01-28-2013, 07:11 AM #1
Cardboard Behind Knee Wall
I came across this in a Cape Cod style house behind the knee wall.
The area would be considered conditioned space as what little insulation is between the rafters. What would you say?
Similar Threads:
-
01-28-2013, 10:06 AM #2
Re: Cardboard Behind Knee Wall
Yep, that's a fire hazard and it has to go.
Recycling is great but creating a death trap with cardboard is not cool.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
01-28-2013, 05:10 PM #3
Re: Cardboard Behind Knee Wall
Won't burn any faster than the facing on that insulation ... ... between the two, that attic ought to up in flames rather quickly.
-
01-30-2013, 08:52 AM #4
-
01-30-2013, 08:54 AM #5
Re: Cardboard Behind Knee Wall
I would not consider an attic to be a "conditioned space" unless there were HVAC vents there.
The walls and ceilings should be appropriately insulated. I recommend removing building materials and insulation from roof sheathing as it limits its inspection and traps heat.
-
01-30-2013, 10:08 AM #6
Re: Cardboard Behind Knee Wall
The walls should be drywalled with taped seams. Minimal air movement. Then some cardboard boxes on the floor are fine.
That kneewall cavity is closet space unless the hatch is permanently sealed.
Back in 70's a family I know lost everything they had in about 20 minutes, including their cardboard insulation.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
01-30-2013, 10:50 AM #7
Re: Cardboard Behind Knee Wall
1) The cardboard is probably there to to secure insulation to the roof sheathing, which is not a good idea.
2) IF you want to consider this space a closet, then there should be no ventilation (soffits) and no baffles open to the upper attic.
3) I'm not aware of any model code requires gypsum board on interior walls (I'm sure the IRC does not). Paneling, hardboard, plaster, or tile would also be acceptable.
4) There is no requirement (at least in the IRC) to "permanently seal" the hatch or door to a knee wall attic space.
5) I can find no code that requires interior gypsum to even be taped at the seams with the exception of a garage.
-
01-30-2013, 05:02 PM #8
Re: Cardboard Behind Knee Wall
Fair enough. It;s not a code issue, aside from removing the fire hazard.
I recommend finishing the space to make it a safe and usable closet. You recommend tearing down the insulation and making it an unheated attic space. If so, then the hatch should be insulated as well and screwed shut to keep it sealed.
Space is limited and there is a hatch in the kneewall. It will be used for storage. The hatches are rarely insulated and weatherstripped properly.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
07-07-2013, 05:16 AM #9
Re: Cardboard Behind Knee Wall
Not knowing the age of the house, it is common to see cardboard used in older homes which predate modern codes.
Would I make a big deal of it? No.