Minimum Sub Panel Height?
Hi,
I ran into this distribution panel today and it has me wondering if there is a minimum height for service and distribution panels? The upper breaker height on this panel is 31" and the bottom breaker is at 22". I know there is a maximum breaker height and that meters have a minimum and maximum. Maybe the electrician wanted to wire it while sitting on the floor?
Other than the ground and neutrals being isolated at the service panel but being bonded at the distribution panel everything else looked good.
Thanks!
Similar Threads:Last edited by Leo Leidlein; 06-17-2009 at 03:21 PM. Reason: correcting terminology
-
06-17-2009, 03:08 PM #2
Re: Minimum Sub Panel Height?
This has been discussed before.
There is no minimum height. There is a required free work space in front of the panel. There is a maximum height.
Low panels are inconvenient but not against code.
And before someone else jumps on you, the forum rules of etiquette state there are only Service Panels and Distribution or Equipment Panels. There are no such things as Sub panels. Subpanels only exist in submarines.
"The Code is not a peak to reach but a foundation to build from."
-
06-17-2009, 03:17 PM #3
-
06-17-2009, 05:14 PM #4
Re: Minimum Sub Panel Height?
While on the subject of panel boxes I came across one today in a master closet that had evidently been used at once for a faux safe box. It had a lock on the panel cover. I pulled the door back far enough to shine a light inside to find it was completely empty and had no electrical componets at the inside.
I guess the homeowner decided to break down and buy a real wall safe as there was one next to it. Funny thing was the screws that held the safe in position was on the outside of the drywall. All anyone would have to do is remove those screws and you could have walked off with the safe.
Genious?
rick
-
06-17-2009, 09:48 PM #5
-
06-18-2009, 03:00 AM #6
Re: Minimum Sub Panel Height?
LL: Assuming that is a garage location and there are no breakers within 18" of the floor, the installation, though stupid, appears to be compliant.
-
06-18-2009, 06:44 AM #7
Re: Minimum Sub Panel Height?
-
06-18-2009, 08:26 AM #8
Re: Minimum Sub Panel Height?
Bingo! That is a garage, or at least looks like it, and breakers would definitely be ignition sources.
As you guys have said, though, it is dumb to put it that low.
-