    I was at the hospital with my daughter yesterday and while waiting for her to get done with her tests I noticed that there are several outlets in the waiting area and the bathroom that are orange. There are also many plain white ones too.

    What is the significance of the orange outlets?

    By the way my kiddo is OK and will be back on her feet today.

    Jonathan

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Orange outlets - why?

    Isolated ground receptacles used to be designated with an orange face.


  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Orange outlets - why?

    Isolated ground receptacles do not necessarily mean that there is emergency power from another source. There would be 2 grounding means in the wiring method, one for the ground prong, another for the conduit and boxes.

    At least in my experience emergency powered devices are red or have a red trim plate.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Orange outlets - why?

    406.2 Receptacle Rating and Type.
    - (D) Isolated Ground Receptacles. Receptacles incorporating an isolated grounding conductor connection intended for the reduction of electrical noise (electromagnetic interference) as permitted in 250.146(D) shall be identified by an orange triangle located on the face of the receptacle.

    Usually, though, the entire face is orange instead of just an orange triangle.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Orange outlets - why?

    Quote Originally Posted by Jim Port View Post
    Isolated ground receptacles do not necessarily mean that there is emergency power from another source. There would be 2 grounding means in the wiring method, one for the ground prong, another for the conduit and boxes.

    At least in my experience emergency powered devices are red or have a red trim plate.
    I think you'all answered the question. Those look red to me, not orange.


  6. #6
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Orange outlets - why?

    Nah, those are orange. The labels on the plates are red.

    The green dot means "Hospital Grade".


  7. #7
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Orange outlets - why?

    Isolated grounds are the only place you are allowed to install receptacles that have the orange triangle or an orange face.