Results 1 to 9 of 9

Thread: Meter Base

  1. #1
    Mark Schniers's Avatar
    Mark Schniers Guest

    Default Meter Base

    What size service breaker is this (pictured) meter base rated for?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Meter Base

    Looks like an old 100 AMP. However, the size of the wire from the meter to the service disconnect may further limit capacity.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Meter Base

    Looks like that says "cx200", which I thought indicated a 200 amp meter.

    Which, of course, is only a meter rating, not a service rating. Service entrance conductor size would limit that as well.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Meter Base

    The meter may well be rated for 200 AMPs - a lot of meters are. The meter base, however, doesn't have the bending space necessary for anything much larger than a #4, maybe a #2 (which will get you to 125 AMPs if copper). However, a lot of the small square meter cans are rated for 100 AMPs Newer ones the same size MIGHT be rated for 125 AMPs -depends on the age and manufacturer.


  5. #5
    Mark Schniers's Avatar
    Mark Schniers Guest

    Default Re: Meter Base

    Quote Originally Posted by Jerry Peck View Post
    Looks like that says "cx200", which I thought indicated a 200 amp meter.

    Which, of course, is only a meter rating, not a service rating. Service entrance conductor size would limit that as well.
    Yeah Jerry that is what I thought too but I also know the shape such as Bill pointed out indicates it's rating or should I say capacity. The only thing I had to go on with this one was the size of the box and the main breaker. I could not see the SC (in runway) or get to the panel as it was blocked by a water softener and the wall/floor were wet.

    Thanks for your help guys!

    Last edited by Mark Schniers; 08-16-2009 at 03:47 AM. Reason: to say thanks

  6. #6
    Tony Dolce's Avatar
    Tony Dolce Guest

    Default Re: Meter Base

    The enclosure does not look big enough for 200 amp wiring (3/0 xhhw)
    Tony Dolce
    Meade Electric
    Affordable Phoenix Electrical Contractor, Meade Electric Expert Electrical Repairs And Installations In Phoenix


  7. #7
    Tony Dolce's Avatar
    Tony Dolce Guest

    Default Re: Meter Base

    The enclosure does not look big enough for 200 amp wiring (3/0 xhhw)
    Tony Dolce
    Meade Electric
    Affordable Phoenix Electrical Contractor, Meade Electric Expert Electrical Repairs And Installations In Phoenix


  8. #8
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Meter Base

    Quote Originally Posted by Tony Dolce View Post
    The enclosure does not look big enough for 200 amp wiring (3/0 xhhw)
    Standard residential service entrance conductors for 200A would be 2/0cu or 4/0al.

    Just a note to H-I's. The "CL200" or whatever it says on the meter is almost always completely irrelevant. The meter itself is pretty much never a determining factor as far as service size goes.
    The POCO's own the meter and will use whatever they need to. Most plug-in style meters will be CL200 meters regardless of service size.
    Since the POCO owns, maintains and replaces the meter itself at their discretion it is my opinion that it is a non-issue as far as inspections go.


  9. #9
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Meter Base

    Quote Originally Posted by Mark Schniers View Post
    What size service breaker is this (pictured) meter base rated for?
    The meter base can fool you. This place has an old 60 amp style base, but they managed to pull #3 copper conductors thru and upgraded to 100 amps.