Metal Chimney distance from an operable window and above soffit
Need clearances for this chimney exhaust from an operable window and above soffit. Picture attached
Thanks, Jim
Similar Threads:
-
04-13-2018, 04:08 PM #2
Re: Metal Chimney distance from an operable window and above soffit
8' clearance from vertical walls so that doesn't cut it. It's more accurately a B-vent and not a chimney.
-
04-14-2018, 08:19 AM #3
Re: Metal Chimney distance from an operable window and above soffit
It's 8' from the sidewall, minimum, or 2' above the roof above.
It's also, as I recall, 10' from a building opening (windows, doors, soffit vents, etc.
-
04-29-2018, 11:01 PM #4
Re: Metal Chimney distance from an operable window and above soffit
Next time get the manufactures info off the appliance. you can look up the manual which gives you the clearances.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
05-09-2018, 06:06 AM #5
-
05-09-2018, 06:22 PM #6
Re: Metal Chimney distance from an operable window and above soffit
What type of appliance was that vent pipe serving? Some appliances allow significantly reduced clearances. Pellet stoves are among some that do.