04-09-2012, 07:35 AM #1
Bonding jumper location on Pushmatic Bulldog panel
Load-side panel. Labeling was not visible and I could not locate the bonding jumper location.
Anyone know where I should be looking?
Yes, I know panel is obsolescent - whole unit was obsolescent, furnace was a Lenox manufactured in Oct. 1971, oldest operating GFAF (41 years) I've even seen.
Thanks
Similar Threads:
-
04-09-2012, 07:50 AM #2
Re: Bonding jumper location on Pushmatic Bulldog panel
When you say load side do you mean a non-service panel, ie there is a means of disconnect ahead of this panel?
Do you have a pic of the neutral buss?
All answers based on unamended National Electrical codes.
-
04-09-2012, 11:02 AM #3
Re: Bonding jumper location on Pushmatic Bulldog panel
Yes, this is a load-side panel ("sub-panel").
This is the only portion of the "neutral bus" visible at the panel.
-
04-09-2012, 11:46 AM #4
Re: Bonding jumper location on Pushmatic Bulldog panel
Micheal is in Chicago, so we know that all equipment grounding is by way of the conduit, eh?
My guess is that the panel is set up as a suh suh remote panel and no bonding device was ever provided.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
04-09-2012, 11:57 AM #5
Re: Bonding jumper location on Pushmatic Bulldog panel
-
04-09-2012, 01:29 PM #6
Re: Bonding jumper location on Pushmatic Bulldog panel
Hi Mike,
The bonding jumper screw in the old Pushmatic of this style are generally between lug 3 and 4 (based on your 1st picture). It will not be green and it tends to blend in. It physically looks different in comparison to the lug connections on the bottom of the bus detail and the single screw (next to the bumped-out stops next to the screws) connections on the bus detail above the lugs. I may have a picture of one, if I do, I'll post it.
Corey
-
04-09-2012, 01:52 PM #7
Re: Bonding jumper location on Pushmatic Bulldog panel
the second photo top breaker allows copper and aluminum...
Last edited by Stephen G; 04-09-2012 at 02:24 PM.
-
04-09-2012, 05:50 PM #8
Re: Bonding jumper location on Pushmatic Bulldog panel
M.T.
This is not service equipment, its MLO. Should be a lock-nut under the bushing at the bottom left to threaded rigid metal conduit, fitting, wireway, etc.. The ground bar bar when installed/present as load side of service equipment would be mounted upon the back wall to the right most starting at a height below the highest breaker and would extend vertically downward. That back wall section is not visible in your photos.
You'll see a grounds bus (painted over) installed at D.F.'s site here: http://inspectapedia.com/electric/Pu...ls021-DJFs.jpg
Last edited by H.G. Watson, Sr.; 04-09-2012 at 06:09 PM.
-
04-09-2012, 05:53 PM #9
Re: Bonding jumper location on Pushmatic Bulldog panel
Looks like there is a locknut there.
-
04-09-2012, 07:14 PM #10
Re: Bonding jumper location on Pushmatic Bulldog panel
I agree with Robert, I see the locknut.
All answers based on unamended National Electrical codes.
-
04-09-2012, 07:28 PM #11
Re: Bonding jumper location on Pushmatic Bulldog panel
Locknut was (is) there:
-
04-09-2012, 07:38 PM #12
Re: Bonding jumper location on Pushmatic Bulldog panel
Now, I'm wondering what this "yellow button" is...
-
04-10-2012, 11:03 AM #13
Re: Bonding jumper location on Pushmatic Bulldog panel
I'm not entirely certain, as it has been many years since I've dealt with a Bulldog Electri Center from Detroit, or an early ITE acquisition panel... I'm also recalling main or lighting main switches that weren't actually breakers used in such, but I'm having a foggy morning.However, if I'm remembering correctly, the same componant parts were used in the manufacture of split buss panels from Detroit. If they had been in a split buss or a main switch not CB panel, I'm thinking that would be where the insulated jumpers would pass so as to connect to the split buss(es), making those "buttons" fillers/insulators/isolators and/or guards, they might be nylon (?).Besides replacements being expensive, costly, older types being unavailable except on the unreliable gray market or used; the breakers themselves are limited in their ability to quickly react to an overload condition (trip type). Panel is of a vintage where direct testing was not undertaken to assure ratings (merely calculated based upon a series of later disproven assumptions). Push button operation and assured fully open or fully closed condition even as indicated, is unreliable, lubrication unreliable, and provides ability for unsafe hack work - provides for direct bolting conductors to buss without use of any special tools, etc. even if unintentional.