Results 1 to 9 of 9
Thread: Meter Base
-
08-15-2009, 04:59 AM #1
Meter Base
What size service breaker is this (pictured) meter base rated for?
Similar Threads:
-
08-15-2009, 06:20 AM #2
Re: Meter Base
Looks like an old 100 AMP. However, the size of the wire from the meter to the service disconnect may further limit capacity.
-
08-15-2009, 06:37 AM #3
Re: Meter Base
Looks like that says "cx200", which I thought indicated a 200 amp meter.
Which, of course, is only a meter rating, not a service rating. Service entrance conductor size would limit that as well.
-
08-15-2009, 06:39 PM #4
Re: Meter Base
The meter may well be rated for 200 AMPs - a lot of meters are. The meter base, however, doesn't have the bending space necessary for anything much larger than a #4, maybe a #2 (which will get you to 125 AMPs if copper). However, a lot of the small square meter cans are rated for 100 AMPs Newer ones the same size MIGHT be rated for 125 AMPs -depends on the age and manufacturer.
-
08-16-2009, 03:46 AM #5
Re: Meter Base
Yeah Jerry that is what I thought too but I also know the shape such as Bill pointed out indicates it's rating or should I say capacity. The only thing I had to go on with this one was the size of the box and the main breaker. I could not see the SC (in runway) or get to the panel as it was blocked by a water softener and the wall/floor were wet.
Thanks for your help guys!
Last edited by Mark Schniers; 08-16-2009 at 03:47 AM. Reason: to say thanks
-
08-16-2009, 11:24 PM #6
Re: Meter Base
The enclosure does not look big enough for 200 amp wiring (3/0 xhhw)
Tony Dolce
Meade Electric
Affordable Phoenix Electrical Contractor, Meade Electric Expert Electrical Repairs And Installations In Phoenix
-
08-16-2009, 11:24 PM #7
Re: Meter Base
The enclosure does not look big enough for 200 amp wiring (3/0 xhhw)
Tony Dolce
Meade Electric
Affordable Phoenix Electrical Contractor, Meade Electric Expert Electrical Repairs And Installations In Phoenix
-
08-17-2009, 12:01 PM #8
Re: Meter Base
Standard residential service entrance conductors for 200A would be 2/0cu or 4/0al.
Just a note to H-I's. The "CL200" or whatever it says on the meter is almost always completely irrelevant. The meter itself is pretty much never a determining factor as far as service size goes.
The POCO's own the meter and will use whatever they need to. Most plug-in style meters will be CL200 meters regardless of service size.
Since the POCO owns, maintains and replaces the meter itself at their discretion it is my opinion that it is a non-issue as far as inspections go.
-
08-17-2009, 08:27 PM #9



Reply With Quote