    Gas WH located within a closet of a laundry room which has a door to the garage.
    Should WH be 18" from the floor or not? Code reference if possible.
    Thanks, Mama M.

    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 18inches or not?

    Is the laundry in the garage, or in the house, with access to the garage?
    In the garage, yes, 18".
    In the house (heated/ cooled room) with access to the garage, no.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: 18inches or not?

    But the door should be a weather stripped type. Not something with a 1 inch gap at the bottom that gas fumes could get through.
    irc 1307.3, 2801.6 18 in above

    irc 2005.2, 2406.2 fire door


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 18 inches or not?

    Quote Originally Posted by wayne soper View Post
    But the door should be a weather stripped type. Not something with a 1 inch gap at the bottom that gas fumes could get through.
    irc 1307.3, 2801.6 18 in above

    irc 2005.2, 2406.2 fire door

    Not quite that easy.

    1) If the laundry room is also open to the living space, no, it is not required to be raised 18".

    2) If the laundry room only opens to the garage, yes, it does need to be raised so that the ignition source is a minimum of 18" above the garage floor.

    3) If 1) above, the door is part of the thermal envelope of the house and needs to be weather stripped - whether or not there is any gas appliances in the laundry room.

    4) If 1) above and the clothes dryer is gas ...

    5) ... What "fire door"? There is no "fire door" between the garage and the house - we have been over this so many times I figured that knowledgeable home inspectors would have quit calling that a "fire door".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 18inches or not?

    4) If 1) above and the clothes dryer is gas ... "


    Gas or electric, no difference