Thread: Service entrance ground wire
09-03-2009, 03:16 PM #1
There are two 70 amp. services coming into this service box but only one ground wire is that acceptable.
09-03-2009, 04:07 PM #2
Re: Service entrance ground wire
Ryan,
I don't think you can really call them mains, since main refers to one, but I am at a loss as to what to call it.
The single ground is fine.
You probably noticed that the doubled neutral conductors in pic #4 are not. Each conductor should have it's own terminal.
09-03-2009, 04:50 PM #3
09-03-2009, 04:51 PM #4
09-03-2009, 05:35 PM #5
"two ... services coming into" or do you mean 'two feeders going out from' that service equipment?
I see the meter right there to the right, which likely means there are bus bars feeding those two mains, which are feeding (i.e., 'have feeders' going out to panels).
On the open lug and double tapped neutrals I am going to guess that who ever wired that up (most likely an electrician as that is service equipment) looked at the larger neutral terminal lug and the smaller ground terminal lugs and thought to themselves ... 'Hmmmm ... I have 3 ground wires and 2 neutral wires but only 1 neutral terminal.', not realizing that at service equipment they are all basically both.
09-03-2009, 08:59 PM #6
09-03-2009, 09:08 PM #7
09-03-2009, 09:28 PM #8
09-04-2009, 11:12 AM #9