TPRV drain pipe on Tankless water heater
Tankless gas water heaters are becoming more popular in my area and I am wondering if the termination height standards for the TPRV pipe are the same?
Similar Threads:
-
07-31-2009, 12:13 PM #2
Re: TPRV drain pipe on Tankless water heater
Yes, the termination height if a factor of the most restrictive of all the following: 1) the code (not more than 6" above the floor, ground or receptor); 2) the manufacturer of the T&P valve (at least 6" above the floor, ground, or receptor); and 3) the manufacturer of the tankless water heater (does not matter what they say, between 1) and 2) you are left at 6" above exterior grade
).



Reply With Quote