Results 1 to 4 of 4
Thread: Service drop clearance
-
08-08-2009, 09:08 AM #1
Service drop clearance
Does the minimum 3ft clearance rule apply (roof is greater than 4:12 pitch) when the SE passes over other portions of the hip roof? The actual position of the mast is within 4ft of the roof edge. Note: The attached picture does not show the "sag" very well in the SE but it is below 18 inches at the ridge cap.
Similar Threads:
-
08-08-2009, 11:13 AM #2
Re: Service drop clearance
2006 IRC
E3504.2.1 Above roofs.Conductors shall have a vertical
clearance of not less than 8 feet (2438 mm) above the roof
surface. The vertical clearance above the roof level shall be
maintained for a distance of not less than 3 feet (914 mm) in
all directions from the edge of the roof. See Figure
E3504.2.1.
Exceptions:1. Conductors above a roof surface subject to pedestrian12 inches (305 mm), or greater, the minimum
traffic shall have a vertical clearance from the
roof surface in accordance with Section
E3504.2.2.
2. Where the roof has a slope of 4 inches (102 mm) in
clearance shall be 3 feet (914 mm).
3. The minimum clearance above only the overhangingside of a building.
portion of the roof shall not be less than 18
inches (457 mm) where not more than 6 feet (1829
mm) of conductor length passes over 4 feet (1219
mm) or less of roof surface measured horizontally
and such conductors are terminated at a
through-the-roof raceway or approved support.
4. The requirement for maintaining the vertical clearance
for a distance of 3 feet (914 mm) from the
edge of the roof shall not apply to the final conductor
span where the service drop is attached to the
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
08-08-2009, 12:05 PM #3
Re: Service drop clearance
OK, so in English...
Assuming that the service drop approaches the house at 90 degrees and the roof slope is greater than 4:12, the service mast can be no more than 4 feet in from the edge of the eave, unless the cables are more than 8 feet high.
Did I get that correct?
This one has always confused me and sometimes I cannot digest the code.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
08-08-2009, 12:28 PM #4
Re: Service drop clearance
"Did I get that correct?"
Kinda, sorta.
Must be 8',
Execpt that 3' is allowed but ONLY when
Pitch =>4/12
AND mast is <4' from edge,
AND SE cable over roof is <6'.
Forget the 90deg thing.
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.



Reply With Quote
Bookmarks