Results 1 to 13 of 13
  1. #1
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default B Vent Window Clearance

    This B vent for furnace and water heater is about 5 feet from the operable window. I noted the clearance less than 8 feet to the sidewall, but I thought there was something else about being so close to an operable window. Anyone else know of this?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Jim Robinson
    New Mexico, USA

  2. #2
    Brian E Kelly's Avatar
    Brian E Kelly Guest

    Default Re: B Vent Window Clearance

    That vent pipe should be above the side roof line by a min. of 3 ft. unless the peak of the higher roof is less than 10' away and then it should be 3' above that.


  3. #3
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: B Vent Window Clearance

    2 feet and 8 feet for gas. I got that part. I was wondering about the window, although I guess you can't have a window without a sidewall, so the question may be irrelevant for this application. 3 / 10 is for wood burning flues.

    Jim Robinson
    New Mexico, USA

  4. #4
    Brian E Kelly's Avatar
    Brian E Kelly Guest

    Default Re: B Vent Window Clearance

    The 3/10 rule also goes for gas in my neck of the woods.


  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Question Re: B Vent Window Clearance

    Do you have a better pic of just the termination? It appears someone cut a hole in the lid and ran a pipe inside a pipe. I see two distinct terminations. Maybe they're mating?

    Keep the fire in the fireplace.

  6. #6
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: B Vent Window Clearance

    That's the only picture I had. It was a pretty straightforward vent. There are some type of vents along the side of the pipe near the top on the outside, but they weren't connected to the flue pipe at all.

    Jim Robinson
    New Mexico, USA

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: B Vent Window Clearance

    Bob,

    Looks like they (whoever "they" are) used one of those flat top four sided vents, cut the top out, then ran the vent up through it and installed a Type Gas Vent Cap on top.

    Probably because a previous inspector said 'That four sided vent cap is wrong, so Mr. Handy Dandy homeowner "fixed it".

    Of course, though, that would lead me to suspect that the vent inside is not a Type B vent, but the old single wall vent which was likely in it originally.

    Don't forget that plumbing vent too. 10 feet from the operable window or other building opening or 2 feet above it. If the gas vent is 5 feet from the window, so is the plumbing vent.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: B Vent Window Clearance

    Exactly my point Jerry. Don't get caught up in the humdrum such as clearances and miss the larger issue. This was tampered with or modified. Remember my warnings about red flags? Where you see one goofy thing, you're bound to find more? (yes, you can write "goofy" in your reports--They will know you're a down to earth kinda guy!) Seriously, take the holistic approach.

    Just to tease you some more: does this vent require roof bracing? How do you brace vents on flat roofs? How do you penetrate the roof deck on a flat roof? That'll keep you busy for awhile! Gotta scoot. I hear a roof calling me.

    Keep the fire in the fireplace.

  9. #9
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: B Vent Window Clearance

    You think this one is a bit close.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  10. #10
    Join Date
    May 2007
    Location
    Frankfort, KY
    Posts
    326

    Default Re: B Vent Window Clearance

    Hope that termination isn't on the windward side of the house.

    Regardless of clearances that could make for a bad situation.

    Measured Performance more than just a buzzword

  11. #11
    Bob Waysack's Avatar
    Bob Waysack Guest

    Default Re: B Vent Window Clearance

    In southern California I run into gas water heater vents closer to 8 feet to the walls at the roof. It's all stucco out here, so why is it a problem?
    IMG_4571.JPG


  12. #12
    Bob Waysack's Avatar
    Bob Waysack Guest

    Default Re: B Vent Window Clearance

    In soutern California I run into gas water heater vents closer than 8 feet to the walls at the roof. It's all stucco out here, so why is it a problem?
    IMG_4571.JPG


  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: B Vent Window Clearance

    Quote Originally Posted by Bob Waysack View Post
    In southern California I run into gas water heater vents closer to 8 feet to the walls at the roof. It's all stucco out here, so why is it a problem?
    Because it is not going to vent properly there.

    It is not about clearance to combustible material (although there is likely combustible wood framing in that wall) but about free air movement.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •