Results 1 to 3 of 3
  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Outlet requirement

    This wall along the landing is about 6 feet. Single family home built in 97. Would an outlet be required along the wall at a landing.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Outlet requirement

    I'd say no.... the most stingent rule you could apply would be a hallway which is every 10 feet. It's not a room where the 2 foot rule would apply... at least not IMO. I'm sure someone may have a differning idea.

    Either way it's nothing that would ever make my radar.


  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Outlet requirement

    A stairway is not a habitable room so the 6/12 rule does not apply. It is also not a hallway so that requirement does not apply either.

    All answers based on unamended National Electrical codes.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •