom and let the client know why. I would be interested in knowing how others handle this circumstance.


    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    "...I would warn my client in the written report that the media room should never be used as a spare bedroom ..."

    I understand your concern, however, I do not think it nessasary report that it is not to be used as a bedroom.

    Would / do you also report the same if it were an, office, den, recreation room, dressing room...?

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Media rooms

    Quote Originally Posted by Rick Cantrell View Post
    "...I would warn my client in the written report that the media room should never be used as a spare bedroom ..."

    I understand your concern, however, I do not think it nessasary report that it is not to be used as a bedroom.

    Would / do you also report the same if it were an, office, den, recreation room, dressing room...?
    I agree with Rick.

    About 20% of the homes I inspect will have a "real" media room in them. They usually have special lighting, seating, and sound systems.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    He came to me with a code perspective question regarding the need for a window (emergency escape and rescue opening ) and a smoke detector in a media room JUST IN CASE the room should ever be used as a spare bedroom by some future occupant.
    PS: That need is very real if the room has a closet.

    My one caveat was that I would warn my client in the written report that the media room should never be used as a spare bedroom and let the client know why. I would be interested in knowing how others handle this circumstance.

    PS: I think you should mention it. I also mention this when offices or studies are incorporated into the floor plan with or without closets. Addi tonally, even though the media room may be specifically outfitted for just that purpose, I mention the desirability of the installation of a smoke alarm.


  5. #5
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    Quote Originally Posted by A.D. Miller View Post

    PS: That need is very real if the room has a closet.

    Not all bedrooms have closets,
    not all rooms with closets are bedrooms.

    The house being inspected is listed as X# bedrooms.
    If the room is not represented, presented or listed as being a bedroom and is not being used as a bedroom then no need to address possible future use as a bedroom.

    If the house is listed as X# of bedrooms and one of the bedrooms is being used for some other purpose, then it should be considered a bedroom on the report.
    Same thing goes when listed as "could be a 4 bedroom".

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  6. #6
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Media rooms

    I think one should always err on the side of caution... but I can see both sides in this.
    If the home is being bought be a reasonably affluent person that is apt to use the room as intended, I tend not to be too concerned, but if it is going to a large family and the need for another bedroom is apparent, then I make a big deal about it. Any doubt and I mention the lack of emergency egress, etc.
    Most newer homes I see tend to have the smoke detector in the media room even though it may not be required.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  7. #7
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Quote Originally Posted by Jim Luttrall View Post
    I think one should always err on the side of caution... but I can see both sides in this.
    If the home is being bought be a reasonably affluent person that is apt to use the room as intended, I tend not to be too concerned, but if it is going to a large family and the need for another bedroom is apparent, then I make a big deal about it. Any doubt and I mention the lack of emergency egress, etc.
    Most newer homes I see tend to have the smoke detector in the media room even though it may not be required.
    JL: I have done hundreds of inspections for families that were both reasonably affluent and large. Case in point many of the families headed by Indian engineers.

    Additionally, since an HI report is usually a point of future disclosure, it may stand to benefit the next property owners.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Phillip Stojanik View Post
    I got into an interesting debate with another inspector recently about media rooms. He came to me with a code perspective question regarding the need for a window (emergency escape and rescue opening ) and a smoke detector in a media room JUST IN CASE the room should ever be used as a spare bedroom by some future occupant.

    My perspective was that if the plans for the dwelling are approved by the local code authority without a window and smoke detector in the designated media room that dwelling is indeed in code compliant in that regard.

    My one caveat was that I would warn my client in the written report that the media room should never be used as a spare bedroom and let the client know why. I would be interested in knowing how others handle this circumstance.
    The IRC requires minimum natural light of 8% of the floor area and minimum natural ventilation of 4% of the floor area, and, if a "sleeping room" (bedroom) then the room requires EERO sized windows.

    Except ... the 2006 IRC includes a change in that which allows for rooms ("media room" is not named by name) to not have natural light and ventilation.

    CAN a media room with no window be used as a bedroom at some point in the future? Sure, just like a kitchen CAN be used as a bedroom, and just like a living room CAN be used as a bedroom, and doing so would violate the codes.

    Now, when a window is installed, and if the room is suitable for use as a bedroom, such as it has a smoke detector inside and outside and there is a closet which could serve as a clothes closet, then I would look for the window to also meet EERO sizes.

    Otherwise (no closet, no smoke detector, just a window) the window would need to meet the 8%/4% requirements.

    Does this get into a dark and dirty area? Yes, like basements did, and basements now must have an EERO *even if not used for living space* - because the code recognizes that it likely will be at some point in time, probably the day after final inspection.

    Thus I would not be surprised to see changes to that exception in future code editions, especially after a couple of people die in them. I can imagine the code eventually treating them like basements - at least one EERO and a smoke detector. By default, then, they would meet the requirements for sleeping rooms even though they may not have a closet - but that will likely be several code cycles away, depends on how soon people start dying in those room.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Scott Murdock's Avatar
    Scott Murdock Guest

    Default Re: Media rooms

    Hope it this is not a stupid question but speaking from the point of view of a past Realtor you should not list any room that does not have a window and a closet as a bedroom (even tho it happens all the time). Now as an inspector do we have some ethical or otherwise obligation to let people know what a room may be used for in the future? Seems to be a crystal ball question that could be applied to any room of the house so I would not note it unless it was expressly said to me by the client that someone was going to sleep in the kitchen or whatever room in question.


  10. #10
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Thus I would not be surprised to see changes to that exception in future code editions, especially after a couple of people die in them. I can imagine the code eventually treating them like basements - at least one EERO and a smoke detector. By default, then, they would meet the requirements for sleeping rooms even though they may not have a closet - but that will likely be several code cycles away, depends on how soon people start dying in those room.
    JP: Yep. Just like nearly everything else in the code, it is all about body count.


  11. #11
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    " it is all about body count"

    I heard that the bathroom is where the most deaths happen.
    Have a heart attack, strain to hard.
    Don't know if it's true or not.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  12. #12
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Media rooms

    No window in our media room. Can't imagine having one. The light f's with the movie screen.

    We do have a smoke detector, and a phone.

    If there is a fire, I'm eating my way through the drywall, kickin out some bricks and jumping to the ground while holding onto my DLP 1080 projector.

    No window, I'm not skeered.

    rick


  13. #13
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Media rooms

    Quote Originally Posted by Phillip Stojanik View Post
    I got into an interesting debate with another inspector recently about media rooms. He came to me with a code perspective question regarding the need for a window (emergency escape and rescue opening ) and a smoke detector in a media room JUST IN CASE the room should ever be used as a spare bedroom by some future occupant.

    My perspective was that if the plans for the dwelling are approved by the local code authority without a window and smoke detector in the designated media room that dwelling is indeed in code compliant in that regard.

    My one caveat was that I would warn my client in the written report that the media room should never be used as a spare bedroom and let the client know why. I would be interested in knowing how others handle this circumstance.

    Patewy

    If it is listed as a three bedroom 3 bath home and a media room then that is what it is.

    You are not responcible for future inhabitants plans for the home.....Period.

    Aaron is blowing smoke. A lot of media rooms have closets for the equipment. Now if you were to smoke the same stuff Aaron does then you may be second guessing yourself on that one as your mind would be wondering.

    Now if they ask you specifically about its use as a bedroom then I guess you should answer that question with the disclaimer that the room is a media room at this time and future use as a bedroom would call for different safety issues.

    A little edit here

    JP is smoking the same stuff as Aaron (hmm, Aaron with 2 A's ) A media room is a media room. The pain in the butt for windows in it is absurd. Youn are defeating the idea of a media room.

    Now RH is not blowing any smoke or anything else. A smoke detector would be a smart choice as when you are watching an awsome movie with lots of sound and you are getting rumbled out of yur chair you may want a smoke detector to alert you of a fire.

    Last edited by Ted Menelly; 07-10-2009 at 07:19 PM.

  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Rick Hurst View Post
    No window in our media room. Can't imagine having one. The light f's with the movie screen.
    Rick,

    Probably 90% or so of the media rooms I inspected had windows with heavy drapes and *NO* light coming in.

    In a few AHJ I did find media rooms with no windows (most did not allow that) and I pointed that out to my clients. They did not want the windows, nonetheless, though, *I* pointed it out to them and put it in my report so that *THEY* could not come back to me later when they went to sell and say "Why didn't you tell me I would need to put a window in when I went to sell?" My answer would have been "*I* *DID* tell you and *I* *DID* put it in the report, and *I* did go over it with you, and *YOU* insisted on not wanting a window, here it is in my report."

    *I* feel we owe it to our clients to point things like that out to them.

    *I* also feel it is their final decision, but I want it on record that I told them about it and discussed it with them.

    Some day media rooms will go out of fashion and then they will want to use that space for something else, and that something else *WILL* need a window.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Media rooms

    Quote Originally Posted by A.D. Miller View Post
    JL: I have done hundreds of inspections for families that were both reasonably affluent and large. Case in point many of the families headed by Indian engineers.

    Additionally, since an HI report is usually a point of future disclosure, it may stand to benefit the next property owners.

    Now I know it is PROPER English I can not stand it when folks use the an word before home inspection. I could care less how proper it is. It just looks and sounds improper.

    An Home inspection report or A home inspection report. Certain usage might sound better as an but in most instances a is just fine. What a crazy language we have.


  16. #16
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Media rooms

    Quote Originally Posted by Ted Menelly View Post
    Now I know it is PROPER English I can not stand it when folks use the an word before home inspection. I could care less how proper it is. It just looks and sounds improper.

    An Home inspection report or A home inspection report. Certain usage might sound better as an but in most instances a is just fine. What a crazy language we have.
    I don't know where this came from, but here is the rule:
    Ted, "An" apple "A" boy. "An" precedes a word which starts with a vowel (A,E,I,O,U).
    "An Home inspection" would be incorrect; at least where I went to school.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Ted Menelly View Post
    Now I know it is PROPER English I can not stand it when folks use the an word before home inspection. I could care less how proper it is. It just looks and sounds improper.

    An Home inspection report or A home inspection report. Certain usage might sound better as an but in most instances a is just fine. What a crazy language we have.

    Now that you have brought of proper use of English ...

    "I could care less how proper it is" really should be 'I could NOT care less how proper it is'.

    When you say "I could care less" you are saying that you "could" care less, which is the opposite of what you meant to say.

    The saying really is "I couldn't care less".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    I don't understand what you mean?

    "Now that you have brought of proper use of English "

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  19. #19
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Media rooms

    Quote Originally Posted by fritzkelly View Post
    I think I may be in an parallel universe where 'An Home Inspection' is correct and Ted is correcting people's grammar!
    (A universe or an universe, Jim??)
    "A" parallel universe or "An" universe which is parallel.
    Something is wrong if "I" am correcting grammar or spelling. Just ask my wife the teacher!

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  20. #20
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Media rooms

    Quote Originally Posted by Jerry Peck View Post
    Rick,

    Probably 90% or so of the media rooms I inspected had windows with heavy drapes and *NO* light coming in.

    In a few AHJ I did find media rooms with no windows (most did not allow that) and I pointed that out to my clients. They did not want the windows, nonetheless, though, *I* pointed it out to them and put it in my report so that *THEY* could not come back to me later when they went to sell and say "Why didn't you tell me I would need to put a window in when I went to sell?" My answer would have been "*I* *DID* tell you and *I* *DID* put it in the report, and *I* did go over it with you, and *YOU* insisted on not wanting a window, here it is in my report."

    *I* feel we owe it to our clients to point things like that out to them.

    *I* also feel it is their final decision, but I want it on record that I told them about it and discussed it with them.

    Some day media rooms will go out of fashion and then they will want to use that space for something else, and that something else *WILL* need a window.

    If it does go out it going to be some time down the road. Jerry, I'm seeing people spending litterally thousands upon thousands of bucks on media room equipment. I call them Man Caves.

    The stores that sells the stuff here in Dallas is booming. You see now on the highway more trucks that do Home Theatre work than you see Pest Control trucks anymore.

    Nothing like having a 120 inch movie screen in your own pitch black room without a window. Fad, I don't think so.

    Wait and see how many people start converting those 2 car garages into media rooms.

    rick


  21. #21
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Rick Cantrell View Post
    I don't understand what you mean?

    "Now that you have brought of proper use of English "
    Oh dear ... it affects us all ... ... I meant to say "brought up".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  22. #22
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Rick Hurst View Post
    Nothing like having a 120 inch movie screen in your own pitch black room without a window. Fad, I don't think so.
    It is, some things take a while to catch on, build up steam, then interest is lost and it is on to something else, maybe a decade or two later, but it has taken a decade or more for the fad to catch on, so it will naturally take a while to fade out.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  23. #23
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Media rooms

    Jerry,

    Today while spending what seen a lifetime in an attic 150 degrees, I thought about attic saunas and wondered if they'd be poplar.

    Nah!

    rick


  24. #24
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Rick Hurst View Post
    Jerry,

    Today while spending what seen a lifetime in an attic 150 degrees, I thought about attic saunas and wondered if they'd be poplar.

    Nah!

    rick
    They are with home inspectors! Home inspectors just cannot wait to get in 1-2-3 times per day.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  25. #25
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Media rooms

    Jerry,
    So according to the 06 IRC you can have a basement media room w/0 windows and artificial ventilation. The reason I ask is because I just inspected a place Tues with a basement media room that was about 1500 square feet. No windows or ventilation. Had in floor radiant. The room was really musty. Built in 2008.


  26. #26
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Quote Originally Posted by fritzkelly View Post
    I think I may be in an parallel universe where 'An Home Inspection' is correct and Ted is correcting people's grammar!
    (A universe or an universe, Jim??)
    FK: I think it's duck and cover time . . .


  27. #27
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by mathew stouffer View Post
    Jerry,
    So according to the 06 IRC you can have a basement media room w/0 windows and artificial ventilation. The reason I ask is because I just inspected a place Tues with a basement media room that was about 1500 square feet. No windows or ventilation. Had in floor radiant. The room was really musty. Built in 2008.
    Not really allowed (note exception I've underlined and commented on below the code text), because basements are specifically stated as requiring an EERO.

    From the 2006 IRC. (bold and underlining is mine)
    - R310.1 Emergency escape and rescue required. Basements and every sleeping room shall have at least one operable emergency and rescue opening. Such opening shall open directly into a public street, public alley, yard or court. Where basements contain one or more sleeping rooms, emergency egress and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Where emergency escape and rescue openings are provided they shall have a sill height of not more than 44 inches (1118 mm) above the floor. Where a door opening having a threshold below the adjacent ground elevation serves as an emergency escape and rescue opening and is provided with a bulkhead enclosure, the bulkhead enclosure shall comply with Section R310.3. The net clear opening dimensions required by this section shall be obtained by the normal operation of the emergency escape and rescue opening from the inside. Emergency escape and rescue openings with a finished sill height below the adjacent ground elevation shall be provided with a window well in accordance with Section R310.2. Emergency escape and rescue openings shall open directly into a public way, or to a yard or court that opens to a public way.
    - - Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2).

    Note that if the basement has one or more sleeping rooms AND other rooms, such as the media room, then, no, an EERO would not be required "in the media room" but would be required in *each* sleeping room.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  28. #28
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    This is probably an old argument, but is a media room actually considered a "sleeping room" and subject to emergency egress and window reqirements?

    Not in my opinion as that is not it's intended purpose.


  29. #29
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    Michael
    "but is a media room actually considered a "sleeping room" ..."

    No, unless it is a sleeping room being used as a media room.

    "...and subject to emergency egress and window requirements?"

    No
    Unless, the media room is in the basement, then, yes it must have EERO.
    Exception; If there is 1 or more bedrooms in the basement, which are required to have and do EERO in them, then the basement is not required to have an EERO.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  30. #30
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Quote Originally Posted by Rick Cantrell View Post
    Michael
    "but is a media room actually considered a "sleeping room" ..."

    No, unless it is a sleeping room being used as a media room.

    "...and subject to emergency egress and window requirements?"

    No
    Unless, the media room is in the basement, then, yes it must have EERO.
    Exception; If there is 1 or more bedrooms in the basement, which are required to have and do EERO in them, then the basement is not required to have an EERO.
    Trust me I get it.

    But what if there is no bedroom and only a family room and bathroom? Hmmm?

    No required in my understanding but I have heard other proclaim the need anyway.

    I see a fair amount of media rooms under the garage slab with no windows. Makes for a nice quite and dark experience.


  31. #31
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Michael Larson View Post
    Trust me I get it.

    But what if there is no bedroom and only a family room and bathroom? Hmmm?

    No required in my understanding but I have heard other proclaim the need anyway.
    In a basement? EERO *IS* required ... period (if there are no sleeping rooms as you stated).

    EVERY basement MUST have an EERO unless the basement meets this exception: "Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2)."

    ONLY IF ... there is a sleeping room in the basement do the other areas not require an EERO.

    You said "Trust me I get it." then asked "But what if there is no bedroom and only a family room and bathroom?", which indicates that you do not "get it" - otherwise you would not have asked that question.

    Or would you like to try again and go back and rephrase your statement and question?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  32. #32
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Quote Originally Posted by Jerry Peck View Post
    In a basement? EERO *IS* required ... period (if there are no sleeping rooms as you stated).

    EVERY basement MUST have an EERO unless the basement meets this exception: "Exception: Basements used only to house mechanical equipment and not exceeding total floor area of 200 square feet (18.58 m2)."

    ONLY IF ... there is a sleeping room in the basement do the other areas not require an EERO.

    You said "Trust me I get it." then asked "But what if there is no bedroom and only a family room and bathroom?", which indicates that you do not "get it" - otherwise you would not have asked that question.

    Or would you like to try again and go back and rephrase your statement and question?
    I ask questions to promote discussion instead of your typical pontifications.

    Get over yourself please.

    Of course a basement with a media room and no bedrooms requires another escape route and I would call it out if it isn't there.

    Typically a basement walkout to grade is what is seen in this area through a sliding patio door.

    Now move along as there is really nothing for you to complain about here.


  33. #33
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Michael Larson View Post
    I ask questions to promote discussion instead of your typical pontifications.

    Get over yourself please.
    Oh, I get it ... *YOU* can say things like that to others, but *OTHERS* cannot say things like that to *YOU* ... oh, how childish you are - you have no problem dishing it out, but you cannot take it back? What a wimpette!

    Now move along as there is really nothing for you to complain about here.
    Yep, you need to move along and quit complaining about what others post as you cannot accept the same about your posts. Sheesh! I figured you as a two faced wimp, but you beat that - you are a two faces wimpette.

    Michael, grow up. Either shut up or put up with what you do to others.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  34. #34
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Michael, grow up. Either shut up or put up with what you do to others.
    JP: Don't you know that ML is actually Peter Pan? He will never grow up.


  35. #35
    Mark Howe's Avatar
    Mark Howe Guest

    Default Re: Media rooms

    Quote Originally Posted by Jim Luttrall View Post
    I don't know where this came from, but here is the rule:
    Ted, "An" apple "A" boy. "An" precedes a word which starts with a vowel (A,E,I,O,U).
    "An Home inspection" would be incorrect; at least where I went to school.
    Hi Jim,
    That is not really correct. The use of indefinite articles is dependent on the sound of the vowell, not the vowell itself. For instance, the consanant 'F' begins with a vowell sound (eff), so if you were to say "I got a F on my report card", you would be wrong. The word 'historic' or the phrase 'Home Inspector' begin with a "sounded" 'H', so you would use 'a' not 'an'. The word 'hour' begins with a vowell sound (ow), so, 'an' would be correct.

    Some believe that the American misuse of 'an' before 'historic' and other sounded 'H' words has its roots in the English (as in The U.K.) pronunciations ('istoric; 'ome inpector; etc.), where the article 'an' would be correct.


    Tim


  36. #36
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Quote Originally Posted by Mark Howe View Post
    Hi Jim,
    That is not really correct. The use of indefinite articles is dependent on the sound of the vowell, not the vowell itself. For instance, the consanant 'F' begins with a vowell sound (eff), so if you were to say "I got a F on my report card", you would be wrong. The word 'historic' or the phrase 'Home Inspector' begin with a "sounded" 'H', so you would use 'a' not 'an'. The word 'hour' begins with a vowell sound (ow), so, 'an' would be correct.

    Some believe that the American misuse of 'an' before 'historic' and other sounded 'H' words has its roots in the English (as in The U.K.) pronunciations ('istoric; 'ome inpector; etc.), where the article 'an' would be correct.


    Tim
    If you are attempting to make literati of these guys you have a hard row to hoe, my friend. And, you might invest in a dictionary yourself. You will likely not find the words "vowell" or "consanant" therein. But, I applaud your attempt to get them to work on their pronunciation.


  37. #37
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Thus, one would be correct in saying "a home inspection" and "an HI" (acknowledging the semi-correctness of the use of "HI" as a made up abbreviation for "home inspection" which we use here).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  38. #38
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Mr. Peck,

    I have observed you on this message board for 4 years.

    You are arrogant, unnecessarily condescending and on top of that an unapologetic Bush hater which makes me question a number of things about your character. So when I poke at you don't acted all hurt. It's just my way of getting your goat.

    Yes, you need to get over yourself.

    The world will survive just fine without your presence.

    Have a nice day.


  39. #39
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Media rooms

    Quote Originally Posted by Mark Howe View Post
    Hi Jim,
    That is not really correct. The use of indefinite articles is dependent on the sound of the vowell, not the vowell itself. For instance, the consanant 'F' begins with a vowell sound (eff), so if you were to say "I got a F on my report card", you would be wrong. The word 'historic' or the phrase 'Home Inspector' begin with a "sounded" 'H', so you would use 'a' not 'an'. The word 'hour' begins with a vowell sound (ow), so, 'an' would be correct.

    Some believe that the American misuse of 'an' before 'historic' and other sounded 'H' words has its roots in the English (as in The U.K.) pronunciations ('istoric; 'ome inpector; etc.), where the article 'an' would be correct.

    Tim
    Like I said, "Something is wrong if "I" am correcting grammar or spelling. Just ask my wife the teacher!"
    I guess I learned the rule but not the exceptions!
    Articles: A versus An - The OWL at Purdue

    Last edited by Jim Luttrall; 07-11-2009 at 01:34 PM.
    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  40. #40
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    You are arrogant, unnecessarily condescending and on top of that an unapologetic Bush hater
    JP: I would wear that like a badge, if I were you.


  41. #41
    Mark Howe's Avatar
    Mark Howe Guest

    Default Re: Media rooms

    Quote Originally Posted by A.D. Miller View Post
    If you are attempting to make literati of these guys you have a hard row to hoe, my friend. And, you might invest in a dictionary yourself. You will likely not find the words "vowell" or "consanant" therein. But, I applaud your attempt to get them to work on their pronunciation.
    I guess I do need to spell check more regularly. I do own several dictionaries; BTW, I just use them for more important writing, not for extemporaneous writing on web forums. Thanks for the correction though; the fact that you would take time out from your busy day to point out someone’s mistakes, is...well....typical (and painfully boorish). My reply, just so you know, was regarding the use of indefinite articles, not pronunciation...but I digress.

    I was attempting to add clarity to the question of the proper use of indefinite articles. My purpose was not to point out Jim’s possible misunderstanding of the 'rule', but to add something to the discussion.

    Thanks again for pointing out my spelling errors. I am on a constant quest for literacy and I take my lessons wherever I can get them.

    KOKO

    Tim

    Last edited by Mark Howe; 07-11-2009 at 03:41 PM.

  42. #42
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Media rooms

    Quote Originally Posted by Rick Hurst View Post
    Jerry,

    Today while spending what seen a lifetime in an attic 150 degrees, I thought about attic saunas and wondered if they'd be poplar.

    Nah!

    rick
    The bottom of the sheathing in the attic of a home (if you want to call it that...dump)

    148 degrees

    Gitter done...........................................or what ever that phrase is

    Oh yeah

    I aint not gonna cowect no one# no how! none more& about dare usahg of Engwish

    By the way. I guess I am like many others. Sometimes I just throw things in there to see what if anything will come back. It breaks the monotony.


  43. #43
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Media rooms

    Quote Originally Posted by Mark Howe View Post
    I was attempting to add clarity to the question of the proper use of indefinite articles. My purpose was not to point out Jim’s possible misunderstanding of the 'rule', but to add something to the discussion.
    Tim
    I, for one, thank you for the information.
    I need all the help I can get.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  44. #44
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Larson,

    Seems that someone (me) doing to you as you do to others (most often me) has got your goat alright.

    Guess that makes you two faced in that you can give it but you cannot take it.

    Like if full of cowards like you. If you cannot take "it" (whatever "it" is) then you should be controlling yourself and not giving "it" out.

    I KNEW my post would spark a fire under you because I KNEW you could not take what you dish out.

    As I said, either grow up and take it like a man or shut up and quit whimpering like a kid caught with their hand in the cookie jar.

    By the way, I think you spilled something on your pants ... or did you wet them ...

    Grow up and learn to take it or shut up.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  45. #45
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Quote Originally Posted by Jerry Peck View Post
    Larson,

    Seems that someone (me) doing to you as you do to others (most often me) has got your goat alright.

    Guess that makes you two faced in that you can give it but you cannot take it.

    Like if full of cowards like you. If you cannot take "it" (whatever "it" is) then you should be controlling yourself and not giving "it" out.

    I KNEW my post would spark a fire under you because I KNEW you could not take what you dish out.

    As I said, either grow up and take it like a man or shut up and quit whimpering like a kid caught with their hand in the cookie jar.

    By the way, I think you spilled something on your pants ... or did you wet them ...

    Grow up and learn to take it or shut up.
    Keep believing your own lies Peck.

    The truth hurts sometimes.


  46. #46
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Michael Larson View Post
    The truth hurts sometimes.
    So now you are admitting it, huh? It hurts less not that you have accepted it and can smile about it.

    Very good, acceptance is the first step toward recovery, you may be on your way. Will have to see what you next posts are like.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  47. #47
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Quote Originally Posted by Jerry Peck View Post
    So now you are admitting it, huh? It hurts less not that you have accepted it and can smile about it.

    Very good, acceptance is the first step toward recovery, you may be on your way. Will have to see what you next posts are like.
    You've been tipping a few too many back I see.

    Watch out for elbow injuries.


  48. #48
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Media rooms

    I should have been more specific. This media room was attached to the basement, which had the required egress. The house was pretty big. But, the theater room had no ventilation. I thought this was required.


  49. #49
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Media rooms

    Quote Originally Posted by Michael Larson View Post
    You've been tipping a few too many back I see.

    Watch out for elbow injuries.
    Michael,

    Your posts confirm what I am saying.

    (sigh)

    Carry on if you must continuing confirming your idiocy in actions, but carry on without me.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  50. #50
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Media rooms

    Quote Originally Posted by mathew stouffer View Post
    I should have been more specific. This media room was attached to the basement, which had the required egress. The house was pretty big. But, the theater room had no ventilation. I thought this was required.
    Code....no code....Any room of any size that does not have ventilation including large walk in closets...I write up and always have. That is just the brink and over the brink not to ad ventilation in any room of size in a home. Even if it were to keep it from getting stuffy and musty or just hot or cold or stale clothes etc.

    All rooms and any size other than small closets need ventilation.

    Last edited by Ted Menelly; 07-12-2009 at 10:04 AM.

  51. #51
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Media rooms

    Quote Originally Posted by Ted Menelly View Post
    Code....no code....Any room of any size that does not have ventilation including large walk in closets...I write up and always have. That is just the brink and over the brink not to ad ventilation in any room of size in a home. Even if it were to keep it from getting stuffy and musty or just hot or cold or stail clothes etc.

    All rooms and any size other than small closets need ventilation.
    TM: Would you pleeeeeeeeeeeaze go to:

    ieSpell - Download

    and install the software and then use it? Or, alternately I guess you could just continue to sit there on your front porch and roll doobies with the dictionary pages.


  52. #52
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Media rooms

    Quote Originally Posted by A.D. Miller View Post
    TM: Would you pleeeeeeeeeeeaze go to:

    ieSpell - Download

    and install the software and then use it? Or, alternately I guess you could just continue to sit there on your front porch and roll doobies with the dictionary pages.

    One wrong out of 70 to 80 words....Geeeesh...I would think you would be telling me of *complete thoughts* and *better grammer* since on here I completely stink at that. At least some times I hit the abc button with the check mark below it. Whatever that means.................

    Oh yeah....there is an s in please not a zzzzzzzzzzzz...But I get it


  53. #53
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: Media rooms

    Quote Originally Posted by Jerry Peck View Post
    Michael,

    Your posts confirm what I am saying.

    (sigh)

    Carry on if you must continuing confirming your idiocy in actions, but carry on without me.
    Just returning the favor and tone of what you post.

    Hope you're up for it.


  54. #54
    dsuser896's Avatar
    dsuser896 Guest

    Default Re: Media rooms

    that sounds outrageous to me. I think the guy's just being picky.


  55. #55
    john_opwin's Avatar
    john_opwin Guest

    Default Re: Media rooms

    When we think about media room the fist thing that comes to mind are chairs, sofas, recliners etc which can provide comfort to spend a couple of hours in media room.


  56. #56
    Join Date
    Apr 2009
    Location
    Melbourne, FL
    Posts
    182

    Default Re: Media rooms

    I sleep in my media room, don't has no window, hope I don't has an home inspection.


  57. #57
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: Media rooms

    Quote Originally Posted by Thomas McKay View Post
    I sleep in my media room, don't has no window, hope I don't has an home inspection.
    So, hooked on phonics didn't work?


  58. #58
    john_opwin's Avatar
    john_opwin Guest

    Default Re: Media rooms

    Scott is probably right........


  59. #59
    Join Date
    Mar 2007
    Location
    Colorado Springs, CO
    Posts
    1,217

    Default Re: Media rooms

    Quote Originally Posted by Thomas McKay View Post
    I sleep in my media room, don't has no window, hope I don't has an home inspection.
    Quote Originally Posted by Rick Hurst View Post
    So, hooked on phonics didn't work?
    What's the problem, Rick? SpellCheck didn't find any problems with that sentence.

    "Baseball is like church. Many attend but few understand." Leo Durocher
    Bruce Breedlove
    www.avaloninspection.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •