Results 1 to 5 of 5
-
08-24-2009, 10:28 AM #1
Non-continuous feeders to load side panel
Is there any reason why the feeders from service equipment to a load side panel cannot be non-continuous, as long as the two lengths are "spliced" with an appropriate connector within a junction box to which they are properly attached?
If allowed, are there any likely defects to check for at such a connection?
- Thanks
Similar Threads:
-
08-24-2009, 10:36 AM #2
Re: Non-continuous feeders to load side panel
Is this the situation with the cable thru the stairwell?
I think for the reliability factor I would just buy new cable. One less point of potential failure. Polaris connectors are for 4/0 are about $30 each x 4 = $120 alone. Add in the cost of the JB and connectors and you are very close to the price of 50 foot of 4/0 SER.
-
08-24-2009, 11:22 AM #3
Re: Non-continuous feeders to load side panel
-
08-24-2009, 11:51 AM #4
Re: Non-continuous feeders to load side panel
Thanks!
Would split-bolts be acceptable?
-
08-24-2009, 11:56 AM #5
Re: Non-continuous feeders to load side panel



Reply With Quote